Isolating the system for a planned power cut
@batpred - that Solis installation page is too vague.
Yes, they state that there's RCD protection inbuilt to the inverter.
But we don't know to what extent that offers protection to the inverter itself,
nor whether that protection covers appliances which are connected to the always-on port.
As matters stand, that integral RCD would still leave the supply cable and isolation switch unprotected.
I don't like having any conductors leaving the distribution board without both over-current and earth-leakage protection.
The regulations for new installations are even tighter.
You now need ARC-detection trips within the consumer unit.
Those will disconnect the circuit in the event of cable damage within the wall - perhaps vermin eating the insulation.
Whether that measure will reduce house-fires or not is too early to say, but insurers like it.
Save energy... recycle electrons!
Bu the way, my understanding is that arcing detection is not required for new circuits unless it is a shared use property? Or is it only for rental properties?
As for SPD protection, for the extra £20 or so when getting a new unit, it was a no brainer. It also helped us removing the ad-hoc surge protectors we had like to stop the boiler PCB blowing up when power comes back following a black-out.
Posted by: @batpredmy understanding is that arcing detection is not required for new circuits unless it is a shared use property?
That's correct.
I was mentioning it as something which would be a future requirement.
Both arc-detection and surge suppression devices (SPD) are like paying an insurance package.
Even if you decide not to implement them, you should at least know that they are available options and why.
There are also different levels of protection offered, according to the specification of the devices you choose to install.
Your SPD might do all that you want at £20.
On the other hand, I use high-end Phoenix Contact suppression systems on both mains and PV panel connections.
The pair in the consumer unit which receives the mains incomer cost substantially more than £100.
There are reasons why some insurance premiums cost less than others.
Save energy... recycle electrons!
Insurance helps and when adding high powered devices like EV chargers, PV panels and some inverters and heatpumps, the other circuits may need to be a bit more shielded, and future proofing is also worth. We had our supply upgraded to 100A but only after a few years and another visit did I feel they had given us that insurance.
Price of components can also be driven by volume and other considerations like supply chain requirements to recoup r&d costs.
Apologies, I don't follow what you've written @batpred
The possibility of damage from surges doesn't increase with 'high powered' devices.
In fact the device most likely to be damaged by a surge or spike on the mains is a landline telephone or internet router, supplied by copper wires.
That's because there can be a voltage difference between the mains and the telecom cables.
Posted by: @batpredWe had our supply upgraded to 100A but only after a few years and another visit did I feel they had given us that insurance.
I was referring to 'insurance' as a metaphor.
The size of the service fuse doesn't change the susceptibility to damage from surges.
Posted by: @batpredPrice of components can also be driven by volume and other considerations like supply chain requirements to recoup r&d costs
Phoenix Contact surge arresters dominate the commercial market.
There are thousands of types in their catalogues.
They are proven to be affective because Pheonix Contact are based in the Black Forest, in the south of Germany.
That area has the highest number of lightning storms in Europe.
They can easily test products in real-world conditions as well as a laboratory.
It's relatively easy to make a surge arrester which protects equipment from a single spike.
The key point is what then happens to the arrester?
If it doesn't recover to full operational specification, then it's useless.
The next surge will get through.
Buyers are prepared to pay more for an anti-surge device that is more likely to provide protection.
Save energy... recycle electrons!
I may have lost you there.. I use the insurance term as proxy for the "additional life" that was only given when the DNO replaced some components that despite being rated for 100A, were more fitting as museum pieces!
When I broadly mentioned circuits needing to be "shielded", it was not in the electrical sense, a better word may have been "cushioned". Specifically that when inverters and similar components are added to a household, some components that protect other circuits like RCDs type AC need replacing, ideally with RCBOs type A. We had a mid sized plastic consumer unit and that went a few months ago, as part of the prep.
- 26 Forums
- 2,265 Topics
- 50.6 K Posts
- 69 Online
- 5,924 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Electricity price predictions
Is the distance between those new farms and where the e...
By Batpred , 3 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa hopefully after the rad balancing it will perf...
By AdamK , 3 hours ago
-
RE: Midea ASHP – how to set weather compensation
@mosibi yes I am interested in potentally evolving my s...
By benson , 5 hours ago
-
RE: UFH downstairs and radiators upstairs balancing question
@davidnolan22 Hi, ok first of all it very hard to truly...
By ASHP-BOBBA , 6 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Installers coming tomorrow. One has messaged messaging ...
By Crimson , 7 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
11.2kW Ecodan Manufacturer: Misubishi Model: PUZ-WM...
By DRB01 , 7 hours ago
-
RE: Homely asking about Solar Panels.
@majordennisbloodnok I will report back with any develo...
By Toodles , 10 hours ago
-
RE: Mediation with RECC, what's your experience?
@editor Thank you, I really appreciate it! I've made ...
By TreeWizard , 11 hours ago
-
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Are you able to post a photo of that 180-litre cylinder...
By Transparent , 13 hours ago
-
Agreed. It doesn't take all that much maintenance to ke...
By Majordennisbloodnok , 15 hours ago
-
RE: Oil Boiler & Heat Pump Hybrid System
OK. Got it. As a fellow rural West Country resident, ...
By Transparent , 17 hours ago
-
RE: My DIY Heat Pump installation
@pollar-bear Top job, I installed my own too and even t...
By bontwoody , 18 hours ago
-
RE: Who has a V2G EV installation
Not sure how you got that information, @batpred. As of ...
By Majordennisbloodnok , 18 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 1 day ago
-
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 2 days ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 2 days ago
-
RE: New build installation query
@paullacey While the others wait for more info do you m...
By ASHP-BOBBA , 2 days ago