Posted by: @amanda1@derek-m Hokay - please could you explain to what part of this process do the terms Flow Temperature and Return Temperature apply? (if they do). And why is it considered more economical for flow temperature to be as low as possible? And what is in those insulated two big pipes connecting the pump to my house - one with a blue lever, the other with a red lever. Is it fluid?
Assuming that you have a monobloc heat pump, the two insulated pipes will be carrying the water, or water antifreeze mixture, into your home.
The Flow temperature, often called Leaving Water Temperature (LWT), is the temperature of the warm water coming out of your heat pump and being supplied to the heat emitters or hot water cylinder.
The Return Temperature or Return Water Temperature (RWT) is the temperature of the water going back to the heat pump from the heat emitters or hot water cylinder.
When the heating system is working normally, the LWT should be approximately 5C higher than the RWT.
The water is heated by the refrigerant gas, which of course needs to be warmer than the water for thermal energy transfer to take place. If the heat pump is warming the water to a higher LWT, then the compressor will need to work harder, which in turn will use more electrical energy. It is therefore normally more efficient to operate the heat pump at the lowest LWT that meets the heat demand of your home.
Posted by: @amanda1@derek-m Hokay - please could you explain to what part of this process do the terms Flow Temperature and Return Temperature apply? (if they do). And why is it considered more economical for flow temperature to be as low as possible? And what is in those insulated two big pipes connecting the pump to my house - one with a blue lever, the other with a red lever. Is it fluid?
@amanda1 Yes, a lot of things happen inside that monobloc case! However, it is a well proven invention as we have been using refrigerators for many many years! The ‘fridge is delivered and apart from letting it stand for a while for the gas to settle before switching on and enjoying food storage advantages for some years without need to service the appliance; the heat pump needs installing with care / skils and requires setting up and if like many people on this forum know, their users take a great deal of care to ensure they are running as efficiently as possible. Of course they are normally outside and exposed to the elements and require servicing on a regular basis… Regards, Toodles.l
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@amanda1 - I can offer a diagram which is somewhat less daunting, if it helps.
I'll assume that you are a teacher by profession.
Please feel free to comment if any of us are going too deep into technicalities.
Disseminating useful information must be a principle reason for the existence of this forum.
Save energy... recycle electrons!
@transparent thanks - I am assuming the compressor is inside the Monobloc? But is the condenser in there as well? What is the small red cylinder for?
@amanda1 Mine was after 12 years without even a service 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I'm adding annotations to your photo, @amanda1
But is that cupboard within the heated envelope of the house or outside?
Save energy... recycle electrons!
@amanda1 This tank is used to apply a pressurised water feed to your circulating heating water. Normally the tank ispressurised from the water main to 1 - 1.5 bar; the tank contains a membrane (rubber or more modern equivalent?) so that the pressure is held and it is shown on a pressure guage attached to the tank. Normally the water main supply is isolated from the tank by two stop valves. Should the pressure drop (due to very slight leaks or evaporation etc., the tank pressure is topped up by opening the two stop valves until the pressure guage shows a level of pressure withing the red region - then the valves should be shut again. Sudden loss of pressure is however, an indication that there is a need for attention to the system. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@amanda1 The red cylinder looks like an expansion tank, which will probably be on the central heating/hot water circuit. The CH/HW circuit will probably be a sealed system pressurised to 1 or 2 Bar, there should be a gauge and a filling loop as well. The expansion tank will regulate the water pressure as it expands and contracts over temperature. Old fashioned open systems had a tank in the loft.
I believe that all of the components of a mono block heat pump are in the one unit. There are also split designs in which only the fan and heat exchanger are outside and the rest is in another unit inside.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 48 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 34 minutes ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump what we did to resolve a not too dissimilar...
By benson , 2 hours ago
-
My Samsung Gen6 (probably same controller as yours) onl...
By Old_Scientist , 11 hours ago
-
@drei When I was in local government we were of cours...
By JamesPa , 11 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 13 hours ago
-
RE: Boiling Mad: Exposing Radiatorgate
@rob-nezard you can see more of Drei's rad dramas here ...
By Mars , 13 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@drei I will say again that Im sorry to heat about your...
By JamesPa , 14 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 1 day ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 1 day ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 1 day ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 1 day ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 2 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 2 days ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 2 days ago