What happens when the outside temperature exceeds the upper WC point?
Ive posted this following a comment in another topic which I didnt want to take off track.
I have always thought that when using a weather compensation curve, once the outside temperature exceeds the top set point (eg a flow temperature of 40C at 17C outside), that the heat pump switches off its heating function.
However it was suggested that what might happen is that the flow temperature just stays at 40C and does not change. I can see the logic of this as at the other end I would not expect the heating to switch off at say -3C 🙂
The problem with this is though that as the outside temperature rises, if the heat pump stays on then it will cause the house to overheat and cost money needlessly. This scenario would require the user to actively turn the heating off.
Does anyone have a definitive answer to this, or do different heat pumps handle the situation differently?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I actively turn my CH off during the summer. I know that doesn't answer your question, but I feel it is the best option.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Our Vaillant at present (outside temp 18C and the heat pump is off since internal temperature is above the set point) has a target temperature for water flow of 22C. In the installer menu there is also a flow temperature limit of 20C (and an upper of 46) plus a external temperature limit for switching off.
That external limit was set to 19C but I’ve put it down today to 17C.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
I cannot speak for other manufacturers, but I know Samsung's WC 'curves' are very simplistic with just two set points with a straight line between, and flat horizontal lines beyond. Once the two points are exceeded, the 'curve' is flat. So if I had a LWT of 30C set at 15C OAT, and 40C at -2C OAT, once the outside temperature gets above 15C, the flow temp would remain at 30C in this example.
The Samsung has a separate configurable setting to turn off space heating above a certain ambient temperature and is set to turn off space heating at 25C on my system (35C was the default).
As you surmise, this is how I would expect most systems to behave rather than simply turning off. The other option would be to extrapolate the curve beyond the set point rather than flat-lining.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist Well thats answered the question for my Samsung 🙂 Is the setting to turn off the space heating just the thermostst in the controller?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
That’s a really good question, and the behaviour can vary slightly between heat pumps, but CIBSE actually recommends that heat pumps should shut off when outdoor temps exceed the compensation curve’s upper limit. The logic is exactly what you’ve highlighted – avoiding unnecessary overheating and runtime.
Some manufacturers implement this as a hard cut-out (e.g., once it’s 17°C outside and your curve tops out at 40°C flow, the heat pump stops heating entirely), while others might let the system idle at minimum output. The risk with the latter approach is exactly what you’ve described: if the house is already warm enough, you’re just burning electricity to maintain a flow temp nobody needs.
This is why we, like @Morgan, just turn our heating off (leaving just HW) when we hit this time of year.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Thanks Mars, thats very helpful
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Mitsubishi has a separate setting, like Samsung, to turn the heat pump off above an outside temperature. And turn the heat pump on below an outside temperature. Mitsubishi call this summer mode.
There's a separate setting again (called auto change over) to automatically switch from heating to cooling, or cooling to heating, at certain outside temperatures.
@robs I will have to see if I can find the Samsung setting. Thanks.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
The weather compensation is a control strategy mainly directed at controlling a capacity step function by using the inverter tech and LEV-EXP devices, this is to say it runs your system slower and faster or higher and lower which ever way you would like to describe it, this is subject to OAT and demand. It is not normally a main stop or overheat protection. CIBSE and building control still mandate that you must have at least one main stat to prevent wasting energy and overheating the house without human intervention. You typically have 3 types of stop, No1 main stat (even open loop systems need a single stat somewhere in the home although set to say to 22 if the open loop is designed 20) No2 timers, this would be 7 day event, holiday or hourly if used and No3 forms of set back pauses and or temperature related function changes for example Mitsubishi Electric Ecodan summer mode function max OAT set run point.
Just get a stat fitted, set it 1 or 2 deg above your open loop design and then you will prevent loosing to much energy, just to give context, if the OAT is 20 and your open loop is designed to deliver 20 and manages to heat the room up to 22 it would not take long to get the building a further 2 deg higher with that OAT.
Or turn the heating off end March and only back on for a couple cold days in April if needed, like we all used to on the old boiler. 🙂
@bontwoody on my gen6 Samsung it's FSV #4013 Heating Off Temp, and by default is set to OAT of 35C (I have reduced mine to 25C). Like @ashp-bobba says above, I tend to just turn the heating off in April and back on in Oct as the weather dictates, but it's a useful safety so the heat pump isn't trying to heat the house when it's 30C outside.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
-
Savings - using Weather Compensation & Time of Use Tariffs
2 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
3 months ago
-
LG Therma V. Software upgrades, AI (weather compensation), SCOP
1 year ago
-
LG Therma V R32 Monobloc. Setup advice inc flow temperature & weather compensation
2 years ago
-
Daikin EDLA14D3V3 COP is now below 1
2 years ago
Currently viewing this topic 1 user ( Potatoman ) .
- 22 Forums
- 2,043 Topics
- 44.5 K Posts
- 39 Online
- 3,264 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
If you have a buffer tank you will have a post buffer t...
By Potatoman , 9 minutes ago
-
RE: Help me understand my Mitsubishi Ecodan system
Does the big on/off button at the top left corner of th...
By Abernyte , 1 hour ago
-
RE: Ecodan Legionella cycle - immersion heater problem
Thanks for letting us know @clockworks I admire your ...
By Transparent , 15 hours ago
-
@fillib what a wonderful result, both for you personall...
By Judith , 1 day ago
-
RE: Revised version of MCS-020 (noise standards for heat pumps)
As you say this is no change, which I personally think ...
By JamesPa , 1 day ago
-
RE: What happens when the outside temperature exceeds the upper WC point?
@editor not via the WC curve but as @old_scientist ment...
By bontwoody , 1 day ago
-
RE: MHHS and Heat Pump compatibility
@toodles to be clear I don't know if there will be a re...
By Scalextrix , 2 days ago
-
I did not know this concept, although others might. I...
By Morgan , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk it's probably filtering different providers in t...
By Mars , 2 days ago
-
RE: why solar diverters for HW instead of the heat pump?
I should probably add to my comments above that, whilst...
By JamesPa , 3 days ago
-
RE: Commencing on an ASHP Installation Process
Lots of reading and questioning which the background ma...
By JamesPa , 3 days ago
-
RE: The Great British Heat Pump Quiz
Not sure how that happened 🤣 I suspect that it ...
By Mars , 3 days ago
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
@patch I think @ashp-bobba gave you some great pointers...
By SUNandAIR , 4 days ago
-
RE: Installing your own ASHP - DIY
Hi @tomasmcguinness, how are you progressing with this?...
By Ashfp , 4 days ago
-
RE: Say hello and introduce yourself
Welcome to the forum. If you are new to ASHPs I sug...
By JamesPa , 4 days ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 5 days ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 5 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 6 days ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 6 days ago