Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
The thing that worries me like you have said previously is this section on the complaints side of the MCS certification.
MCS do not have the authority to enforce the following:
To award compensation or other financial redress.
Arrange for installation removal or refunds.
Appoint another installer to undertake remedial work on your behalf.
So if it all fails and gets no where I'm basically stuck with what I have 🤔
So you start to ask yourself what's the actual point in all these organisations 😬
The work is Apparently insured through HIES and NAPIT I think they are called so building regs so we shall see what comes of it.
Preferably I'd like the outside unit put on a concrete base (I'm more than happy to pay to have the base installed)
The external pipe work re done outside to allow better flow/be neater looking. (Again id happy to pay for that fancy conduit boxing to cover it)
A radiator moved to acceptable distance from the wall.
The plastic microbore pipework that should have been replaced replaced.
Buffer tank removed or mounted correctly and re plumbed into a volumiser.
But again we shall see
Posted by: @burtisconcrete base
But with soak away also, otherwise you will have a big chunk of ice that gets deeper every day below zero.
I would remove soil under gravel
Posted by: @burtisradiator moved to acceptable distance from the wall
What is now compared to the minimum in the installer manual - generally it's 400mm.
Posted by: @burtisBuffer tank removed or mounted correctly and re plumbed into a volumiser.
Would ask a more basic question do you need either. If you are running a single zone, unlikely you need either. If you want zones the volumiser brings nothing to the party as it doesn't ensure min flow rates can be maintained.
Posted by: @burtisexternal pipe work re done outside to allow better flow
Yes should be sorted. Note: bends do not directly affect flow rate, they affect system head loss, which results in a pump having to work harder to move a set volume of water. For good efficiency head loss should be minimised where ever possible.
Posted by: @burtisplastic microbore pipework that should have been replaced replaced.
If was in the quote don't make them do it. Don't pay your final bill until happy.
@burtis You are not just stuck with a complaint to MCS.
1: You can use the Consumer Rights Act 2015 (which replaced the earlier "Sale of Goods Act").
It operates through the Citizens Advice Bureaux, which means they can guide you as to which rights of redress are available.
2: For any specific faults which the installer hasn't put right, you can also get it corrected by another company.
Present the bill to the installer and request payment.
If no payment is forthcoming then the Small Claims Division of the High Court is a route you could consider.
3: After checking with your LPA Councillor, he/she may wish to instruct a Building Control Surveyor to have a look.
They might ask you to pay for such a visit.
Or perhaps not. After all, the LPA has a responsibility for Building Control Standards.
Whether you are asked to contribute or not, that route would provide you with a letter or report which identifies where the Regulations haven't been met.
That's a very powerful document, and well worthwhile seeking.
Save energy... recycle electrons!
@johnmo
To be honest I paid up as at the time it all looked ok.
Then when I got into looking at heat pump installs more and researching I realised I may have some problems.
But yes sadly I have already paid.
Currently I don't have a soak away it's just some shingle chucked over the soil that was under the slabs.
The company offered to remove the buffer tank and pump but I would have to pay them to do it to see if it would work. My system is a single zone I believe.
Thanks again I will keep on at it, not something I have ever had to do before or am wanting to do but needs must I suppose 😞
This morning it has stopped working and chucked a error code for flow issues. 😭 Just on time for the weather to cool off 😅
There's a load of black grit stuff in the radiators and one of them was blocked with debris so I'm not surprised to be honest.
If you have a buffer you have a primary and secondary circuit. The primary circuit is the ASHP and buffer. Your flow sensor is in the primary circuit and part of the ASHP. What occurs in the secondary circuit should not affect the primary.
One exception will be system debris. Your primary circuit will have a strainer this is likely clogged up. The secondary circuit a magnetic filter. Clean both.
Was your system filled with antifreeze or water / chemical and antifreeze valves?
@johnmo thank you buddy no my system was never filled with anything, neither did they put anti freeze valves.
We had decorating to do so they left the inhibitor out until we were done sadly.
Posted by: @burtisThere's a load of black grit stuff in the radiators and one of them was blocked with debris
That's almost certainly iron oxide (Fe3O4) ...
... the sort of stuff which a magnetic filter is meant to eradicate.
Are all your radiators new?
Or were some original ones connected to the new heat-pump system?
Did the installer run up the (secondary) system and then drain it to remove debris?
If so, that "flush through" should be listed on the Commissioning Chart.
Save energy... recycle electrons!
@transparent there was only 1 radiator that wasn't changed a old towel rail funnily enough that same room is always cold.
They did flush the system but it didn't really work as it blocked up some upstairs rads straight after.
More troubles 😅
Posted by: @burtisThey did flush the system but it didn't really work as it blocked up some upstairs rads straight after.
Does the installer know that yet?
When a flush-though doesn't fully clear out the system, then you need a Central Heating Cleaning Fluid such as Sentinel X800 or Fernox F3.
There are also additives which break down sludge, particularly iron oxide, but take longer to act.
There's no point adding a System Inhibitor until the existing deposits are flushed out.
Have you checked that the drain-off valve is at the lowest point in the system?
When you drain after a flush through, open the air-bleed valves at the top parts of the plumbing, and that towel radiator in particular.
If you don't do that, then the weight of water leaving the system will be creating a vacuum, which leaves the sludge in place.
Posted by: @burtisa 2nd one on the shut off valve that I can't undo as I don't have a big enough spanner
I have spanners here up to 56mm.
How far can you reach?
In rural areas like where I live, we'd just pop down to the local garage and borrow one.
How friendly is your neighbourhood?
Save energy... recycle electrons!
Yeah the installer is aware that I had a blocked radiator and debris and rust in the system.
This is the only thing they were willing to come back and do.
I will be buying any tools I need to do these strainers definitely just as it's a simple easy fix 👌
I have found a local Heat Geek installer in my area so will speak with him to see if he can check it over as well yomsee if there are any glaring issues I need to sort
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 287 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 19 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 27 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 13 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 14 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 14 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 17 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 23 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 23 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago




