The Definitive Guide to Weather Compensation and Curves for Air Source Heat Pumps
If you’ve been following our Homeowners’ Q&A podcast series, you might know that one of the most valuable takeaways has been around optimising the weather compensation curve for heat pumps. My discussions with experts – including a few off-topic conversations after the recordings ended – have highlighted just how nuanced and crucial this setting is for ideal efficiency. Since every home has unique requirements, setting the perfect weather compensation curve can be challenging but it's highly advisable that homeowners try to figure this out because it'll lead to cheaper running costs.
This thread is a space for sharing insights, experiences and questions around weather compensation settings.
For those starting out, I’ve attached the weather compensation curves issued with our Global Energy Systems 16kW Caernarfon heat pump to serve as a reference point.
Throughout October and November, ours is set to 0.2 which results in a flow temperature between 32-35C, which has comfortably maintained most of our property at 21C (apart from the TV room – our index circuit).
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Please post your heat pump's weather compensation curves and data as a reference.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Im still experimenting with mine Mars, having made some changes to my house in the summer. My low end is 32C (at OAT of 15C) which is probably hotter than I need to keep the house warm but the minimum I can get away with before my heat pump starts to cycle as the radiators cant lose enough heat.
I suspect many people hit this problem.
My upper end will be evident after the winter 😉
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Hello Mars
4 bed large house in Portugal 16kW Mitsu. Still playing around and waiting to have buffer tank converted to volumiser.
Also pondering on PAR-WT50 wireless remote to let it do the thinking.
We’re on Vaillant’s 0.55 curve which means 42C at -2C and around 30C at an OAT of 15C.
The pump cycles about once an hour once it’s warmed up the house after set-back. The house upper limit is set at 21C (expanded mode for occasional solar gain) and the rooms are mostly at 20C (bedrooms less).
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@boycey the curves for your Ecodan should be published in your manual.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
The Ecodan WC curve doesn’t have presets like you see in other systems it’s fully customisable. So you can set the high and low end at any OAT and change the gradient as you see fit between those values
Like bontywood my low end doesn’t go below 32C to prevent cycling and is set at 45C at -10 which gives 37C at -2C
Posted by: @garyThe Ecodan WC curve doesn’t have presets like you see in other systems it’s fully customisable. So you can set the high and low end at any OAT and change the gradient as you see fit between those values
I had no idea that was the case. Thanks for the clarification.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 22 Forums
- 2,084 Topics
- 46 K Posts
- 50 Online
- 3,377 Members
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Surface mount or bury primaries for heat pump installation?
Current thinking is a Kronoterm Adapt. Doing the ground...
By tomasmcguinness , 57 minutes ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
It took me more than a few goes as well, plus some help...
By cathodeRay , 15 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 1 day ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 2 days ago
-
RE: Vaillant AroTherm Plus 7kW
@jamespa I have a hydronic baseboard heater in the kitc...
By Scalextrix , 2 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 3 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 3 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 3 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 4 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 5 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 6 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 6 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 6 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 6 days ago