Surface mount or bury primaries for heat pump installation?
Hi,
I'm in the early stages of planning my heat pump installation and whilst I know where the pump itself will be sited, I need to work out how to get the water into the garage. The path will see the pipes run up the side access and turn into the garage before getting connected to my heating. The route includes data and power cable.
I have two options.
1. I surface mount the primaries and run them along my neighbour's wall. I then have to either go under the paving or run the pipes up an over. I'll need a bracket of some sort between my neighbour's wall and the heat pump itself as I can't fix them to their failing timber fence.
2. I bury an instulated pipe that holds everything. The problem is that my side access is pretty busy underground with storm, waster and water main pipes. I'm told I should bury the pipe at 600mm, but I don't believe that's possible. At least not all the way. I have photos of this before it was backfilled.
What I want to know is why we can surface mount pipes in insulation, but we're required to put insulated pipes quite deep in the ground.
Has anyone got their primaries buried at a depth less than 600?
Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Next big project is a heat pump!
I think I would be wary of attaching my services to a neighbours property without some form of legal agreement to allow this and the required access to them in perpetuity. It also leaves the pipework at the risk of the neighbouring owner, or any future owner, making perfectly legal changes to their property which impacts on your pipe run.
@abernyte That is an excellent point. I hadn't considered that at all! I think I'll be burying a pipe 🙂
Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Next big project is a heat pump!
Posted by: @tomasmcguinnessHas anyone got their primaries buried at a depth less than 600?
Yes, ours are buried. 20m run from the heat pump to the utility room. Buried at roughly 50-60cm. I dug the trench myself with pickaxe and spade, because I knew there pipes (waste and gutter run off) underground.
The insulated heat loss pipe is quite pricey from what I can remember.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor My side access already contains services, so it's not easy. I think I'm going to have to shallow bury the pipe as it will need to go over some of the existing services. There is clay pipe down there and I don't want to disturb that.
Is there any solid guidance on buying pipes? I'm less concerned about the water and more about the electrical cable.
Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Next big project is a heat pump!
Broadly, the electrical cable will need to be either earthed armoured or in a duct to prevent mechanical damage. Both need to be marked with the required tape.
@tomasmcguinness, because ours runs under our driveway, and I was keen to avoid going too shallow in case it ever got damaged from heavy vehicle deliveries or future resurfacing.
As for guidance on insulation depth, the general 600mm recommendation is more about frost protection and physical damage prevention than some hard and fast requirement (as far as I know anyway). If you’re using decent insulated pipework and you’re not in an area prone to severe frost, going a bit shallower (like 300–400mm) in tight spots should be fine.
In your case, I’d agree that shallow burial with good-quality pre-insulated pipework is a practical way forward. You could always add some additional foam lagging and a protective duct over the section that runs shallower, just to give it a bit of extra mechanical protection.
On the electrical side, the key thing is to use appropriately rated armoured cable, preferably in its own duct separate from the primary pipe, especially if it’s running alongside heat-carrying pipework. It’s also worth checking the manufacturer’s guidance… some kits include pre-bundled solutions, while others require cables to be run independently.
Out of interest, which heat pump are you going with? And who’s installing it? Always helpful context for others following your project too.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@abernyte I was thinking of an SWA *in* the ducting. I'm looking at a combined water and electrical pipe (uponor or isoflow for example).
Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Next big project is a heat pump!
Current thinking is a Kronoterm Adapt. Doing the ground works myself (trench digging, base casting, that sort of thing). Then the professionals will finish the job.
Presently, I'm just exploring my options to get the water from the heat pump into the garage.
I'm constrained by the existing services, so I'm not sure how deep I'll actually manage.
Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Next big project is a heat pump!
@tomasmcguinness bold choice on the Kronoterm. Nice! Will be very curious to see how it performs. Have heard very good things about them.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@tomasmcguinness HI, The rules is a best practise, the heating pipes do not come under the same rules as services such as gas and mains drinking water.
Mostly its for frost protection but when the pipes are only just below the surface it is advisable to well insulate above 100mm thickness to slow losses and mechanically protect if possible.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @tomasmcguinnessI was thinking of an SWA *in* the ducting.
What you run the cable through will affect its current rating (and hence voltage drop).
SWA is intended for direct burial in the ground... the wetter the better.
You want any heat-loss from the cable to be conducted away into the surrounding soil.
Placing a cable inside an air-filled duct has the opposite effect.
The air acts as an insulating jacket. You've just made yourself an underground oven in a long tube. 😥
When you select the required cable size, you would usually enter the figures into an online calculator.
Here's one on the website for TLC-Direct.
That will tell you the cross-sectional area of the copper conductors you will require.
Secondly, if you have any services at shallow depth, where they might get hit by a garden fork for example,
place some basic paving slabs above them.
Although buried electrical cables must also have warning tape above them,
there's nothing like having the fork hit a 40mm piece of concrete slab to warn you there's something down there!
Save energy... recycle electrons!
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
2 weeks ago
-
Rodents! A word of warning for heat pump owners
1 month ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
2 months ago
-
Running my new Nibe ASHP efficiently
2 months ago
-
Weather compensation- why you should use it
2 months ago
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 458 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Underfloor Heating Installation Issues with Heat Pump
I'm going to install Thermacome ACOSI+ radiant ceiling....
By bobflux , 13 minutes ago
-
Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Hi all I'm having some trouble with a Grant ASHP and ...
By Renewables345 , 1 hour ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 1 hour ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
*** I now see @jamespa has already posted but will stil...
By cathodeRay , 3 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 3 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 4 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 8 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 15 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 15 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 19 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 19 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 22 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago