@transparent Noted re the lagging and yes the arrow is the flow sensor.  Have reseated this cable too just incase

 


   
ReplyQuote
(@ashp-bobba)
Estimable Member Member
343 kWhs
Expert
Joined: 3 months ago
Posts: 67
 

@netdonkey let me know the make and model of the cylinder and I will check the options for the format of pipework layout.

 

 


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
12955 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2278
 

Posted by: @ashp-bobba

I thought adding arrows to the picture may help as I was trying to work out which part of the circuit was doing what, something was not looking quite correct but I didnt want to work it out until I can see the cylinder diagram and confirmed the location identity of all ports on that multi port cylinder.

 

 

Oh, I'm all in favour of arrows to illustrate the flow @ashp-bobba
... especially if they're different colours.

In discussions with Councillors on my Local Planning Authority, we feel an annotated photo like that would satisfy a number of the requirements in Building Regs Part-L for site-specific information.

Part L 9

A photo with the valves identified would make it so much easier for a householder to be talked through an issue on the phone, post-installation.

This post was modified 3 months ago 2 times by Transparent

Save energy... recycle electrons!


   
ReplyQuote



(@ashp-bobba)
Estimable Member Member
343 kWhs
Expert
Joined: 3 months ago
Posts: 67
 

@transparent So, as you would have it, its the law for exactly this in commercial applications over a specific size job under CDM regulations. Commercially you legally have to produce a Building safety manual which is basically an abbreviated operation and maintenance manual but you also have to provide the O&M and well as the BSM which covers exactly what you are describing. The reason you need it commercially is because it serves the public so maintaining safety especially under the new building safety rules is as big a part of the job as is the understanding of the systems operated on that public building and its maintenance.

 

It would be magic if (as commercially) all valves were numbered, you were given a schematic showing all pipe connections and flows / sizes and a helpful snippet of the design detail, then someone like me could say, send me over the O&M and I will take a look.

 

What I do know is that currently Vaillant are offering all ASHP contractors / installers a full drawn schematic and design for Vaillant systems before you install, if so I dont see why these same designs given to the engineers cannot be passed on to the clients / end user for their records. I am not aware of other manufacturers offering this service yet, but thats not to say others dont, they may but I am not aware of it.

 

    


   
👍
2
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
12955 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2278
 

We could equally well say that "It's the law" for domestic installations...
... in that it's a requirement of the Building Regs!

But MCS seem to believe that their own regulatory framework should be the 'master',
and that Installers can self-certify their work to the LPA, who then send a 'Letter of Compliance' to the consumer.

That clearly isn't working. 😥 

 

I do actually tag each of my valves with a physical printed label,
but that's because this house is somewhat 'experimental' in nature.

PipeLabels

I'm trying to think what would happen if an ordinary heating engineer or electrician arrived here once I've gone gah-gah!

For most domestic Heat-Pump systems, I think a photo with numbers/letters next to each control would be heaps better than what's currently happening.
At least the Installer could then refer to them in discussions with the consumer or in documentation being left with them.

 

Save energy... recycle electrons!


   
ReplyQuote
(@johnr)
Estimable Member Member
736 kWhs
Joined: 4 months ago
Posts: 97
 

Posted by: @ashp-bobba

@netdonkey let me know the make and model of the cylinder and I will check the options for the format of pipework layout.

I think it's this cylinder https://www.telford-group.com/product/tempest-heat-pump-indirect-50l-buffer-copy (I've got one).

 


   
ReplyQuote
(@netdonkey)
Estimable Member Member
313 kWhs
Joined: 6 months ago
Posts: 56
Topic starter  

Posted by: @ashp-bobba

@netdonkey Ok. Can you give me the model and serial of the cylinder so I can work out the ports, I cant quite see the badge and different manufacturers use different ways for the bottom mounted buffers which this look like, I am not sure if I am placing the flows the correct way round. 

Pink is ASHP flow

Blue is ASHP return

Red Buffer F/R

Orange DHW F/R

Green Circle (assumed heating pump and connections)

 

Screenshot 2024 12 09 at 10.52.20

 

It's a tempest cylinder but I cant get enough angle to get the model/serial.  Took a few more pics as attached.  

IMG 4271
IMG 4270
IMG 4272

 Got the magnet opened and there was a spec of sludge but nothing untoward.  Heat pump started up and outlet temp got up to 22 then all of a sudden it dropped to 13.6. It then climbs back upo to the 20-23C mark then drops to 13C or around about that.

 


   
ReplyQuote
(@netdonkey)
Estimable Member Member
313 kWhs
Joined: 6 months ago
Posts: 56
Topic starter  

@johnr It certainly looks like it.  we are 220L


   
ReplyQuote
(@netdonkey)
Estimable Member Member
313 kWhs
Joined: 6 months ago
Posts: 56
Topic starter  

Outet temp got up to 28C a sec ago and then just dropped to 17C.  Do you think it's the ASHP that might be faulty?


   
ReplyQuote



(@netdonkey)
Estimable Member Member
313 kWhs
Joined: 6 months ago
Posts: 56
Topic starter  
IMG 4278
IMG 4279

On the 3 way valve the selector switchisn't all the way towards me.  Would that make a diff?  There is a small notch that says auto that the lever could come towards more.

 

It appears to be a honeywell box on the 3 way valve

This post was modified 3 months ago 2 times by NetDonkey

   
ReplyQuote
(@ashp-bobba)
Estimable Member Member
343 kWhs
Expert
Joined: 3 months ago
Posts: 67
 

@transparent agreed.

 

The labeling looks good.

 

        


   
ReplyQuote
(@ashp-bobba)
Estimable Member Member
343 kWhs
Expert
Joined: 3 months ago
Posts: 67
 

@netdonkey Most 3 port valves dont look like they are all the way over but they are. You can ignore that lever for now. 

It looks like the arrows I marked on the picture could be correct, the orange circuit according to the data sheet is connected to the DHW circuit for the cylinder, so heat should travel this way when in DHW mode.

The red circuit is going to the buffer mounted on the bottom which then feeds the heating circuit circled green.

What I am surprised with is if the ASHP is just feeding a 50ltr buffer on the bottom of the cylinder the flow should not be running so slow assuming the pipe run is in 28mm and no strainer in line and the filter was clean.

My next thing to check is, can you see what speed the main pump is on? 


   
ReplyQuote
Page 3 / 10



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security