Samsung 12kw cycling?
Hi
We have had our ASHP for 10 months now. And it cycles like crazy?
currently on Water pump 3 setting. Compensation set to 30/44
these are what I can see on monitoring tool and on controller:
the hive thermostat I have at high temp to try and stop it cycling but it’s not working that way. Above photos are from 18th October.. getting same today but with higher consumption jumps
Well if its a 12kW model and if Im reading your graph correctly its only using 2kW intermittently, I would guess that its struggling to generate a low enough power output. I had a similar issue with my 5kW model and discovered that raising the flow temperature to 38C at 17C outside on the weather compensation setting got rid of the cycling. It seems counter-intuitive but a higher flow temperature gives a bigger temperature difference between the emitters and the internal room temperature and so the heat pump can push more energy into the house. Try it, it might work and you have lost nothing if it doesnt 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody thank you I’ll give it a go. Just trying to find that balance between heating and economy.
today it seems to be spiking at 2.3-3.5kw so being a little hungry so need to nip in bud 😊
@lfranklin You may find that as the weather gets colder, it will stop on its own because the demand is higher, but it does look like it is cycling a lot which might not be good for the compressor long term.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodyWell if its a 12kW model and if Im reading your graph correctly its only using 2kW intermittently, I would guess that its struggling to generate a low enough power output. I had a similar issue with my 5kW model and discovered that raising the flow temperature to 38C at 17C outside on the weather compensation setting got rid of the cycling. It seems counter-intuitive but a higher flow temperature gives a bigger temperature difference between the emitters and the internal room temperature and so the heat pump can push more energy into the house. Try it, it might work and you have lost nothing if it doesnt 🙂
What happened to the IAT when you raised the WC curve?
@derek-m it went up marginally Derek, but to be honest I was happier with it slightly hotter. My appendages seem to get cold at anything under 22C 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Internal Air Temperature. We really shouldnt use these acronyms but we do 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
BTW, please let us know what happens after you try the changes out 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@derek-m it went up marginally Derek, but to be honest I was happier with it slightly hotter. My appendages seem to get cold at anything under 22C 🙂
Yes, many of us prefer the IAT slightly warmer. One of the pleasures of growing older. 🙄
Of course increasing the IAT, increases the heat loss, which in turn increases the demand on the heat pump, and could possibly increase the electrical energy consumption.
This is one of the areas I have been investigating to see what may be the most efficient and cost effective method of operation.
When you raised the WC curve, did your heat pump run continuously, or did it run for a longer period and then stop for a longer period? Did the electrical energy consumption increase or decrease?
Whilst all heat pumps are likely to cycle at some point during milder weather conditions, I suppose it is a matter of finding the settings which work best for your particular circumstances.
Is it just a matter of finding the OAT at which your heat pump pulls back to the minimum LWT, and runs continuously, without cycling. Then set these parameters at the mild weather end of the WC curve. It is still important to get the slope of the WC curve correct for colder weather operation.
An alternative method I have suggested in the past, is to raise whole WC curve using the offset by 1C or 2C, and then use a room thermostat to start and stop the heat pump at a temperature 1C higher than desired. The heat pump is therefore likely to run longer at slightly higher loading to raise the IAT, then stop for a lengthy period of time while the IAT falls back to the thermostat setting.
@derek-m yes, I managed to get it to run continuously. You can see the difference if you look at my graphs for the last couple of weeks here:
https://emoncms.org/app/view?name=RoseCottageHeatpump&readkey=1a60decebfd925c412d19c85fb1adacc
I also raised the temperature of the high end of my WC from 15C to 17C which should have had the effect of raising my flow temperature slightly again say at 12C OT.
It all seems to work nicely at the moment, so roll on the cold weather and Ill see how the low end of the WC works 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 37 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: No-code, plug-and-play monitoring for your heat pump
By Grantmethestrength , 18 hours ago
-
@eliuccio good to hear you’re happy with the install. A...
By Mars , 1 day ago
-
RE: Is this just haze or something more?
I am not a scientist nor a meteorologist and I know the...
By Toodles , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
It will improve performance, but by how much depends on...
By Brendon Uys , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 3 days ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 3 days ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 3 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 4 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 4 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 4 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 4 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 5 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 6 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 1 week ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 1 week ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 1 week ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 1 week ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago