Replacing knackered oil boiler with ASHP - Perthshire
Interested in red flags, guidance on replacing 26Kw oil-boiler with in-boiler 127l HW tank, with ASHP, 300l tank.
Timber frame with block exterior, 275sq.m, bilt 1999, UFH both floors with room stats in all but 3 bathrooms which are always open. Original heat loss as designed was ca. 18kW. two log burners, one in front hall one in large living room upstairs. Oil aga for cooking always on.
Two suppliers quoted: one calculated heat loss at 13.3kW, the other at 18.94kW so ASHP at 16kw and 2x19kW.
Both quote for buffer tank.
I think I would be tempted to do my own heat loss assessment. Using heatpunk

or you could try this simple one https://openenergymonitor.org/tools/SimpleHeatLoss.html
There is a substantial difference between the two you have. Also i would look at possible easy insulation upgrades to reduce it.
Also I would ask the installers to justify why they think a buffer is necessary. Much better not to have one if possible as it will lower your efficiency.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Thanks - will have a go at the calcs as I've the data that they used. I've asked about buffer today and waiting on a reply.
@dowallydrifter if you had oil usage figures and didn’t use the wood burners much you could use that as well to get a sanity check.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @dowallydrifter@bontwoody Thanks - will have a go at the calcs as I've the data that they used. I've asked about buffer today and waiting on a reply.
You will not need a buffer if the system is correctly installed. I will connect you with two excellent installers shortly that cover your area so you can get comparative pricing.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @bontwoody@dowallydrifter if you had oil usage figures and didn’t use the wood burners much you could use that as well to get a sanity check.
Totally agree and I would be suspicious of the high loss estimates. Even if you did use the wood burners and know how much wood you burned you could add that in. I am sceptical about even 13kW unless it's poorly insulated. Any sanity check you could do would be a good idea
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@bontwoody Thanks. Oil figures available but can't isolate aga from the dead boiler usage unfortunately.
@jamespa oil varies 2500-4000 litres a year for boiler and aga, ca. 4 cu.m wood p.a. Original design for UFH showed outside walls with K=0.45 W/sq.m/K roof K=0.24 W/sq.m/K, and windows at 3.5 W/sq.m/K . Independent engineer in 1999 when built reckoned 18Kw at -5degC. Not trivial to add wall insulation to timber frame. Loft insulation doable to some (bats permitting!) more constrained access in rest of roof.
Posted by: @dowallydrifterNot trivial to add wall insulation to timber frame
It is pointless adding EWI to a timber framed house with external block rainscreen. The movement of air around the timber frame inside of the block outer makes adding EWI irrelevant.
Also in Perthshire with leaky timber frame in an exposed site.
results from the simple calculator point toward 16.5kW heat pump plugging in U values from original docs. walls 0.45, roof 0.24, windows 3.5 - the simple calc will be ignoring the large lounge with vaulted ceiling i guess.
Posted by: @dowallydrifter@jamespa oil varies 2500-4000 litres a year for boiler and aga, ca. 4 cu.m wood p.a. Original design for UFH showed outside walls with K=0.45 W/sq.m/K roof K=0.24 W/sq.m/K, and windows at 3.5 W/sq.m/K . Independent engineer in 1999 when built reckoned 18Kw at -5degC. Not trivial to add wall insulation to timber frame. Loft insulation doable to some (bats permitting!) more constrained access in rest of roof.
Ive done some rough calculations on those figures after trying to add in the wood and Ive come up with a demand of about 19.5kW at -3C to achieve 21C internal temperature (using the 4000 liter figure), so if James concurs then the original estimate isn't far out. (Although this drops to 13kW using the 2500 liter figure)
We like our living room warm (22.5C) so the way I have approached insulation is to concentrate on that room. Insulated plasterboard has worked very well on both the walls and inaccessible loft areas.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 40 Online
- 5,673 Members
Podcast Picks
Latest Posts
-
Thanks. No buffer. Def controlled by the Samsung. Therm...
By Profzarkov , 56 minutes ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 1 hour ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 3 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
A bit of a follow up on the progress of the Ecodan pump...
By ThunderMink , 4 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 5 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 6 hours ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 16 hours ago
-
My Samsung Gen6 (probably same controller as yours) onl...
By Old_Scientist , 1 day ago
-
@drei When I was in local government we were of cours...
By JamesPa , 1 day ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 2 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 2 days ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 2 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 3 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 3 days ago