Primary Pump positioning for Samsung Gen6 system

12 Posts
4 Users
5 Reactions
214 Views
(@ecobaker)
Estimable Member Member
351 kWhs
Joined: 7 months ago
Posts: 39
Topic starter  

I'm about to have my LLH removed, and to take my system to an open loop with one pump. Currently I have two pumps both either side of the LLH, both of them fitted to the return and not the flow. See the attached system diagram. 

My questions is, all info i've found from Joule, Midsummer etc shows the primary pump has to be on the flow, not the return. Should I swap the pump to the flow when I remove the LLH or does its position make no difference?

Thanks for any advice.

Screenshot 2024 03 27 at 20.26.11

 

Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
👍
1
Quote
(@johnmo)
Prominent Member Member
2092 kWhs
Joined: 2 years ago
Posts: 406
 

It should make zero difference if on the return or supply pipe. Convention always puts the pump on the lowest temperature side of the system.

I quickly did a Google search and the first image I found was this, with the pump on the pump on the return side

image

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
(@heacol)
Noble Member Contributor
2127 kWhs
Expert
Joined: 3 years ago
Posts: 351
 

Hi

It does not matter which side the pump is on, it is a circuit. You must however make sure that you have enough open zone system volume and flow. You will need at least 50 liters of open zone system volume. A single panel radiator, 0.6m high and 1 m long will hold about 3 liters, if you do not have enough, you may need to get a volumisor and install it on the flow, not the return. Remove all control from all common area radiators and only control your bedrooms. If possible, move the controller to the hall or somewhere where it is not influenced by other heat sources. As you are not controlling the Delta T, your flow rate must be about 14.5-15 l/min (For your 8 Kw unit), no more. You may need 2 pumps to achieve this but try with 1 first.

This should work well.

Brendon

This post was modified 1 month ago by Brendon Uys

Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas


   
👍
1
ReplyQuote



(@ecobaker)
Estimable Member Member
351 kWhs
Joined: 7 months ago
Posts: 39
Topic starter  

@johnmo Thanks, I hadn't seen that set up diagram before

Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
ReplyQuote
(@ecobaker)
Estimable Member Member
351 kWhs
Joined: 7 months ago
Posts: 39
Topic starter  

@heacol Thanks for the info. I've currently hot 48 litres in my radiators, so a bit below 50 but the documentation for Samsung 8kw says 30 is the minimum, so I think it should be okay. Also I'm planning at least one new radiator and one swap to a largeer one. 

I've got a pump with variable speed, so I think I can adjust that to get the right flow rate once I've made the changes. 

Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
ReplyQuote
(@johnmo)
Prominent Member Member
2092 kWhs
Joined: 2 years ago
Posts: 406
 

Posted by: @ecobaker

Samsung 8kw says 30

That's really for defrost support. 50L would be to limit short cycling. More volume the better and will lead to longer cycle times and overall better CoP.

Have you considered leaving the LLH there? It provides a point to remove air and catch debris. Just plumb across the flow side only. So remove secondary pump and return connections from the low loss header and allow the return to by pass around the LLH. Leave the flow connected.

Less work, add some volume, retain air bleed and debris catcher. No loss of efficiency, one pump removed.

 

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
(@bontwoody)
Noble Member Contributor
3768 kWhs
Joined: 3 years ago
Posts: 545
 

Posted by: @ecobaker

I've got a pump with variable speed, so I think I can adjust that to get the right flow rate once I've made the changes. 

The Samsung Gen 6 supports Pulse Width Modulation control of pump speed if you have a pump that supports it, so it sets the speed that is most appropriate at that particular time.

I made a mistake of initially buying the wrong pump, but rectified it later and it works well now. My blog for April 2023 describes a lot of the things to look out for if you want to go down that route.

https://thegreeningofrosecottage.weebly.com/blog/archives/04-2023

 

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@ecobaker)
Estimable Member Member
351 kWhs
Joined: 7 months ago
Posts: 39
Topic starter  

@johnmo I had considered leaving the LLH in, but wouldn’t it be best to by pass the flow and leave the return connected to it for catching debris from radiators? 

My other option was to take it out completely, but add an automatic air valve at the highest part of the pipe work and a mag filter on the return to the heat pump. 

Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
ReplyQuote
(@ecobaker)
Estimable Member Member
351 kWhs
Joined: 7 months ago
Posts: 39
Topic starter  

@bontwoody I don’t have the PMW control pump just the Auto with the ability to adjust the flow rate on the pump. Changing it to an PMW pump is on the list, but a bit further down than a few other things. I’m going to manualy adjust the pump I have once the set up changes have been made and see what performance I get. I’ve got at least one radiator adjustment to make as well before the pump gets changed. Thanks for the blog posts, lots a great info there.

Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
👍
1
ReplyQuote



(@heacol)
Noble Member Contributor
2127 kWhs
Expert
Joined: 3 years ago
Posts: 351
 

@ecobaker Your system volume will be fine, just make sure you get the right flow rate with all TRV's open and at least 8 l/min with all closed. Leaving the LLS header in is an option but on the flow. It will benefit you more there. Some older GEN 6 controllers do not have the software for PWM pump control, running a slightly lower flow rate than peak optimum is a good compromise but not as good as PWM.

This post was modified 1 month ago by Brendon Uys

Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas


   
🤩
1
ReplyQuote
(@ecobaker)
Estimable Member Member
351 kWhs
Joined: 7 months ago
Posts: 39
Topic starter  

So I made the switch of pumps and took out the LLH (also added a magfilter) the pump I put in is a ump3 flex 15-70 130, got it all wired up and the system working.

The problem is, although COP is fine between 4.0 and 4.1, I'm getting a lot of cycling when the heating is on, and two radiators on one branch of the heating are not getting hot. Could this be an under powered pump? Maybe I could try taking the PWM cable out and just running the pump at full speed. According to my flow meter I'm getting 18 - 19 l/m when it's operating. 

Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
👍
1
ReplyQuote
(@bontwoody)
Noble Member Contributor
3768 kWhs
Joined: 3 years ago
Posts: 545
 

@ecobaker if you are sure that the two radiators dont have an airlock, then it might just be a matter of balancing all the radiators to ensure that they all get adequate flow. The cycling is probably due to not being able to lose enough heat from your radiators for the heat pump to be able to run at its lowest setting. Getting the two radiators working will help that but you may have to look at raising the flow temperature slightly if it still occurs.

Ive played around quite a bit in my blog and have now just about got it working as I want.

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote