NIBE heat pump comms error when freezing
Hi
i have a nibe f2040 12 which was installed in 2015.
three years ago it started to shut itself down when the outside temp fell below freezing. The error was BT301 “comms error slave 1”.
i reset the alarm and if the temp had climbed above freezing the pump would run again until the next cold spell. If it was still below freezing the pump would restart and run through the heating cycle, the hot water cycle and then start the defrost cycle. After a couple of minutes the alarm would go with the same error message.
i called a local recommended NIBE firm (my installer was a family firm who had since retired). They came out, needless to say the fault was not present when they called, and they could not replicate it so couldnt fix it.
the pump ran ok all through the next summer until freezing conditions occured again. Same error!
and again last summer, until this latest cold snap came. Same problem. In the meantime i had contacted nibe technical dept who suggested it could be an error on PWB1 or with the comms cable. This time i contacted another local nibe engineer who came out when the weather was not freezing. Needless to say he could find no problem. He suggested that the fan motor might be struggling, but recommended i recontact nibe to get an engineer out. However they will not attend fir breakdowns or diagnosis, as i am out of warranty.
i know from the time that the pump runs when i reset the alarm that there is something not right with the defrost cycle (which is pretty obvious!) but no one seems to know what.
has anyone else experienced this and can anyone help please
I have just seen your post. NIBE installers are few and far between and communication with NIBE isn't easy. I was looking at the service plan info on their website and came across this document about one-off chargeable call-outs which applies if you are not under warranty or not subscribed to a service plan. I should imagine it will be expensive. It looks like when you were in touch they didn't suggest this option.
I hope you find a solution.
- 26 Forums
- 2,228 Topics
- 49.5 K Posts
- 99 Online
- 5,890 Members
Join Us!
Podcast Picks
Latest Posts
-
-
RE: Twin 10kw Grant Aerona Volumiser Tanks using lots of power
The Grant Aerona3 external volumisers are insulated uni...
By Grantmethestrength , 4 hours ago
-
RE: How good is the app support for your heat pump?
The Bluetooth signal does not reach due to the distance...
By Batpred , 4 hours ago
-
Samung 16kw 5 months in - Happy with heat and DHW but some questions
Where to start? In brief we are happy with the system...
By DowallyDrifter , 5 hours ago
-
Question about Heating Pump Operation mode – Ecodan FTC6 v20.06
I have a Mitsubishi Ecodan EHST20D-YM9D with PUHZ-SWM80...
By Johj45 , 6 hours ago
-
RE: Electricity price predictions
Currently we are a net importer of electricity, and one...
By Jeff , 6 hours ago
-
RE: Replacing knackered oil boiler with ASHP - Perthshire
@jamespa just confirming that after 5months with the 16...
By DowallyDrifter , 7 hours ago
-
RE: How to increase DHW water temperature on Samsung Gen 6 Control Panel
Im just in the process of connecting up my mixergy cyli...
By bontwoody , 14 hours ago
-
Unless anyone can tell me differently, there appears to...
By DowallyDrifter , 16 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
I run my Vaillant on either expanded mode (either end o...
By JamesPa , 18 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
on a facebook thread someone has comented to the effect...
By AdamK , 1 day ago
-
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
Wanted to add an update. As I am running HomeAssistan...
By bubuontheweb , 1 day ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
You are correct you dont need the second pump if there ...
By JamesPa , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
From my experience with inverters from different Far Ea...
By Transparent , 1 day ago
-
@bontwoody Thank goodness you are ‘back on-line’ so to ...
By Toodles , 1 day ago
-
RE: Automation options to maximuse efficiency & ToU tariffs
@majordennisbloodnok Seems reasonable. It would be m...
By Batpred , 1 day ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas OK Thanks. Will do.
By bontwoody , 1 day ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
@transparent Thank you for a very comprehensive, tim...
By Batpred , 2 days ago
-
RE: Isolating the system for a planned power cut
@transparent 😊 I may have lost you there.. I ...
By Batpred , 2 days ago