New Samsung 12KW Heat Pump Help

31 Posts
6 Users
6 Reactions
817 Views
(@dinhp)
Eminent Member Member
121 kWhs
Joined: 2 weeks ago
Posts: 13
Topic starter  

Hi,

We’ve had a new heat pump fitted, a 12KW Samsung, and our COP is 2. We did have a cold spell but it’s been fairly mild now 7-14 degrees. 

It’s been fitted via a grant so we didn’t have much control over it and the installers seemed more set up for gas installs and had never done a project as big as ours as it was a first time central heating. I’ve been trying to learn as much as possible but it seems a fine art! It wasn’t set up for water law/weather compensation and was set to heat 65 degrees. I’ve amended this now to water law -3/45 and 15/25 and it’s keeping the house a steady 20 degrees. I’m not sure what to do with DHW it was set to constant eco 55 with a once weekly 60. I’ve changed this to eco schedule for 50 at 2x2hr periods a day with a once weekly 60. COP is still around 2. Just wondering what the next things to check would be?

I’ve contacted a local heat pump engineer with good reviews to come and have a look at the whole set up but it’s a 4 week wait and at the current rate it will be a £700 electric bill I’d like to get down if possible in the meantime. 

Thanks in advance


   
Quote
Mars
 Mars
(@editor)
Illustrious Member Admin
22949 kWhs
Veteran
Joined: 4 years ago
Posts: 2754
 

Setting the heat to a fixed 65°C is shocking, so it’s great to hear you’ve switched to weather compensation – definitely a step in the right direction. That said, achieving a COP of 2, even with this week’s cold temperatures, is still very low. There’s likely another issue impacting your system’s efficiency that needs addressing. There are plenty of users on these forums with Samsungs, so helpfully they can shed some light. A photo of the plant room might help!

As for hot water, it really depends on your household’s usage patterns. For us, working from home 99% of the time, we’ve set our hot water to 45°C with a 15°C differential. This means when the tank temperature drops to 30°C, it reheats back to 45°C. It suits our needs perfectly.

Regarding the legionella cycle, the “standard” weekly routine can be overkill for some households. If you’re regularly emptying your tank, doing the cycle fortnightly is usually sufficient, provided you’re confident about usage and water turnover.

PS - just for reference, was this an ECO4 grant?

This post was modified 2 weeks ago by Mars

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
4397 kWhs
Joined: 3 years ago
Posts: 641
 

@dinhp

I have a Samsung, so happy to answer any questions I can. It seems you have done an excellent job of altering the settings and I cant believe that the COP hasnt changed because of that. Could you be reporting the average COP over a longer period that is overly weighted by the earlier settings?

You might want to look at tariffs that will help you run more cheaply and time Hot water runs in cheap periods if you can.

Ive also mentioned the advantages of having monitoring equipment in another thread. You can soon see how this pays back when you are faced with a £700 bill.

This post was modified 2 weeks ago by bontwoody

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@dinhp)
Eminent Member Member
121 kWhs
Joined: 2 weeks ago
Posts: 13
Topic starter  

@editor thank you I appreciate your reply. So it doesn’t sound like the DHW set up alone would be the cause of the low COP?

I’ve attached some photos if there is anything glaringly obvious that needs addressing I’d be grateful for anyone pointing it out. They are coming back to replace the external trunking which is too short and I have a list of things to go back to them with so far

- the pipe work bending out of the back of the heat pump and if that’s an issue

- the condensation pipe (I think that’s what it is?) is just drilled through existing slab isn’t draining away - we asked about if a soak away/base was needed prior to install but told it wasn’t necessary 

- to find out if there is glycol in the system, I’m not sure if there is an antifreeze valve on one of the pipes  but I thought 2 were needed

All my learning has been from Google and YouTube over the past week or so I’ve not really got much of a clue what I’m looking at. It was the home upgrade grant and they were a nice bunch but I’m a bit concerned about the level of experience with heat pumps, so I’d like an independent engineer to have a look for peace of mind. But the more I can learn the better too.

IMG 8649
IMG 8645
IMG 8644
IMG 8648
IMG 6828

 

This post was modified 2 weeks ago by dinhp

   
ReplyQuote
(@dinhp)
Eminent Member Member
121 kWhs
Joined: 2 weeks ago
Posts: 13
Topic starter  

@bontwoody hi thank you for your reply! I’ve attached our consumption/generation. It’s not been in very long - the first night it used a lot before we adjusted the settings. Yesterday it did run a legionella cycle so that may skew that one but nothing today. Hopefully I’m working out the COP right! Or hopefully I’m not and it’s better than I think 🤣

IMG 8678
IMG 8679
IMG 8683
IMG 8682
This post was modified 2 weeks ago by dinhp

   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
4397 kWhs
Joined: 3 years ago
Posts: 641
 

@dinhp 

Ive  worked out the daily COP below and added my Outside Air Temperature, yours might be quite a bit cooler depending on where you live:

image

So, the relatively good news is that you achieved a COP of 3.32 on the 23rd, which isn't great but is better than the 2.19 you had initially. The better news is that Ive calculated my COP over the same days using the Samsung figures and compared that to my COP reported by my in-line certified heat meter. The Samsung figure are consistently only 80% of the actual figure.

That suggests you may be doing better than you think, particulary if its cold where you are. Looking at my figures, it seems that Samsung are over reporting the electricity used and under reporting the heat produced.

image

This is the sort of information you get with Open Energy Monitor, in my view worth every penny as the savings you can make by knowing what is actually happening are substantial.

image
image

With respect to your installation I would be making sure that any bare pipework outside was insulated. The ends of the flexible hoses always seem deficient in my experience.

It looks like you have one anti-frost valve, so you wont be using antifreeze. 2 valves is common, but i have seen one fitted before and some people dont even bother with that given the highly unlikely event of sub-zero temperature and no electricity for an entended period. (Unless you live in Scotland!)

This post was modified 2 weeks ago 3 times by bontwoody

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
🤩
1
ReplyQuote



(@dinhp)
Eminent Member Member
121 kWhs
Joined: 2 weeks ago
Posts: 13
Topic starter  

@bontwoody thanks so much for taking the time to do that. Our temps are fairly similar, the day with a COP above 3 we actually set the flow temps to a Samsung manual online of -2/38 and 15/48. We moved it down to -3/40 and 15/25 after reading around online at what others were using and it has kept the house at a good temperature at the lower settings but it looks like the COP is worse rather than better, I’m sure I’m oversimplifying though. 

I will definitely have a look into the monitors and we’ve asked for a smart meter to hopefully get onto a better tariff thank you. 

Will do and good to know re the anti frost valve. 


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
4397 kWhs
Joined: 3 years ago
Posts: 641
 

@dinhp dont have second thoughts about your weather compensation setting. Lower is better for COP.

Im not sure what you mean by:

Samsung manual online of -2/38 and 15/48

a flow temperature of 38C at -2C outside sounds reasonable but then 48C at 15C outside is the wrong way around. I would try 33C at 15C outside as you probably wont be able to go any cooler than 33C without cycling badly and you may have to go up slightly to 34 or 35C.

If you keep an eye on if the heat pump keeps stopping and starting often that will give you a hint that it is cycling. Have a look at my blog if you want to see how I run mine with a mixture of weather compensation and a single thermostat.

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@dinhp)
Eminent Member Member
121 kWhs
Joined: 2 weeks ago
Posts: 13
Topic starter  
@bontwoody sorry wrong way round -3/48 and 15/38 - I’ll try bring up the 15 C setting and keep an eye out for cycling. 

I’ll give it a read - thanks again

   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
22949 kWhs
Veteran
Joined: 4 years ago
Posts: 2754
 

@dinhp, I reached out to one of the top installers in the UK for their insights on your post and the photos you provided and they said it’s actually quite difficult to make a system run this inefficiently. According to @bontwoodyl at least the numbers are a tad better.

Here’s the installer’s feedback, which I’ve expanded upon to provide clarity and guidance, and which you can share with your new installer:

Placement of the antifreeze valve: The antifreeze valve should always be positioned at the system’s lowest point. From the pictures, it’s clear this hasn’t been done, which could lead to operational inefficiencies or future maintenance issues.

Water pooling on the floor: The water you’re seeing on the floor is likely condensation from the heat pump. This should have been directed to a drain or soakaway as part of the installation. Improperly managed condensation not only impacts efficiency but can also cause unnecessary wear on the unit and surrounding areas.

Efficiency requirements under eco schemes: Even under ECO-funded installations, there’s a minimum efficiency requirement. For MCS installations, the current minimum Seasonal Coefficient of Performance (SCOP) is 2.8. If your system is underperforming significantly, you should raise this with the installation company and escalate it to the relevant competent persons scheme if they fail to act. It’s not likely to lead to anything meaningful but worth a try. Might be worth reporting them to RECC or HIES depending on who they’re registered with.

Likely root cause: The main culprit here is almost certainly the system’s control setup. According to the installer, correcting the controls alone could provide a 50% improvement in efficiency without any mechanical changes. 

It’s frustrating to see installations like this, especially when they fail to meet even the basic standards. Let me know how you get on.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@dinhp)
Eminent Member Member
121 kWhs
Joined: 2 weeks ago
Posts: 13
Topic starter  

@editor thank you so much for this and please thank the installer for me - I’ll raise this with our installer and hopefully we can get somewhere. 

Hopefully I can come back and update with some improved figures!


   
ReplyQuote
(@dinhp)
Eminent Member Member
121 kWhs
Joined: 2 weeks ago
Posts: 13
Topic starter  

Any advice on if I should adjust the weather compensation temperatures further yet and if so the best way to do this? Do you lower both ends or just start with one? The 23/11 looks to be our best day which makes little sense from what I’ve read about online and lowering the temperatures to improve efficiency. 

IMG 8727

I think our Delta T is lower than it should be usually at 1 sometimes 3 - not sure how to rectify this or if I need to if anyone has any advice on that it would also be appreciated. All TRVs are set to 5. The house is holding its temp 21 in living areas and 18/19 in bedrooms - we’ve not limited any areas the radiators were designed smaller for those areas I think. There is one third party thermostat which is set up to 24 in the living room just to stop the pump turning off. 

Currently waiting on our installers to get back to me on the poor efficiency and other points  

Thanks!


   