Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
My Mitsubishi ASHP has used 1078kWh from 25 November to 31 December – Help please
Posted by: @harriupAt the bottom of page 6 it states the water flow rate range is 10.0 to 24.8 l/m. Similar to mine, though I have also seen the tank installation manual be a bit more specific that the flow rate should be 24l/m. Not sure what to make of that difference. There is discussion in other threads about altering the flow rate to manage the difference between flow and return temperatures to 5°C, but if the manifold temps of 28 and 21 are typical then you have a slightly too large difference, which is to be expected if the flow rate is lower than it is meant to be.
Hi @Harriup
i thought I ought to add some comments on this for Sarah to consider.
Theres a good reason why there is a flow rate range quoted, and probably other reasons too.
It was generally believed in an earlier thread (Keystone COP) that Ecodan does not have an internal pump to regulate deltaT so there are 2 things that can control it. 1. Adjusting the flow rate via the circulation pump of the primary flow and primary return and 2. The internal modulating electronics which cannot regulate the circulating pump. In other words the ecodan operates at a constant flow rate depending on the chosen set pump speed.
A flow rate must therefore be measured on the return primary pipe since that is precisely en-route back to the heat pump and will give a near accurate measurement of flow through the heat exchanger. (I would say it’s essential to check this before any adjustment of flow rate)
another thing to point out is that a 28 to 21 differential is only 7c which is quite common when the hp is still settling down. I’ve noticed it fluctuates all the time between 3c and 8c and when it starts up it can be more.
So a flow rate of 13LPM is within the acceptable band of the ecodan 8.5 provided it is being measured in the correct place in the circuit. But if the temperature difference never settles close to 5c then a slightly faster pump speed will lower the temperature difference. However there are other issues such as balancing flow rates between the primary loop and other heating circuits so this kind of adjustment really needs to be done by a professional.
Hope this helps
@sunandair hi - yes that does help and again makes sense that it's set by the gauge on the pump itself - i.e. that is the maximum it will flow. I've had a manic week this week - but I need to look at the manifold on a regular basis for the living area to see what the return is. The thermostat is set to 18 for the living area - but rarely gets to that, unless there is solar gain - for the past two days it is still 17 degrees at 18:00 - when it was 16 degrees at 09:00. In all honesty this could be what I have to live with and it doesn't feel cold. The other 2 zones always get up to their set temp - although their set temps are 16 (bathroom area) and 17(bedroom area). Everything generally is SO MUCH BETTER since I first found this forum 🙂
- 26 Forums
- 2,670 Topics
- 62.5 K Posts
- 118 Online
- 7,079 Members
Join Us!
Directory
Degrees of Separation
Latest Posts
-
RE: MCS 2.0 - Changes in January 2025
It strike's me that there's various improvements which ...
By Temperature_Gradient , 51 minutes ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@majordennisbloodnok The M5StickC turned up...
By Bash , 1 hour ago
-
Hi Everyone, I wanted to share something with you all...
By ASHP-BOBBA , 2 hours ago
-
RE: Load Shift and Lifestyle Shift Complete - our journey has ended, for now
Great journey @allyfish. Totally relate to your experie...
By ChandyKris , 4 hours ago
-
-
Many messages back and forth later… GOV UK One Login ...
By Toodles , 5 hours ago
-
No. The shape of the waveform has no bearing on the d...
By Transparent , 6 hours ago
-
RE: Say hello and introduce yourself
@will-h, this isn't a dig but we would prefer if anyone...
By Majordennisbloodnok , 7 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
Thanks Tim. That SolarEdge data also shows voltages a...
By Transparent , 10 hours ago
-
RE: Configuring third party dongle for Ecodan local control
A few notable developments: I'm working through addin...
By F1p , 23 hours ago
-
RE: Vehicle-to-Home with a Heat Pump: Is the Technology Ready and Which EV Should I Buy?
Vehicle to Grid is the further step and here is the IEA...
By Judith , 23 hours ago
-
RE: Renewables & Heat Pumps in the News
Where the grid is heading? Input from Kraken.
By Jeff , 1 day ago
-
RE: Plug and play solar. Thoughts?
@jamespa Yes, unfortunately our policymakers learned...
By Batpred , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
@l8again It seems you did very well. With our HG h...
By Batpred , 2 days ago