Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
My Mitsubishi ASHP has used 1078kWh from 25 November to 31 December – Help please
Posted by: @harriupAt the bottom of page 6 it states the water flow rate range is 10.0 to 24.8 l/m. Similar to mine, though I have also seen the tank installation manual be a bit more specific that the flow rate should be 24l/m. Not sure what to make of that difference. There is discussion in other threads about altering the flow rate to manage the difference between flow and return temperatures to 5°C, but if the manifold temps of 28 and 21 are typical then you have a slightly too large difference, which is to be expected if the flow rate is lower than it is meant to be.
Hi @Harriup
i thought I ought to add some comments on this for Sarah to consider.
Theres a good reason why there is a flow rate range quoted, and probably other reasons too.
It was generally believed in an earlier thread (Keystone COP) that Ecodan does not have an internal pump to regulate deltaT so there are 2 things that can control it. 1. Adjusting the flow rate via the circulation pump of the primary flow and primary return and 2. The internal modulating electronics which cannot regulate the circulating pump. In other words the ecodan operates at a constant flow rate depending on the chosen set pump speed.
A flow rate must therefore be measured on the return primary pipe since that is precisely en-route back to the heat pump and will give a near accurate measurement of flow through the heat exchanger. (I would say it’s essential to check this before any adjustment of flow rate)
another thing to point out is that a 28 to 21 differential is only 7c which is quite common when the hp is still settling down. I’ve noticed it fluctuates all the time between 3c and 8c and when it starts up it can be more.
So a flow rate of 13LPM is within the acceptable band of the ecodan 8.5 provided it is being measured in the correct place in the circuit. But if the temperature difference never settles close to 5c then a slightly faster pump speed will lower the temperature difference. However there are other issues such as balancing flow rates between the primary loop and other heating circuits so this kind of adjustment really needs to be done by a professional.
Hope this helps
@sunandair hi - yes that does help and again makes sense that it's set by the gauge on the pump itself - i.e. that is the maximum it will flow. I've had a manic week this week - but I need to look at the manifold on a regular basis for the living area to see what the return is. The thermostat is set to 18 for the living area - but rarely gets to that, unless there is solar gain - for the past two days it is still 17 degrees at 18:00 - when it was 16 degrees at 09:00. In all honesty this could be what I have to live with and it doesn't feel cold. The other 2 zones always get up to their set temp - although their set temps are 16 (bathroom area) and 17(bedroom area). Everything generally is SO MUCH BETTER since I first found this forum 🙂
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 298 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 5 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 5 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 6 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 6 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 7 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 7 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 8 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 10 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 11 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 13 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 15 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 19 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago