Mid terrace - ASHP Install location
Hi all (first post),
I've had a survey and quote for an ASHP in our retrofitted 1907 house.
Two different companies have spec'd 5kW size heat pumps.
The challenge I'm having at the moment is locating the heat pump, given that they need maitenance/performance clearances, and R290 needs safety clearances. There are sub floor vents in places and multiple drains.
I've sketched up the outside area I had envisaged it going, though I'm struggling to find an R32/R290 ASHP that would suit. (Images attached).
Thought i'd use the forum hive mind to get any reccomendations or considerations.
Cheers!
All I can say from a very quick look, the first issue that hits me is space. If you are considering siting your ASHP in that alley outside the window in your picture you will experience serious issues. That site looks totally unsuitable.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @samiebon1Hi all (first post),
I've had a survey and quote for an ASHP in our retrofitted 1907 house.
Two different companies have spec'd 5kW size heat pumps.
The challenge I'm having at the moment is locating the heat pump, given that they need maitenance/performance clearances, and R290 needs safety clearances. There are sub floor vents in places and multiple drains.
I've sketched up the outside area I had envisaged it going, though I'm struggling to find an R32/R290 ASHP that would suit. (Images attached).
Thought i'd use the forum hive mind to get any reccomendations or considerations.
Cheers!
-- Attachment is not available -- -- Attachment is not available --
I would be asking my installer (both installers) to tell me where they would install it since they are quoting.
Then take them to task on why they would put it where they recommend.
Regarding limitations on position of R290… this is an outdated law which urgently needs to be reviewed. It’s because the gas inside a R290 is propane so it falls into gas safety requirements of any high volume outdoor gas appliance which might spring a leak near an opening window or door. However there is such a small and finite amount of gas in the heat pump that it doesn’t really match the reason for the law.
however there are all sorts of environmental and performance reasons why the R290 is more superior. It’s just that you are an early adopter with specific site limitations so you are breaking new territory.
post edit
Another major consideration is your access to your own garden without a cold blast of air in the area you like to occupy. Decide what you don’t want to compromise on. Convenient and comfortable access to your outdoor space is, or should be an important consideration.
At a quick glance @samiebon1 I would be inclined to put the heat pump at the end of the alley (as far away from your window as possible), or even around the corner that we can’t see in the photo, where the air movement will be greater.
The R290 law as SUNandAIR says needs urgent changing, but that doesn’t help you.
Did your prospective installers not give you any siting suggestions?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Maybe consider a first floor wall mounted design. Check out Glyn Hudson’s self install on YouTube which looks like a similar position.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Our installation has similar restrictive drains, doors and windows which was a pain; we went for daikin ASHP and that uses R32; with this, the restrictions no longer applied. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@morgan Thanks - are you thinking air flow / noise issues or others? Definitely isn't the most ideal but its a common arrangement around me (Manchester) so someone going to have to find a solution at somepoint! Attached a better photo - had thought about the end of the wall but the bu-folds are next to it, also don't think my partner would accept it being there...
@editor copying you in as you raised similar questions.
Looking at some Vaillaint installation documentation, one bit says 1000mm clearance out the front of the ASHP, some say 600mm. If its was 600mm, then I could technically make it work.
@sunandair both installers kind of were a bit flippant about location saying 'yeah it should be ok there' but something seems like its not been taken into account.
They've spec'd either a Vaillant aeroTherm Plus 5kW (R290) or EcoDan 5kW (R32) with the EcoDan specificed to address the clearance issues of R290. It has lower clearance figures required for maitenance but is quite tall and wouldn't fit under the window at the end (see image in response to Morgan at the top of thread).
I've heard about the outdated Propane limitation - hopefully gets sorted and allows more uptake.
Thanks @toodles do you have any photos of your install location that could help with my context? Just looked at your profile and looked up the spec of you Daikin ASHP. Its clearances and dimensions look like they would be suitable for one location i'm thinking (where the bins are in the image).
@samiebon1 I’ll take a few photos tomorrow and post them for you to see - sun has put its’ nightcap on now though. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@samiebon1 If you are to site the ASHP in that alley I can guarantee you will have serious issues with air flow. A guaranteed 'cold well'. If your installer is suggesting that as a viable site, I would recommend you look for advice from a different installer.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
I doubt it could go in the alleyway anyway as it’s going to be within 1m of the boundary so won’t meet permitted development requirements
-
Is this ASHP install OK?
30 minutes ago
-
Rate the quality of your heat pump design and installation
2 months ago
-
Any installer recommendations for Samsung ASHP?
1 year ago
-
Ecodan - optimal external installation?
1 year ago
-
Any recommendations for ASHP installers in the North West?
2 years ago
- 26 Forums
- 2,118 Topics
- 46.5 K Posts
- 20 Online
- 4,522 Members
Join Us!
Latest Posts
-
@majordennisbloodnok Thank you. I have sent a very ster...
By El3b , 30 minutes ago
-
Fitting new shower valve ..........
This may be too generic but I need to change the ...
By Lenny , 2 hours ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
So the manual is correct and looks fine to me, to abbre...
By ASHP-BOBBA , 6 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
Hi I, like others, avoid Amazon for ethical reasons....
By Topher , 7 hours ago
-
RE: Benefits of an extra horizontal loop for GSHP
I would deffo install an additional slinky run, especia...
By Transparent , 7 hours ago
-
RE: Say hello and introduce yourself
@editor fab - thanks Mars, and keep up the great work o...
By normpang , 8 hours ago
-
RE: Compressor and Evaporator Stratification
@trebor12345 So I think the 1st zigzag section shows so...
By ASHP-BOBBA , 23 hours ago
-
RE: Is this just haze or something more?
@majordennisbloodnok I was giving a talk to primary sch...
By Toodles , 1 day ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
We had our Tesla Powerwall 3 (and Gateway) installed ea...
By Old_Scientist , 1 day ago
-
Indeed. With a battery its presumably the battery con...
By JamesPa , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
To update an ESP device using ESPHome in Home Assistant...
By Grantmethestrength , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 5 days ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 5 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 5 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 6 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 6 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 6 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 6 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 1 week ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 1 week ago