Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Low flow rate on Samsung Gen6 12KW heat pump
Posted by: @riponowlAs far as I can see there is no way that the Eastron could possibly know which zone is active. It's not incorrectly wired, it's not wired at all.
You are correct. There should be a cable from terminal B17 in the control kit (the large white metal box with all the electrics inside) that goes to the L2 terminal in the Eastron. B17 becomes live when DHW is being heated and so when B17 is
connected to L2 in the Eastron, this becomes live as well. This tells the Eastron to label the flow temperature reading as DHW (there is only one flow temperature reading - it is just the label that changes). When L2 is not live the flow temperature is labelled as space heating.
It took 3 months for G L to get Passivliving to work at all. The G L electrician, who eventually sorted it, seemed very capable, but I presume they are instructed not to bother to connect a cable between B17 in the control kit and L2 in the Eastron. It is quite clearly explained in the Passivliving MMSP installation guide, so why they don't follow it, beats me. In my case there is a connection between L1 and L2, which there shouldn't be, which means that L2 is permanently live and my flow temperature is always labelled DHW. I did finally get a date for another G L electrician to correct this, but I had to cancel it and despite leaving messages they never got back to me. I asked Ofgem if it was important to rectify and they never replied, so I left it.
Posted by: @riponowl@iancalderbank Where do you go to set a reheat timer for the HW? I'll try adding some lagging to the pipework and see if that helps.
settings button , buttom right hand corner of your controller.
scroll right -> schedule
fairly intuitive from there on
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
-
Hypothetical House Design
1 month ago
-
Flow Rate & Low Loss Headers
1 year ago
-
Primary Pump positioning for Samsung Gen6 system
2 years ago
-
Training videos/course/whatever. Control settings
3 years ago
- 27 Forums
- 2,736 Topics
- 64.2 K Posts
- 760 Online
- 7,141 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: PV and battery long payback - sense check query
@old_scientist I have now drafted 2 replies - both have...
By DavidB , 1 hour ago
-
RE: Can I start an argument about buffer tanks please? 🙂
Assume flow from the heat source is higher than flow to...
By bobflux , 10 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks for that. BTW I'd be happy to test one for you...
By BlizzardGreen , 12 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: adrian Manufacturer: Appliandirect.co....
By Adrian , 13 hours ago
-
RE: Acond heat pump failed after four years - diagnostic quote £940 plus VAT
@downfield Thank you Downfield. This sounds potenti...
By Mia , 1 day ago
-
RE: Digest of UK Energy Statistics
@jeff Yes my brother in Oz told me of that charge year...
By Jancold , 1 day ago
-
RE: Love veg, hate watering cans
My dear daughter came for a bath and was given clear (I...
By Jancold , 1 day ago
-
RE: Questions about A2A for heating as well as cooling
@ashp-bobba ah that's good to know, I'll get in contact...
By donciccio , 1 day ago
-
RE: Aircon - in listed buildings
@etchedpixels thanks for giving such a full and helpful...
By GrahamF , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist The service engineer powered down the ex...
By Papahuhu , 2 days ago
-
RE: Issue with Samsung Cascade System
@jamespa It's a funny system, but was out only option l...
By Renewables345 , 2 days ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Thanks, I like the chart, very helpful and this will de...
By baroquebank , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Production resumed to normal once the issue ...
By MK4 , 3 days ago