Posted by: @riponowlAs far as I can see there is no way that the Eastron could possibly know which zone is active. It's not incorrectly wired, it's not wired at all.
You are correct. There should be a cable from terminal B17 in the control kit (the large white metal box with all the electrics inside) that goes to the L2 terminal in the Eastron. B17 becomes live when DHW is being heated and so when B17 is
connected to L2 in the Eastron, this becomes live as well. This tells the Eastron to label the flow temperature reading as DHW (there is only one flow temperature reading - it is just the label that changes). When L2 is not live the flow temperature is labelled as space heating.
It took 3 months for G L to get Passivliving to work at all. The G L electrician, who eventually sorted it, seemed very capable, but I presume they are instructed not to bother to connect a cable between B17 in the control kit and L2 in the Eastron. It is quite clearly explained in the Passivliving MMSP installation guide, so why they don't follow it, beats me. In my case there is a connection between L1 and L2, which there shouldn't be, which means that L2 is permanently live and my flow temperature is always labelled DHW. I did finally get a date for another G L electrician to correct this, but I had to cancel it and despite leaving messages they never got back to me. I asked Ofgem if it was important to rectify and they never replied, so I left it.
Posted by: @riponowl@iancalderbank Where do you go to set a reheat timer for the HW? I'll try adding some lagging to the pipework and see if that helps.
settings button , buttom right hand corner of your controller.
scroll right -> schedule
fairly intuitive from there on
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
-
Flow Rate & Low Loss Headers
3 months ago
-
Primary Pump positioning for Samsung Gen6 system
1 year ago
-
Training videos/course/whatever. Control settings
2 years ago
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 37 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 2 hours ago
-
@cliffhanger - seriously though, I have no idea. What I...
By cathodeRay , 4 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 4 hours ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 6 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 9 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 12 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 12 hours ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 13 hours ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 1 day ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 1 day ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 1 day ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 2 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 2 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 4 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 5 days ago