Low flow rate on Samsung Gen6 12KW heat pump
Posted by: @riponowlAs far as I can see there is no way that the Eastron could possibly know which zone is active. It's not incorrectly wired, it's not wired at all.
You are correct. There should be a cable from terminal B17 in the control kit (the large white metal box with all the electrics inside) that goes to the L2 terminal in the Eastron. B17 becomes live when DHW is being heated and so when B17 is
connected to L2 in the Eastron, this becomes live as well. This tells the Eastron to label the flow temperature reading as DHW (there is only one flow temperature reading - it is just the label that changes). When L2 is not live the flow temperature is labelled as space heating.
It took 3 months for G L to get Passivliving to work at all. The G L electrician, who eventually sorted it, seemed very capable, but I presume they are instructed not to bother to connect a cable between B17 in the control kit and L2 in the Eastron. It is quite clearly explained in the Passivliving MMSP installation guide, so why they don't follow it, beats me. In my case there is a connection between L1 and L2, which there shouldn't be, which means that L2 is permanently live and my flow temperature is always labelled DHW. I did finally get a date for another G L electrician to correct this, but I had to cancel it and despite leaving messages they never got back to me. I asked Ofgem if it was important to rectify and they never replied, so I left it.
Posted by: @riponowl@iancalderbank Where do you go to set a reheat timer for the HW? I'll try adding some lagging to the pipework and see if that helps.
settings button , buttom right hand corner of your controller.
scroll right -> schedule
fairly intuitive from there on
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
-
Flow Rate & Low Loss Headers
7 months ago
-
Primary Pump positioning for Samsung Gen6 system
1 year ago
-
Training videos/course/whatever. Control settings
2 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,367 Topics
- 53.7 K Posts
- 376 Online
- 6,042 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Interesting question. To be frank, since I have no inte...
By Majordennisbloodnok , 2 hours ago
-
RE: Changing from 4-port buffer to volumizer
@andy1618 see the very sage advice from @editor above. ...
By JamesPa , 12 hours ago
-
RE: New Fogstar 15.5kWh upright solution
The video shows the JK balancer, but the connection of ...
By Batpred , 14 hours ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 Hi, yes this is the issue with every (stand alon...
By ASHP-BOBBA , 16 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk FWIW I managed unintentionally to 'coax' mine in...
By JamesPa , 16 hours ago
-
RE: Help needed with Grant Aerona 3 issues
Ok please post back once experiment complete. Give it ...
By JamesPa , 16 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
You are in essence right. Adia only works with selecte...
By JamesPa , 17 hours ago
-
No, you haven’t missed out, @batpred. This thread’ll st...
By Majordennisbloodnok , 18 hours ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
Also, though they weren’t prepared to match the price t...
By Toodles , 19 hours ago
-
RE: How long will your energy contract last?
My INTELLI-FIX-12M-25-08-29 has less than 12 months to ...
By Batpred , 19 hours ago
-
RE: GivEnergy 2025 forthcoming batteries and inverters
Then, perhaps @toodles , you should've made a submissio...
By Transparent , 19 hours ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I am wondering if anyone with an EV could find the 7p/k...
By Batpred , 19 hours ago
-
Possibly, but it would also reduce DeltaT across the em...
By JamesPa , 19 hours ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@cathoderay It was reminiscent of the BBC Open Universi...
By Toodles , 20 hours ago
-
-
@morgan They are unsupervised these days, can’t get the...
By Toodles , 4 days ago
-
RE: Setback savings - fact or fiction?
Exactly. We only need to compare conditions, to decide ...
By cathodeRay , 5 days ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Welcome @mickamills We too have an oversized 12kW Sa...
By Old_Scientist , 5 days ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
@caron I can confirm that the power usage of the PW3 is...
By Old_Scientist , 5 days ago