Low COP on Samsung 16kw Gen6
I got the pipes on the hot water cylinder lagged (although ran out for a small area). Shocked at the difference it made. Heat loss went from 0.46 degrees per hour to 0.38 degrees per hour. Also got the water onto the schedule to only heat 1 hour in the morning which was lovely and hot this morning. I'll get some more lagging next week to do the last few pipes that are exposed.
Weather was slightly warmer last night (+1 to +6 degrees vs -4 to +4), but only used 33kw yesterday (COP 2.7) vs the 41-74 that we've been using the last week or two. Will keep tracking and see if it stays more sensible.
Posted by: @catapult@iancalderbank @derek-m I got some thermometers onto the pipes to/from the buffer. At flow temp of 37 degrees
from ASHP to buffer 36.7
from buffer to rads 34.8
from rads to buffer 33.4
from buffer to ASHP 33.8
ok so lots to consider here. first thought: is this definitely a radiator system? if so you've got some quite low temps in the rads (implied MeanWT of 34.1), so you're at least doing well from being able to run the ASHP at the lower temp end of its performance curve for a rad system. Or is it UFH (I thought I saw something a bit like an UFH manifold in one of the pictures)?
secondly the DT between flow and return , buffer to/from rads seems to be really low @ 1.4C. heat transfer is proportional to DT times flow rate. heat pump rule of thumb DT is 5C. 1.4C implies either an enormous flow rate or you're just not getting much heat through to rads. DT on the ASHP side is only 2.9 as well. did you say you had a flow rate number for the ASHP side from the heat pump itself? worth monitoring the temps on inputs and outputs of the manifolds as well to see what they are doing.. is it the same as the rad-side buffer pipes, or there some other mixing going on (you had a complex pipe topology I recall).
there might be a few tweaks that could come out of this, but (In my opinion) this will probably conclude in substantial physical plumbing changes being required to achieve a system that is efficient, vs one that does work but is inefficient. please read brendon's article that I posted link to if you've not done so already.
I think the basic question you need to ask yourself at this point is this:
Are you from the side of the spectrum that is keen to do this yourself, with free no-warranty guidance from forum members, make mistakes, likely have to break it whilst you do so (so one for the summer!) learning along the way etc? (hope this doesn't come over as rude - certainly not intended that way). or do you want to pay a pro to sort it?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankthis will probably conclude in substantial physical plumbing changes being required
I recall from the initial post that this system has individual flow and return to every radiator (hence the manifolds), or almost every radiator (see first couple of posts).
That may allow for a less dramatic change (probably focused on radiators, and the buffer tank). The MCS standards require the design meets 99% days of the year heating needs at design temperature. If you are prepared to go a bit lower than 99% and with slightly lower design temperatures there will likely be more, and less disruptive options with the current setup. e.g. adding fans to the radiators, sizing up some radiators or both to some.
Posted by: @catapult@iancalderbank @derek-m I got some thermometers onto the pipes to/from the buffer. At flow temp of 37 degrees
from ASHP to buffer 36.7
from buffer to rads 34.8
from rads to buffer 33.4
from buffer to ASHP 33.8
A buffer tank can be a problem with ASHP systems, since it makes balancing the flows and temperatures around the system more difficult. Probably the easiest way to modify, and hopefully improve your system, would be to connect the pipe from your heat pump directly to the pipe to the radiators, bypassing the buffer tank in the process. Then connect the return pipe from the radiators to one of the upper connections of the buffer tank, and plug the remaining open connections. This would convert your buffer tank into a volumiser, so that the water going to the radiators is now at full LWT without any possible mixing to cool it down. Once done it may also make the two additional water pumps surplus to requirements.
To carry out this modification would necessitate draining the system, so in the meantime you could try varying pump speeds to try to balance the flow rates and even up the temperatures.
The objective is to get the water going into the radiators as close as possible in temperature to the LWT of the heat pump.
@william1066 yep agree. tbh what I was going through was exactly what derek-m just suggested. drain down and rebuild without buffer is what I'd do (But not sure'd I'd do in january). wasn't clear to me whether the OP is the type to want to do this level of modification themselves.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbank@william1066 yep agree. tbh what I was going through was exactly what derek-m just suggested. drain down and rebuild without buffer is what I'd do (But not sure'd I'd do in january). wasn't clear to me whether the OP is the type to want to do this level of modification themselves.
Actually looking at the photo's, if there are isolation valves in appropriate locations, it may be possible to shutdown the system, and isolate the buffer tank. Then remove the pipework to the air vent on the top of the buffer tank, and using a suitable hose siphon most, if not all, of the water from the buffer tank into suitable containers if it contains antifreeze.
Re-pipe the system as previously suggested, then refill the buffer tank, which is now a volumiser, either with the collected antifreeze mixture or just cold water. Open the isolation valves and get any remaining air out of the 'volumiser' and re-pressurise, then restart the system.
It may also be necessary to adjust the WC curve to accommodate the anticipated improvement in efficiency.
- 26 Forums
- 2,417 Topics
- 54.8 K Posts
- 269 Online
- 6,096 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
So, after much anguish, and even visiting the neighbour...
By razz , 6 hours ago
-
MLCP (Multi-Layer Composite Pipe) for ASHP
@editor nope. The info you reported was sufficient for ...
By iotum , 8 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
@robs Quick response while I'm in stationary traffic le...
By Sheriff Fatman , 9 hours ago
-
RE: Setback savings - fact or fiction?
Maths looks right to me, my only question about this ca...
By JamesPa , 9 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
@jamespa I wasn’t offended at all. You are very knowled...
By Davesoa , 9 hours ago
-
RE: Experience - New Build / Complete New Heating System
@vincro I would be surprised if it is much above 5 to 6...
By ASHP-BOBBA , 10 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Yes, certainly not enough could have been tested in any...
By Batpred , 10 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
Yes bang on and maybe I can illustrate that by way of e...
By iotum , 12 hours ago
-
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
A big thank you to @jamespa for all his efforts online ...
By trebor12345 , 15 hours ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor It is indeed for servicing. My current service ...
By Morgan , 16 hours ago
-
RE: Sunsynk Whole House Backup Issue
Hi @lostandconfused , I agree that topic/thread is the ...
By Batpred , 16 hours ago
-
RE: Speedcomfort radiator fans
In case it helps Andrew Kuhne on openenergy monitor has...
By JamesPa , 17 hours ago
-
Things have gone quiet with you @drei. Any updates?
By Mars , 20 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Thanks @tim441. Interesting timing, as Passiv are a cur...
By Mars , 21 hours ago
-
Hi everyone, I have a two year old Marlec Solar iBoos...
By Tallmarc , 24 hours ago
-
RE: Please help with the settings ecodan
Are you trying to address any particular performance is...
By Sheriff Fatman , 1 day ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
🤣 Well, I never managed to get the HA solis "...
By Batpred , 1 day ago