Legionella cycle: Heat Pump or Immersion Heater?
Hi,
I've had my Grant ASHP for about 6 months now, and am slowly adjusting the set-up to hopefully more reasonable values.
Initially, DHW was set to temp of 55°C to run at 05:00, 11:00, and 15:00 (each for 1 hour), with a separate immersion heater element also running for an hour each Monday at 01:00 (for legionella sterilisation I assumed).
I've gradually reduced this until now I have it running from 15:00 to 16:00 only, set to 45°C, with the legionella cycle now running at 16:00 on Monday, directly after the ASHP has finished heating the water to 45°C.
My thinking now is that the immersion heater element runs at COP of 1 (at best); and the HP runs at COP of 1 (at the very worst) so it actually makes more sense for the HP to do all of the legionella work i.e. on Mondays set the DHW to 60°C (the maximum it will permit) for 1 hour at 15:00, and no longer use the immersion heater at all.
Does this seem reasonable? I also think that 60°C is possibly too high, and something like 58°C would be fine. At the moment the HW is at about 58°C by 17:00 on Monday, and stays above 55°C until almost midnight. That seems more than adequate to kill legionella (over 55°C for 7 hours).
Grant Aerona 3 10kW
Posted by: @mikeflMy thinking now is that the immersion heater element runs at COP of 1 (at best); and the HP runs at COP of 1 (at the very worst) so it actually makes more sense for the HP to do all of the legionella work i.e. on Mondays set the DHW to 60°C (the maximum it will permit) for 1 hour at 15:00, and no longer use the immersion heater at all.
Does this seem reasonable? I also think that 60°C is possibly too high, and something like 58°C would be fine. At the moment the HW is at about 58°C by 17:00 on Monday, and stays above 55°C until almost midnight. That seems more than adequate to kill legionella (over 55°C for 7 hours).
When I was looking at legionella cycles a while back, I found a lot of variation in opinion regarding how often to run the cycle. Regs say one thing, others point out that the bottom of traditional cylinders rarely if ever reaches the required temperature. The actual temperature and duration required to kill the bacteria though was pretty much consistent.
If you can reach the required temperature using your heat pump then yes it makes a lot more sense to use it rather than the immersion coil. The only exception I can think of to this is if you have solar panels and a diverter, which essentially will do it for free (or a loss of export)
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodyIf you can reach the required temperature using your heat pump then yes it makes a lot more sense to use it rather than the immersion coil. The only exception I can think of to this is if you have solar panels and a diverter, which essentially will do it for free (or a loss of export)
For what its worth Vaillant R290 heat pumps (I discovered a few weeks ago) are designed to do the legionella cycle in the heat pump only, and appear (unlike many other HPs) not even to be capable of controlling the immersion. So thats the decision Vaillant made once they got to the point of having a FT high enough.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have a Grant ASHP and have the HW output from it set at 60degC for 75 minutes daily. This will charge my 250litre pre-plumb Grant cylinder to 55degC usually within 1hr, and it maintains this temperature for many hours if no hot water is drawn off. It's more thorough at heating the cylinder than the built in 3kW immersion. If I use the immersion the built in immersion thermostat starts to cycle on and off but the tank content thermostat never reaches above 54degC. The immersion stat is set to it's highest setting, supposedly 65degC.
Also, the tank contents cool much more quickly with no hot water drawn off compared to when I heat using the ASHP. That to me proves that the immersion heating is not very thorough. I have more faith in the ASHP providing better Legionella protection daily to 55degC than the 3kW immersion weekly to 54degC! The ASHP heating coil is lower down than the immersion element and a much larger surface area.
The ASHP will give a CoP of 2-2.5 in heating, so is much more energy efficient than the immersion. I have solar PV+battery and a diverter. Initially I thought using the diverter would be most cost effective, but charging the battery using solar, and then using it to power the ASHP is more economical. I'm using less than half kWh than direct immersion, and can export more surplus PV that way at 15p/kWh. 'Every little helps!' 😀
-
HOT TIP - DHW Cylinder Thermostat
2 years ago
-
Why run a disinfectant cycle ?
3 years ago
- 26 Forums
- 2,149 Topics
- 47.1 K Posts
- 12 Online
- 5,667 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Electricity price predictions
@jeff Thanks for that clarification. As we don't ha...
By JamesPa , 2 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I am pleased to see the change. We definitely need t...
By Jeff , 3 hours ago
-
RE: is a home battery without an EV worth it?
OK but that's market forces not minimum wage and of cou...
By JamesPa , 3 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@jamespa Crossing sheep with kangaroos?
By Toodles , 6 hours ago
-
RE: Octopus tariffs - a quick comparison
I'm on Intelligent Go . Only since start of Feb. Before...
By Tim441 , 10 hours ago
-
RE: How Do I Know When the Hot Water Has Run Out?
@transparent that is a very interesting suggestion, tha...
By GrahamF , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
Sorry to resurrect this thread, but it is sort of relev...
By cathodeRay , 1 day ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I missed your 22nd June post on this. I am sure it can ...
By cathodeRay , 2 days ago
-
Now posting on the right topic.... With general build...
By benson , 2 days ago
-
RE: How to waste energy (and time) playing with AI.
I’m sure like many software toys that it is addictive! ...
By Judith , 2 days ago
-
RE: Does anyone have experience of a smart water meter?
@judith With Anglia Water it was a compulsory upgr...
By TechnoGeek , 2 days ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
We’re high energy users other than the ashp so the OVO ...
By Judith , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
Something isn't right here, you don't design ufh to wor...
By JamesPa , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
No I'm not mining anything @drei but I am doing R&...
By Transparent , 3 days ago
-
RE: Rodents! A word of warning for heat pump owners
Wasps caused frequent tripping of my lighting circuit a...
By JamesPa , 3 days ago
-
RE: Ecodan & MelCloud scheduling
Yes, the 2 are separate. To add to the complex desig...
By HCas , 4 days ago
-
I should clarify that the FoxESS web interface is not l...
By Old_Scientist , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
@robs Hi Rob, At the end of a note to Mitsu UK, thank...
By DavidAlgarve , 5 days ago
-
RE: Why so many sigenergi installer recommendations?
@adamk Tesla is a great option, it’s also one we instal...
By SAEnergy , 6 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As a potential heat pump customer, it would be good to ...
By Temperature_Gradient , 6 days ago