Issue with Samsung A2W Heat Pump - Water Outlet Temperature
Dear Community
Today - It was 0.4°C outdoors, but the Water Output Temperature was regulated to 34°C. Based on the Water Law configuration, it should start at 35°C.
I assume there is some setting that prevents the unit from allowing more than 35°C for Floor heating.
I do not have a Samsung so I'm just speculating until someone more useful comes along.
Just using the numbers you've provided it seems like you're getting 8.4kW from the unit (DT * flow rate * SHC). I wonder if the flow temp won't go any higher because you're right at the limit of the unit's power. Samsungs have external pumps, right? Is that set to full power or is it controlled by the heat pump via PWM? I would have thought in any case that higher flow rate and lower temps is better for efficiency reasons anyway.
-
Samsung E911 intermittent issue
5 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
7 months ago
-
Sudden drop in COP
1 year ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
-
Any installer recommendations for Samsung ASHP?
1 year ago
Currently viewing this topic 2 guests.
- 22 Forums
- 2,084 Topics
- 46 K Posts
- 32 Online
- 3,378 Members
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Renewables & Heat Pumps in the News
Yes I realise I'm picking this up a week late...... but...
By Transparent , 2 hours ago
-
Mitsubishi Ecodan Fails to Heat Water despite temperature drop
My daughter has recently moved into a new flat where wa...
By m1kegibson , 3 hours ago
-
@editor Mars if you have any recommendations for down s...
By abam48 , 14 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness HI, The rules is a best practise, the ...
By ASHP-BOBBA , 18 hours ago
-
RE: Vaillant AroTherm Plus 7kW
@scalextrix if your under unit heater is like our Myson...
By Judith , 19 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@cathoderay how did you get a script to run for that- d...
By benson , 21 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 2 days ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 3 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 4 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 4 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 4 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 5 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 6 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 7 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 7 days ago