Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

How quickly would you want/expect heat recovery to take from setback?

73 Posts
9 Users
6 Reactions
2,142 Views
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5664
 

Posted by: @andrewj
↑

It’s an interesting discussion.  As I’ve mentioned I’m trying to understand how my Cosy unit is working and how the WC curve is impacting how the house heats and is maintained.  I do know if I bump the WC warm weather temp to 36c the living area in the house will warm to around 22.5c, and other rooms to over 23c (which my wife loves).  That does require the thermostat to be placed in the downstairs loo with a target temp of 21c (or 20c or 19c it doesn’t matter actually.) My target is to be able to keep the Cosy running without interruption from the thermostat, providing heat constantly but not overheat or consume a large amount of power.  

I think the resolution to this (in the absence of some sort of auto adjust mode in the heat pump - which for all we know the Cosy may have) may well lie in 

a) adjusting your weather compensation curve so its 'critical' (ie just, but only just,  at the right level to heat the house)

b) balancing your radiators for the desired room temperature differences.

c) setting the desired temperature to just over that you actually desire (for example 1 degree)

This essentially means that you are operating on pure weather compensation except that the heat pump will be turned off when the room where the sensor is rises more than 1C above the desired.  You may want to put it in the room most affected by solar gain.  Its how many here would advise that heat pumps of all makes initially be set up.

To do anything more sophisticated probably requires you to measure the temperature in each room and adjust accordingly, taking into account response times etc, always ensuring that there is enough system volume accessible for defrost, and balancing the temperature of individual rooms in a way that takes into account the fact that rooms share heat and operating at lowest FT is always going to be most efficent, and therefore its (probably) inefficient to shut off heating to some rooms unless it cant be avoided without making them uncomfortable.  Only Adia Thermal has this level of sophistication to the best of my knowledge.

If you have mechanical TRV heads then you could try putting these on a small proportion of radiators in rooms that have a tendency to overheat.  There is some tolerably believable evidence (albeit from a single, properly controlled, lab experiment) that mechanical TRVs (not digital ones) fitted to an almost balanced system behave as flow regulators in an analogue manner not on/off.  Effectively they are acting as automatic balancers/flow rate controllers

The downside is that recovery from any off period will be slow, as it always will be if the FT is critically adjusted to avoid cycling (which is what you have said you want to do).  You cant have it both ways!

Posted by: @andrewj
↑

Man, I would kill for a holiday mode on the Octopus app.  As it is, all has to be done manually.

Wow, Im shocked by that.  Even some of the bargain basement heat pumps feature holiday mode.  This is a strange omission and you should campaign Octopus to add it.

 

 


This post was modified 14 minutes ago by JamesPa
This post was modified 13 minutes ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   