Hitachi Yutaki M efficient operation
So i think i have narrowed it down without however knowing the solution. Buffer creates a loop. Hp provides the required water temp to the buffer but somehow the energy is not diverted to the ufh but returns to the hp, hence the low dt and the reduced temp at the manifolds compared to the outlet reading of the hp. Does this means that there is unbalanced flow between the primary circuit (hp and buffer) and secondary circuit (buffer and manifolds)? The circulating pump in the first circuit is adjustable but the second is not
Posted by: @iraknicDoes this means that there is unbalanced flow between the primary circuit (hp and buffer) and secondary circuit (buffer and manifolds)? The circulating pump in the first circuit is adjustable but the second is not
Yes, almost certainly.
I dont know if the HP can control the buffer, some can. If the buffer has two temperature sensors at different heights then its possible in principle to use this information modulate the speed of one or other pump so that on average the rates are the same (which is ideally what you want). It would be worth looking at the HP manual and the buffer in case it can do this.
Otherwise you are down to adjusting the pump rates. The HP might adjust the primary pump to suit its needs. If it does so and unless the HP does feature buffer management, Id be loathe to touch this. That said there is generally no harm in turning the primary up, HPs complain about low flow (because its not enough to take the heat away) more than about high flow.
Im surprised that there is no adjustment on the secondary pump, many have three settings.
Having the primary a bit faster than the secondary will tend to force the thermocline (barrier between 'hot' and cold' water, assuming its stratified) down the tank, which means that the feed to the emitters should be at the same temperature as the feed from the heat pump, thus minimising the sacrifice in efficiency which would occur if the feet to emitters is lower temp than the feed from the heat pump. Obviously this will cause a little bit of recycling through the heat pump, but its better so far as I understand these matters than pushing the thermocline to the top which is what happens if the primary is slower than the secondary.
Do you know why the buffer is fitted? Generally they are a bad idea in heat pump systems, albeit that many installers put them in because its pretty much guaranteed to reduce callouts (by masking problems).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@iraknic how are you monitoring your UFH delta T?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@jamespa the buffer was fitted to increase water in the system due to the existence of zones. @editor
I am measuring the temps at the manifold using an IR thermometer. In my case it seems that the primary water pump is slower than the secondary (after the buffer) one? Can the secondary flow be reduced by manually decreasing ufh flow at the manifolds?
Posted by: @iraknicCan the secondary flow be reduced by manually decreasing ufh flow at the manifolds?
Yes. Its the same as turning down the lockshield on a radiator
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
i attach the setup of the buffer, highlighting the return lines and the specs of the water pump that is placed after the buffer. I thought of closing a bit of the outlet and return valves of the left side of the buffer (to and from) the manifolds and increase the flow of the primary pump (from hp to the buffer) to see what happens
@iraknic Please note, I don’t have any experience at all (diddly squat) of UFH plumbing but if a circuit has both send and return valves, it is probably only necessary and better to just constrict the flow to the circuit and leave the return without any restriction. I may be talking through the wrong orifice of course! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @iraknicA reason i believe is causing a low delta-t is the waterflow that is too high
I also tried lowering the internal waterpump speed but have not found yet how to do that. The setting in the installer section of the controller did have a deltaT setting and a HP ON deltaT setting I changed both to the same increase but the waterpump speed still is 100%
How did you try changing the deltaT?
I have a modbus gateway from which I can extract most relevant information. No real cycle information to be found though. Once can monitor and deduce it sure.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 56 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 1 hour ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 2 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 2 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 3 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 3 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 3 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 5 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 7 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 9 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 21 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 24 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 9 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 10 hours ago
-
SolarPV tables / online calculator
By MichelleC 17 hours ago
-
By Toodles 2 days ago