Posted by: @lfranklin
- @derek-m yes the vessel (buffer I think new one says) was exchanged and is fully pressurised and have checked system fully for any air.
Do you have a suitable thermometer or thermometers that could be used to measure both room temperatures, and could also be taped to radiators and pipework (with suitable insulation) to measure the system temperatures.
Starting from the pipework leaving the heat pump, could you work your way through the system and provide both wide angle and close up photo's of any equipment that you locate, things like valves, pumps, cylinders etc.
Posted by: @william1066Posted by: @derek-mWe can then try to go through your system operation in a logical and systematic manner.
@lfranklin - there is definitely two (or potentially more) components to this, and as Derek said, being systematic will speed things up. From what I can determine in the thread, there are a whole bunch of things that need addressing. My summary is as follows.
- can hear expansion vessel working and its very annoying when trying to sleep
- struggling with system not heating two rads on the system
- added a second pump onto the return side of the system trying to fix problem 2 above and that seemed to help for a few hours when first installed but now not coming back on again
- if i turn the TRV off on others earlier in the system off the last two do get warm but even then not hot
- We had solar installed at the time too (16 x 405w panels) and even that isn't working right at just 1-1.8kwh per day generation at the moment
- wired remote controller showing water pump and some other bits and a very high heat water temp on main front screen even though heating has been off
- heating stopped all together today despite pump running and eating lots of electric!
- DHW not getting up to temp and so not letting the radiators have hot water
1,2,3,4 and 8 could be combined into a single group, which is likely [mostly] plumbing rather than heat pump settings related. (with the caveat that for heat pumps you should be going for warm radiators, not hot radiators)
Item 5 probably needs its own thread on this forum.
6 is likely config/understanding of the Samsung Gen6 system operation
7 probably a mixture of hive, samsung settings, plumbing
I can probably help with 6, the rest, not so much.
To save me having to forage through the Samsung manual, do you know where the control settings for booster or back up heaters are located, and if they can be disabled if necessary?
From what @lfranklin has previously stated, you have correctly identified that there could be a number of issues.
My suggestion would be to initially set the system to operate in fixed LWT mode, and then carry out temperature measurements around the system to try to identify where the heat energy is flowing. Could you therefore explain how to set the system to fixed LWT at say 40C?
@derek-m The easiest way that I found to do this was to set the weather compensation to 40 at minimum and 40 at maximum outside temperatures. That way it’s always going to be 40° C. There is another way, I presume but I haven’t found it!
Posted by: @derek-mTo save me having to forage through the Samsung manual, do you know where the control settings for booster or back up heaters are located, and if they can be disabled if necessary?
The booster heater can be disabled [#3031], but you can also disable it by making sure your hot water is on economical setting, not standard, power or forced. That you can do in the schedul
The benefit of leaving it enabled is to speed things up when needed, by just changing the mode on the remote controller (not so convenient if in the loft)
Posted by: @lfranklinI think that the booster heater is set to come on for last 10 mins of heating if not at temp.
#3032 and #3033 will tell you when and for how long
Posted by: @lfranklinI think that the booster heater is set to come on for last 10 mins of heating if not at temp.
Note: there is an element of "lost in translation" in all the heat pump manuals, but this is what they say.
In Power or Forced mode the booster heater starts without any delay (so ignores) FSV #3032
In Economic mode the DHW heating is via the heat pump only (I think this only applies if your target HW temperature is 55 degC or less. see page 34 of the manual)
- 26 Forums
- 2,118 Topics
- 46.5 K Posts
- 22 Online
- 4,522 Members
Join Us!
Latest Posts
-
@majordennisbloodnok Thank you. I have sent a very ster...
By El3b , 22 minutes ago
-
Fitting new shower valve ..........
This may be too generic but I need to change the ...
By Lenny , 2 hours ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
So the manual is correct and looks fine to me, to abbre...
By ASHP-BOBBA , 6 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
Hi I, like others, avoid Amazon for ethical reasons....
By Topher , 7 hours ago
-
RE: Benefits of an extra horizontal loop for GSHP
I would deffo install an additional slinky run, especia...
By Transparent , 7 hours ago
-
RE: Say hello and introduce yourself
@editor fab - thanks Mars, and keep up the great work o...
By normpang , 8 hours ago
-
RE: Compressor and Evaporator Stratification
@trebor12345 So I think the 1st zigzag section shows so...
By ASHP-BOBBA , 23 hours ago
-
RE: Is this just haze or something more?
@majordennisbloodnok I was giving a talk to primary sch...
By Toodles , 1 day ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
We had our Tesla Powerwall 3 (and Gateway) installed ea...
By Old_Scientist , 1 day ago
-
Indeed. With a battery its presumably the battery con...
By JamesPa , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
To update an ESP device using ESPHome in Home Assistant...
By Grantmethestrength , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 5 days ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 5 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 5 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 6 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 6 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 6 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 6 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 1 week ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 1 week ago