Heat pump's integral circulator pump
Acting on current advise from this channel and others, I'm planning to ask my installer to remove the 4 port buffer and associated circulator from my 200 square meter UFH system over two floors.To be fair to them I had originally (naively) intended to use zoning controls. I'm running weather compensation - fully open loop and I have balanced the zones to achieve desired room temperatures 😀 .
My concern is "will the Daikin integral water pump be powerful enough to provide sufficient circulation" ?
6kW Daikin-ERGA06EAV3A - Indoor Hydrobox Model: EHBH08EF6V
Secondary circulator - Grundfos 25-50 180 (set to minimum speed )
Any advise please.
The quick answer to your question is that the Daikin's own circulation pump probably won't be powerful enough. So in instances like this, if the installer has calculated that it's insufficient, they can repipe your 4-port buffer into a volumiser and then utilise your Grundfos post volumiser to help flow.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Iam also looking at this route from 4 pot to maybe a volumiser thaks to Jamespa. Can I ask how does the volumiser help ,or not, if you are putting the return to the top of the old buffer then back to the HP at the bottom of the buffer. Is it not simpler to straight connect through returns.
I understand how important feedback to a question can be, so here is mine.
With no disrespect intended to Mars, I decided to chance it and go ahead with the removal of the 20ltr. 4 port buffer and secondary water circulator to further simplify my system, retaining the redundant components with the proviso that they could be re-instated if needed, .
By using only the Daikin's integral circulator the flow rates appear to be sufficient with no increase in cycling frequency.
I'm very pleased with the results so far, with a COP (using Daikin's on-board energy meter figures!!) of just above 400%- with a happy wife to boot!
@ubert767, I'm really pleased to hear that your pump is strong enough. That’ll definitely be interesting reading for those with Daikins. I’ve been in private contact with a homeowner who’s had issues with Daikin’s defrost cycling and distribution pumps, so it’s great to hear yours is working well.
For the benefit of others, did you remove or bypass the buffer tank yourself, or did you have someone do it for you?
This is a great example for anyone still doubting whether buffer tanks actually improve system efficiency!
And, just to clarify, my doubts about the Daikin pump weren’t unfounded – most installers I’ve spoken to say that because buffer tanks are so commonly used, many manufacturers cut corners on the power of the internal pumps, leaving them with insufficient head.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @alfapat@ubert767 Thanks , no wonder I get too much of a temp drop , mine is 200L , too much mixing .
Ours is 100 litre and it's been piped for maximum distortion/mixing with an X shape between the pipes. Ridiculous. We're planning to get ours repiped in late spring.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
In order to answer my doubts about my buffer vessel I built a cheapish temperature logging system from a Raspberry Pi and five DS18B20 temperature sensors(one sensor on each buffer port and one measuring O.A.T.) This allowed me to see the differentials across the flow and return ports, to check the distortion in the buffer vessel and record the system cycling intervals.
Posted by: @alfapatIam also looking at this route from 4 pot to maybe a volumiser thaks to Jamespa. Can I ask how does the volumiser help ,or not, if you are putting the return to the top of the old buffer then back to the HP at the bottom of the buffer. Is it not simpler to straight connect through returns.
It provides extra system volume which is useful for defrost but may well not be necessary. Have you any idea what volume of water you have in your secondary circuit.
One of the ports at top and the other at bottom to ensure it's actually both heated by the water passing through and engaged in the flow. Otherwise you could end up with most of the water in the volumiser just being 'bypassed'
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,122 Topics
- 46.6 K Posts
- 35 Online
- 4,529 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@terry1812 Yes, I use Homely, as to whether Daikin is u...
By Toodles , 39 minutes ago
-
RE: ASHP heat output monitoring
@carlo - welcome to the forum. I don't know about LG...
By cathodeRay , 5 hours ago
-
RE: Why do we need pressurised systems?
@old_scientist If that were the case (and it might well...
By Toodles , 9 hours ago
-
OK... I'm here. But the amount of my time needed to add...
By Transparent , 11 hours ago
-
RE: 300 Liter Tank - Do I have to heat it all?
There’s no second hand market for DHW tanks (I was told...
By Judith , 16 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 1 day ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 1 day ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 1 day ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 1 day ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@davidalgarve It should just be recovered by both servi...
By dgclimatecontrol , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
Aggregators have been recognised for many years, and it...
By Transparent , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Great news I edited my previous post (probably af...
By JamesPa , 2 days ago
-
RE: Double or Triple Glazed Windows?
@toodles Glad to hear things are progressing well for y...
By TRBob , 3 days ago
-
How to waste energy (and time) playing with AI.
A friend of mine who subscribes to an AI service was ex...
By Toodles , 3 days ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@topher you’re more than welcome to, yes. I’ll send you...
By Mars , 4 days ago
-
RE: Fitting new shower valve ..........
I’ve never taken a chance when fiddling and changing ou...
By Mars , 4 days ago
-
You should contact the council and report the unsatisfa...
By JamesPa , 4 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
I would deffo install an additional slinky run, especia...
By Transparent , 5 days ago