Heating coming on when not required
Im probably having a brain fart, but for the life of me I cant think what is going on with my heating.
My Samsung Gen 6, keeps coming on intermittently to run the heating when the weather is warm. Im running it on weather compensation, but also have the control unit in my lounge to limit it when the lounge reaches temperature. At the moment I have the lounge stat set to 16C. As you can see in the first graph my room temperature never got below 20C, so by my logic the heating should be off.
The second graph shows how some days its on and others its not!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
So you're saying that nothing is calling for heat because all your indoor thermostats are below temperature?
Is it quite cold outside where you are? Below 16ºC?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Thats correct. Its not particularly cold but the purple line in the first graph shows the outside temperature. Its shows that the heating came on at 9.30pm when the outside temperature was about 16C and the indoor temperature 21C.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody, his is one of those odd things Rob Berridge mentioned in one of my podcasts and it stuck with me. I assume your heating isn’t manually switched off, correct?
If I remember rightly, he said that some heat pumps have an in-built setting linked to a CIBSE guideline (I think it was around 15.5C, but don’t quote me) which can automatically trigger certain pre-configured heating systems to come on below that point, regardless of whether there’s an actual "call for heat".
After that episode, I asked the panel about it, and they all agreed it’s usually better to switch heating off entirely (keeping HW on) in the shoulder months and summer if you don’t need space heating at all.
Just wondering if that could be what’s happening in your case... might not be, but worth checking. Just thinking out loud!
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor It may be that. I do remember setting up a max OAT at which the heating should turn off but can't remember where it was in the settings. I'm curious as to what I set it to now.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@editor It may be that. I do remember setting up a max OAT at which the heating should turn off but can't remember where it was in the settings. I'm curious as to what I set it to now.
I played with a max heating temp but there is a world of difference between what you want it to do on a cool day in shoulder season and what you want it to do on a coolish summer night for example.
So I reverted to simply switching heating off altogether for summer as I did with the boiler. Sometimes simple is best!
Perhaps if it offered a setting that looked forward and averaged the next 24-48hrs before deciding whether to switch off altogether that might cut it, but realistically I can do that myself and I don't want my heating control to be dependent on the internet.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 36 Online
- 5,673 Members
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 45 minutes ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 11 hours ago
-
My Samsung Gen6 (probably same controller as yours) onl...
By Old_Scientist , 21 hours ago
-
@drei When I was in local government we were of cours...
By JamesPa , 21 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 23 hours ago
-
RE: Boiling Mad: Exposing Radiatorgate
@rob-nezard you can see more of Drei's rad dramas here ...
By Mars , 23 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@drei I will say again that Im sorry to heat about your...
By JamesPa , 24 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 2 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 2 days ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 2 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 2 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 3 days ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 3 days ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 3 days ago