Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heat pump size advice
So the Financial Director as given the green light to getting an heat pump a few months ago.
Got 3 quotes from Octopus, British Gas and Heatgeek.
Octopus: heatloss of 5.2 with installing a Daikin 6kW, design at 50c bedrooms and hallway 18c and dining and living room at 21c.
Heatgeek: heatloss of 5.3 but want to install a 7kW Valliant and stating in the survey the reason why a bigger heatpump "This is due to the latest cold snap has highlighted some issues with output figures. During frequent defrost cycles the units are looking to loose up to 30% output" design at 45c all rooms 20c.
British Gas: heatloss of 4.4 with installing a Daikin 4kW, design at 45c all rooms 21c.
If I had the money I would go with HG but it's 4x times more than Octopus.
I'm going with BG as they've price matched Octopus and will put in new pipework and repipe some plastic runs at no extra cost.
Spoke to BG surveyor(who did install heatpumps before downing tools) regarding the other surveys I gotten and he said 4kW will do the job even at -7.
After seeing multiple posts regarding DWH and in a cold snap the heating will be off for maybe 2hrs(210L cylinder) the 4kW will struggle to catch up and will be working at it's top end(which i assume isn't good for longevity)
So i'm i best asking for a 6kW Daikin instead of a 4kW?
sorry for the ramble, want to make sure i get this right as I don't want the financial Director getting cold in winter and asking to get a combi installed.
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 1,069 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 3 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 17 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 4 days ago