Heat pump size advice – is 16kW overkill for this property?
Im looking for some second opinions to confirm what I think about a Thermal Earth installation in a neighbours house. I just want to be sure that the mainstream of thinking is the same as mine.
Thermal Earth did a heat loss report (not shared with owner) which predicted a 5835W loss. The owner then told them she might at some point in the future convert a garage space of 30 m2. They have subsequently fitted a 16kW Acond heat pump.
Their argument was that the extra heating requirement tipped it over their original choice so they went for the next one up.They havent said yet what their original choice of unit was, but it would have been an Acond. I estimate that the 30m2 space built to regs would add at most an extra 1200W giving a total of 7035W loss.
Does anyone else think that it is outrageous and inappropriate to fit a 16 kW model? Her usage for the last week was 255 kWh and she prefers her house cool.
Thanks in advance
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
What's the square footage of your neighbour's house?
The other alarm bell is why the heat loss report wasn't shared with the homeowner. If they've hired and paid them, they're entitled to that report. They should demand it.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm:https://kirstenandmars.com
@editor Sometimes, things can be even better; Octopus Energy’s Plumber and their Electrician spent three hours each assessing our property for a heat pump installation and shared their thoughts, reservations, suggestions on how to maximise siting and routing of pipes etc., provided us with the Heat Loss Calculation (verbally anyway) without any charge whatsoever, (They are our energy suppliers but there was no obligation involved for this survey). As it happened at that time, as they were the new boys on the block (early 2022), they were unable to provide an installation matching our desires due to using a narrow set of formulations and they did say that in due course, they would be widening the scope of installations. Regards, Toodles.
Toodles, 77 years young and hoping to see 100 and make some ROI on my renewable energy investment!
Here is the report size. I made her ask for it once I got involved, they said they usually provide it after installation!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
and the losses
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
it does seem excessive for a 100m2 house that has a heat loss in the normal range.
@kev-m well I guess it would be nearer to 120m2 after the possible extension, but by my calculation still twice what is required.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody holy ***t batman, yes! 16kw unit for a 5.8kw heat loss? even with a bit of growth room for an extension, thats bonkers.
I just had a look at the Acond range, there are two units. The N is rated at 1.5-7 kw. The R is rated at 3-16. Don't know at what temps, or how accurate the "plate rating" numbers are, not found that level of detail yet.
If the installer really felt that that brands "small" wasn't enough then surely the professionally appropriate thing to do would be to look at and discuss with customer alternative brands that have a more "medium" unit? Not just stick in the "large" because they have a deal with that brand?
Additional thought whilst getting coffee - we have "design conditions" weather right now. If the system is installed and running, it should be possible by looking at the systems stats to derive the house's actual heat loss in design conditions.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank That mirrors my feelings Ian. Unfortunately the owner has not been given a manual yet or even instructed how to turn off the heating. Its costing her £10-15 a day at the moment compared to my £5-7 a day in a similar sized worse insulated property just down the road, and I like it a lot warmer than she does.
The company want her internet installed to monitor it from there end but this is proving problematic in her property. I haven't been able to get an answer as to whether it can be controlled just from the controller unit or if it is an internet function via an app.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@kev-m well I guess it would be nearer to 120m2 after the possible extension, but by my calculation still twice what is required.
do you think excessive enough to hit the not fit for purpose clause in the sale of goods act?
I'm not sure about the relevant consumer law. It might be hard to prove it's not fit for purpose if it's able to heat the property and especially if it can modulate down to 3kW. An undersized system would be easier to prove. Also, if it complies with MCS I would think it would be deemed fit for purpose.
However, I don't think a twice oversized ASHP need cost twice as much to deliver the same amount of heat as the correctly sized one (as suggested by your own figures) so maybe it's the way it is set up and used?
Posted by: @bontwoody@iancalderbank That mirrors my feelings Ian. Unfortunately the owner has not been given a manual yet or even instructed how to turn off the heating. Its costing her £10-15 a day at the moment compared to my £5-7 a day in a similar sized worse insulated property just down the road, and I like it a lot warmer than she does.
The company want her internet installed to monitor it from there end but this is proving problematic in her property. I haven't been able to get an answer as to whether it can be controlled just from the controller unit or if it is an internet function via an app.
Has the controller been correctly optimised?
I always find posts and cases like this very disconcerting. Our floorspace is around 380m2 and we have an 18kW ASHP which is probably the right size for the entire property. This nonsense about heat pumps scaling down is such mumbo jumbo in my opinion, because there have been times when I've shut off half the house (UFH and rads) and there's very no drop off in electricity consumption.
@bontwoody, I don't think there's much of a case for it hitting any thresholds under the "fit for purpose clause in the sale of goods act?". I've looked into this when we ran into issues with our Samsung fridge (which is 10000% not fit for purpose), there's an awful lot of subjectivity involved in the definition of what is and isn't "fit". I have, however, been researching the complaints process of badly installed heat pumps and will now be adding incorrectly sized heat pumps to my research.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm:https://kirstenandmars.com
- 25 Forums
- 1,612 Topics
- 34.8 K Posts
- 51 Online
- 1,887 Members
Join Us!
Latest Posts
-
RE: In the middle of an ASHP installation - a few questions
On the grounds that an installation other than by an MC...
By JamesPa , 4 mins ago
-
RE: Midea ASHP – how to set weather compensation
Many thanks @mphb and @cathoderay. Didn't expect so qui...
By iWolf , 32 mins ago
-
RE: British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
@jancold My day 1 of install over. It started at 7 wi...
By Lucia , 11 hours ago
-
RE: Undersized Vaillant ASHP and abandoned by installer
Ps to the above. The requirements on the heat pum...
By JamesPa , 11 hours ago
-
The greenhouse tomatoes have ,as usual, done well but t...
By Jancold , 11 hours ago
-
RE: Locational electricity pricing
@transparent Phew! ok have skim read despite hectic d...
By Lucia , 11 hours ago
-
RE: How to Solve Mould and Mildew Issues in Renovated Properties
The answer if you’re doing a major renovation is a MVHR...
By Judith , 11 hours ago
-
RE: Will heat pump heat hot water without increasing the temp in my home?
Do you have a reference for that directive @toodles ? ...
By Transparent , 13 hours ago
-
RE: Calculating inverter size to match battery size
I expect your Seplos kit came with some guidance as reg...
By Toodles , 15 hours ago
-
RE: Determining correct flow rate for a heat pump
It’s clear from what you say, above and what we have ex...
By SUNandAIR , 19 hours ago
-
'If you are not part of the problem there's good money ...
By AllyFish , 24 hours ago
-
RE: Suitability of 45C flow temp with existing pipework
I've ordered a cheap borescope online and I'm going to ...
By Alex_N , 2 days ago
-
RE: Ecodan - flow rates, sensors, settings
Hi @rhh2348 , coming late to this thread as our Ecodan ...
By SUNandAIR , 2 days ago
-
RE: Agile: average import cost vs other tariffs?
@tim441 Last year I ‘netted’ about £400 that way so I h...
By Toodles , 3 days ago
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
@irmartini I think that @editor might sympathise with t...
By Toodles , 3 days ago
-
RE: Heat pumps don't work: debunking myths & misconceptions
I applied for my G99 last November. Largely as a resul...
By IanMK13 , 3 days ago
-
Setback for Vaillant Arotherm Plus
Currently our Vaillant Arotherm Plus is set in fully We...
By JWilliams89 , 3 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Unfortunately @burtis James is right. MCS is the Gove...
By Transparent , 4 days ago
-
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
@simonh Im not sure how useful they are but Ive attache...
By bontwoody , 5 days ago
Latest Topics
-
Calculating inverter size to match battery size
By Homonid 1 day ago
-
Agile: average import cost vs other tariffs?
By Tim441 3 days ago
-
Suitability of 45C flow temp with existing pipework
By Alex_N 3 days ago
-
Setback for Vaillant Arotherm Plus
By JWilliams89 3 days ago
-
By Toodles 4 days ago
-
By Jeff 4 days ago
-
By dssr 5 days ago
-
Solar Edge Inverters, returns recycling policy
By AllyFish 6 days ago