Heat pump install overloads home fuse - 80A limitations
Evening all.
I'm in the process of getting a heat pump installed.
The initial surveyor put a tester on the mains inlet, while getting me to turn on fully electric shower, kettle, oven and the 2 biggest induction hobs.
He stated it overloaded our 60A fuse, so I got the DNO to fit the biggest they could which was 80A, fitter didn't see a problem with what I told him we were proposing fitting.
In the meanwhile I got a solar install with 5kw inverter.
Didn't think there was a problem until octopus sent in a DNO request which they've refused as it exceeds our limit coming in at 92A, that's without the solar.
Anyone else see a solution or had similar problems?
I've emailed octopus but they don't always reply as soon as I'd like.
Is the electrical test really just turn on fully all the highest powered appliances in the house at the same time, take a reading and pass or fail?
Thanks
Why did your dno limit you to 80A. Was it a supply problem or because of inadequate meter tails (which they won't change).
I ask because mine did this but also told me that if I had the meter tails changed I could ask them to come out again and upgrade to 100A.
To answer the question you asked an electrician should do a calculation of your load making some assumptions about 'diversity' (basically an allowance for the fact that not everything will be on simultaneously). This tells them what capacity incoming you need. They will also make some assumptions about the load on each socket circuit which may well be much higher than you actually need.
It might be possible to adjust these assumptions by persuasion, or by reducing the capacity of the breakers on the circuits. Many ring mains have 32A breakers from the days when we had electric fires. These days the circuits are used predominantly for low wattage tech and the odd cooking appliance. In many cases 20A would cover the load. (As a matter of fact some electricians will exploit this by replacing the 32A breaker with a 20A one, which means that the restriction on numbers of sockets on a spur can be lifted. making for easier wiring if you need more sockets.)
I would try arguing the point particularly as presumably your heat pump is 8kW or less so only 16A?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks JamesPa,
Our DNO won't install anything more than 80A, in fact while they were changing our fuse, the neighbours came out and said can you update ours to 80A too please, assuming it was like ours 60A
Unfortunately theirs was already 100A and they dropped it back down to 80A.
I've just read up on diversity thanks, but unsure if octopus calculated using that.
Heat pump is 8kw, on the DNO form they put down 24A.
Hopefully octopus reply with a solution today.
Posted by: @njtHeat pump is 8kw, on the DNO form they put down 24A.
Would have thought looking at a data sheet that would be nearer 17A and that allows for an immersion to be driven directly from the heat pump. Have a look at you make model datasheet it will be on there.
@johnmo
Hi Johnmo,
I've looked on the data sheet and it does say 24A, recommended fuse 25A, so looks like it's the correct figures given to the DNO.
That doesn't bode well for climate change mitigation, much of which, at a household level, depends on power electrification (car, heat pump, hob).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I had a similar pantomime with my DNO. My incoming fuse is 80A with 25mm2 meter tail L&N incomers from external fuse and meter box to internal consumer unit. DNO wanted £800 & 8 week lead time (not a typo) to upgrade the fuse to 100A. I would have to then replace L&N tail incomers between meter and my consumer unit. Both were a non-starter, fuse upgrade due to price & lead time, and incomers due to them being under a hard tiled floor in 3 rooms. So I remain with an 80A fuse and have a very slightly undersized 10kW ASHP with 17.5A max FLC and recommended breaker rating 20A. Next size up 13kW ASHP, which I was planning to fit, was not then not connect and notify and requires a 32A breaker. DNO would not accept that additional load onto the consumer unit with an 80A fuse.
I rang our DNO on Friday they did the 60A to 80A swap on the Monday free.
Did your heat pump require an electrical amp test?
I don't think I'm extreme by having solar, a shower, induction hob etc but I'm way over 100A according to octopus.
I’m a bit confused by the comments above. Why are DNOs reducing this when the UK’s goal is the electrification of everything: cars, heating, cookers, etc.
Can you please pop who your DNO is and which ones have been involved in these incoming fuse “downgrades”?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi,
My DNO is National Grid (West Midlands area).
I had a 60A fuse, they came out but would only replace it with an 80A fuse. All at no cost.
Our neighbours with same house who have lived there since new asked if at the same time as changing ours would increase theirs thinking 60A to 80A, but for some reason there's already had a 100A fuse installed.
They said they couldn't leave the 100A in and they replaced it with an 80A.
Found this which may explain what is going on: https://connections.nationalgrid.co.uk/news-and-events/latest-news/standardisation-of-fusing-to-80a#:~:text=National%20Grid%20Electricity%20Distribution%20(NGED,a%20cutout%20fused%20at%20100A
I read that UKPN is still doing 100A fuses.
- 26 Forums
- 2,113 Topics
- 46.4 K Posts
- 27 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 6 hours ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 7 hours ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 19 hours ago
-
RE: Wood burner with ASHP - direct air?
I love the new fully Viking look... best personal avata...
By Mars , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 2 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 3 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 3 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 3 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 5 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 5 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 6 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 6 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 6 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 6 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 6 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 1 week ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago