OK - thanks @vanq
What we're (jointly) about to say here, might sound contrary to the way in which you've imagined your heat-pump works.
Please don't immediately rush to a specific conclusion because the underlying concepts are more important than "How do I add Homely"!
I'm going to tag @jamespa and @majordennisbloodnok initially, but others might join in.
Your heat pump is unable to perform as it should because it's having external controls imposed upon it.
The present arrangement is what we'd expect to see for a boiler running on gas or oil.
The basic idea is that the Areona 3 is meant to run continuously, and not have thermostats and time-clocks switching it on/off.
Its own native firmware will adjust the Flow to meet the heat demands of the house.
The ground floor UFH manifold needs those valve actuators removed, and replaced with the manual knobs which it probably came with.
Those knobs are then turned so that the flow through each loop is balanced.
That's where the sight-glasses at the top are needed.
Each pipe loop will have a different length, and might also be constrained by having more bends than the others.
You will end up having the manual knob fully open for the longest pipe-loop, which is the one with the most resistance to flow.
By this stage you will be picking up something heavy to throw in my direction...
... because all those thermostatic controls don't come cheap!
You will wondering how the Heat Pump "knows" how much heat to send into each room.
The answer lies in the original Heat Loss Survey which was completed before the system was designed and installed.
The Heat Loss for the whole house has been used to define the required size of the heat-pump itself (in kWh),
and the heat loss for each room is used to define the UFH pipe runs within that room.
The installer calculates for each room:
- the length(s) of pipe required to meet the heat demand
- the distance between each each pipe within the floor
... based on the known temperature of the water leaving the heat pump, which should be around 50°C.
That might not be what actually happened for your particular house, but that's how it's meant to be.
The obvious situation when things won't be right is when a house which has existing UFH changes from using a boiler to a heat-pump.
But we'd need to know more about the history of your installation in order to advise further if that's the case.
Let me stop there and give you a chance to contemplate your next question...
Save energy... recycle electrons!
Currently viewing this topic 1 user ( Toodles ) and 9 guests.
Recently viewed by users: JamesPa 4 minutes ago, Grantmethestrength 18 minutes ago, Transparent 21 seconds ago.
- 26 Forums
- 2,306 Topics
- 51.7 K Posts
- 456 Online
- 5,970 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Extend the colder range of the weather compensation curve?
Not necessarily. Some heat pumps flatline at either en...
By JamesPa , 8 minutes ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
OK - thanks @vanq What we're (jointly) about to say h...
By Transparent , 22 minutes ago
-
RE: Cashback Incentives That Reward Shorter Heat Pump Warranties
This is analogous to the PCP (personal contract purchas...
By Davesoa , 33 minutes ago
-
Threeway Diverter Valve question
I am looking at a few upgrades/fixes to my Grant Aerona...
By Grantmethestrength , 3 hours ago
-
RE: Commencing on an ASHP Installation Process
@benson It will be interesting to see what Homely have ...
By Toodles , 3 hours ago
-
@sheriff-fatman Im well impressed with it for the money...
By bontwoody , 4 hours ago
-
RE: Don’t Install a Heat Pump Until You Read This
@jamespa We have a wood burner, and use it. But one...
By davidnolan22 , 5 hours ago
-
RE: Maintaining temperature on windy day
"done some add on control"??? It's a most elegant solut...
By cathodeRay , 5 hours ago
-
Thank you! I use plotly in python, with the data comi...
By cathodeRay , 6 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Interesting temperatures this morning: this is what I'm...
By AndrewJ , 10 hours ago
-
RE: 10kw heat pump run in 24*7 data?
Vaillant are pretty good maintaining their ...
By JamesPa , 10 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
So this morning marked 24 hours up for installer. Rooms...
By Crimson , 18 hours ago
-
RE: Buffer tank bypass on EDF Ideal heat pump installation
@kevb, many of these companies look for the smallest of...
By Mars , 20 hours ago
-
RE: Electricity price predictions
Simple article with a DENZ graph showing how gas which ...
By Jeff , 22 hours ago
-
RE: Heat Pump on Flat Roof Low Frequency Noise from Detached Neighbor
@davidnolan22 Yes have been communicating woth the neig...
By People_Noise , 22 hours ago
-
Power Cut - Heat Pump Evaporator Iced Up
We have just had a power cut and 1 hour later power was...
By trebor12345 , 23 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
A few weeks ago, I was having a discussion with someone...
By Majordennisbloodnok , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk Hi I see you posted on openenergymon...
By JamesPa , 1 day ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
@editor When do “Mars Heat Pump Installation and Servic...
By Toodles , 1 day ago
-
@morgan Likewise, I realise that some readers will appr...
By Toodles , 1 day ago