@markc The installers put buffer tanks in to stop low flow errors occurring with their badly designed heating systems. It covers their inadequacies, at your cost.
Mars's system is a bivalent system, therefore he gets paid for the renewable heat he produces ONLY. If his running costs are high due to the poorly designed system, he does not get compensated for this. If it was a stand-alone system, the payment would be deemed, based on the EPC figure.
Professional heat pump installer: Technical Director Ultimate Renewables Director at Heacol Ltd
Hi Mark,
I think that you are correct that the DHW valve is not functioning correctly, this is shown by the changes in operation after you lowered the water flow temperature for heating. What appears to be happening now is that the water in your hot water tank is being heated to 50C, at which point the system switches over to heating at 35C. Because the DHW control valve is not closing, water from the ASHP at 35C is still being pumped through the coil in your hot water tank, which of course cools the water in the tank. Since hot water production takes priority over heating, when the water in the tanks falls below the reheat setting the system once more switches over to hot water production at 50C.
First thing to check, there should be a lever on the DHW valve actuator, which can be locked in the open position. Please check by moving the lever backwards and forwards. If the actuator is the type that I think it is, it requires power to open the valve, but the valves closes by spring return when the power is removed. It may be that the actuator has been left in the latched open position.
Please check the above and let me know what you find.
Posted by: @derek-mHi Mark,
I think that you are correct that the DHW valve is not functioning correctly, this is shown by the changes in operation after you lowered the water flow temperature for heating. What appears to be happening now is that the water in your hot water tank is being heated to 50C, at which point the system switches over to heating at 35C. Because the DHW control valve is not closing, water from the ASHP at 35C is still being pumped through the coil in your hot water tank, which of course cools the water in the tank. Since hot water production takes priority over heating, when the water in the tanks falls below the reheat setting the system once more switches over to hot water production at 50C.
First thing to check, there should be a lever on the DHW valve actuator, which can be locked in the open position. Please check by moving the lever backwards and forwards. If the actuator is the type that I think it is, it requires power to open the valve, but the valves closes by spring return when the power is removed. It may be that the actuator has been left in the latched open position.
Please check the above and let me know what you find.
The lever is loose. i.e. I can movie left to right meaning it is open.
As a test this morning when the DHW was at 35º I turned off the DHW heating, made sure the space heating was on and increased the flow temp to 40º. 2 hours later the DHW is at 40º. So what you have described is definitely happening.
Mark,
Move the lever to the valve open position and then let go, it should return to the closed position via spring action. If this is not the case, try holding the lever in the valve closed position and see what affect that has on your system operation.
You should still get your installer back to resolve the problem and if they try to charge for the visit I would be inclined not to pay since they did not fully complete the installation and commissioning of your system in the first place.
Posted by: @heacol@markc That valve you have there is a low flow high-temperature valve, you are throttling your system, effectively it cannot breathe. You need to change it to a full bore 3 port valve for it to work properly.
Thanks for your suggestion Brendon. You clearly have a comprehensive understanding of ASHP systems.
I imagine swapping out that valve in isolation would cause other issues due to how my pipework has been designed.
Posted by: @derek-mMark,
Move the lever to the valve open position and then let go, it should return to the closed position via spring action. If this is not the case, try holding the lever in the valve closed position and see what affect that has on your system operation.
You should still get your installer back to resolve the problem and if they try to charge for the visit I would be inclined not to pay since they did not fully complete the installation and commissioning of your system in the first place.
I've just tried that on another valve that controls flow to the radiators and yes manually opening it (move to the left) is quickly followed by an automatic closing (move to the right).
With the DHW valve in question there is no resistance to the lever left or right so it seems to be permanently open. I've put a call in to the installers (voicemail). As I have a maintenance contract with them this will be covered.
Putting that to one side for the moment, with the DHW turned off, can we get back to your thoughts on the system settings?
Hi Mark,
It would appear that the valve is the problem, here is a video you may find of interest.
I don't think that it will be possible to utilise weather compensation with your present system because of the location of your controller in the utility room.
To fully utilise weather compensation it would first require the addition of a remote sensor, either hardwired or wireless. If you wish to consider this option then please let me know and I will have a detailed look at the manual to guide you through the process.
@markc I can guaranty that your pipework will be wrong. Installing these valves it is the equivalent of driving your car with a potato up its exhaust pipe, and you are blaming the car for not getting above 20 miles per hour and having horrendous fuel consumption.
Professional heat pump installer: Technical Director Ultimate Renewables Director at Heacol Ltd
Mark,
One thing that you could try would be to tap the valve body with a rubber mallet or a block of wood, which may free the valve if it has some dirt stopping if from closing.
Another thing if you feel up to it, would be to switch off the electric supply and remove the cover from the actuator, as shown in the video. Check that the springs are in place and try moving the internal mechanism.
Posted by: @derek-mMark,
One thing that you could try would be to tap the valve body with a rubber mallet or a block of wood, which may free the valve if it has some dirt stopping if from closing.
Another thing if you feel up to it, would be to switch off the electric supply and remove the cover from the actuator, as shown in the video. Check that the springs are in place and try moving the internal mechanism.
Aha! It seems the motor had gotten jammed. After quick manual turning of the little cog with some pliers the valve seems to open and close as expected.
I've just set the DHW heating back on and watched the motor open (the level becoming loose). I'll give it an hour or so and see if the valve closes.
Thanks Derek.
Back to the weather compensation, yes I am interested in trying this out.
Mark,
It is always a good feeling when you solve the problem and fix it yourself.
Once you are certain that the valve problem is resolved, i would suggest that you set your heating water flow temperature to 35C and DHW to 50C again, and monitor your system to see how this affects the COP values. Because of the valve problem, and the original settings by your installer, your system has been operating with a water flow temperature of 50C under all conditions. It will therefore be highly useful to see the different COP values obtained between DHW production and heating. If, as I suspect, it shows quite an improvement in efficiency, it may be cost effective to have the additional equipment installed to provide active weather compensation.
Without wishing to upset 'she who must be obeyed', you could try manually lowering the water flow temperature for heating, to the point where it no longer meets the heat demand. Obviously, because home heating systems respond slowly to changes in temperature, it would be a matter of making a slight adjustment and then waiting several hours to see the effect.
Mark,
A quick question, how did you produce the graphs? Were they derived from your Ecodan controller?
-
Slash Your Heat Pump Bills Overnight
3 months ago
-
Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
4 months ago
-
Ecodan help with efficiency setup and design - removing manifold mixers, LLH and pumps
4 months ago
-
Ecodan wont heat with mild outside temps
5 months ago
-
Auxiliary Heating
10 months ago
- 25 Forums
- 1,439 Topics
- 30.2 K Posts
- 24 Online
- 1,225 Members
Join Us!
Latest Posts
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I don't think so, because Octopus use Daikin and the vo...
By IvanOpinion , 43 mins ago
-
RE: Incorrect Billing of Customers with a Smart Meter
It seems someone else stumbled upon the same issue earl...
By KoRWraith , 11 hours ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 13 hours ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 20 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
But if you compare what was predicted with what happene...
By Majordennisbloodnok , 20 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 1 day ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 2 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 2 days ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 2 days ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 2 days ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 2 days ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
Hi, Bit of an update. I bought a decibel meter and moni...
By Lokisam , 2 days ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
As I mentioned, there are going to be some follow-up ar...
By Majordennisbloodnok , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Now, I know that this may be a little simplistic and pe...
By Toodles , 3 days ago
-
-
RE: Save the Energy Save the World using Daikin Altherma 3 operation mode and schedules settings.
Hello Mevl, I won't be able to answer all your question...
By HCas , 3 days ago
-
I have been watching, with interest, the rebuild and re...
By iantelescope , 3 days ago
-
RE: Making best use of Agile with a battery and ASHP
On the subject of automating battery charging schedules...
By jamesw , 4 days ago
-
Safety update; RCBOs supplying inverters or storage batteries
BEAMA have issued a safety update (March 2024) regardin...
By Transparent , 4 days ago
Heat Pump Humour
Latest Topics
-
Share Your Experiences with Heat Pump Manufacturer Support
By Mars 13 hours ago
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 5 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 5 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 1 week ago
-
Home energy storage & battery register
By Mars 1 week ago
-
Meter Readings - What are theses meters telling me?
By Potatoman 1 week ago
-
Have Octopus Energy discovered a way to Narnia?
By Davesoa 1 week ago