Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @derek-mPosted by: @kev-mNo, I lost it when they installed MMSP in early October! Flow and return temps are available without MMSP and I can still see them in Melcloud. I assume they are from different sensors to the ones on the MMSP energy meter. The meter part of the energy meter is connected to the FTC6.
Hi Kev,
I have just noticed under section '5.1 DIP Switch Functions' of the FTC6 manual, that there are some DIP switches that need to be changed when MMSP is installed. It would appear that SW3-4 and SW3-8 need to be changed from off to on.
@kev-m also note that the manual specifically says that you have to power off the whole system before you flick those dip switches.
Speaking of manuals, here are the links for the MMSP Quick Start Guide and the MMSP Hardware Installation & Configuration Guides. They explain what all the different sensors are that it involves.
https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_MMSP_QSG
https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_MMSP_Application_Guide
Posted by: @justinsbSpeaking of manuals, here are the links for the MMSP Quick Start Guide and the MMSP Hardware Installation & Configuration Guides. They explain what all the different sensors are that it involves.
https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_MMSP_QSG
https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_MMSP_Application_Guide
Thanks Justin. My heat meter is slightly different from that one in that the return sensor fits directly into the meter rather than a t-piece. I do find it a little concerning that not only do I now know what a heat meter is and how it's installed, I also even know the detailed differences between slightly different models from the same manufacturer! Who's have thought it...
Thanks Justin. My heat meter is slightly different from that one in that the return meter fits directly into the meter rather than a t-piece. I do find it a little concerning that not only do I now know what a heat meter is and how it's installed, I also even know the detailed differences between slightly different models from the same manufacturer! Who's have thought it...
Be careful Kev, they say 'a little knowledge can be a dangerous thing'. LOL
Hi Everyone,
Could I ask that if anyone carries out any of the suggestions provided on the forum, that if possible they provide feedback, good or bad, so that others may benefit from their experience.
'All is quiet on the western front', or could it be that everyone is busy adjusting their system to improve efficiency?
Posted by: @derek-m'All is quiet on the western front', or could it be that everyone is busy adjusting their system to improve efficiency?
I think it's just that it's the weekend Derek. Remember them? 😉
Posted by: @kev-mPosted by: @derek-m'All is quiet on the western front', or could it be that everyone is busy adjusting their system to improve efficiency?
I think it's just that it's the weekend Derek. Remember them? 😉
I'm afraid I get confused, since the whole week is a weekend for me. 😋
There is normally an increase in traffic on the forum at the weekend, when people have more time on their hands. It obviously means that they are happy with their system's performance, or are desperately searching for a cheaper tariff. 🙄
@derek-m We are waiting to hear from the developer as we have been told not to touch any controls in the loft otherwise we jeopardise the warranty from Daikin. One neighbour has ignored this and has been changing settings, monitoring the system and feeding this back to the rest of us while we await the developers response. He has just told us he thinks that the back up system is coming on all the time which is costly, as it is set to come on at 0 and he has changed his to -5. We are not sure if this is the case with our system or not and he is going to monitor the change he has made to it over the next few days and feed back to us all so we can jointly pursue the developer to allow us to change our own systems or at least check them to see if they are working efficiently. We suspect not due to energy usage but no choice other than to wait while they respond.
Whilst it’s quiet then 🙂
I just had this from my ASHP installer when I asked them about weather compensation mode - I have a LG Therma V, with UFH downstairs and radiators upstairs. Would welcome feedback on their reply from this audience.
"Hi Dan,
All good here thanks. Glad to hear you’re both on the mend, it’s a tough gig being ill with a little one isn’t it!
When we have rads and UFH working together we tend to find using the weather compensation curve is not particularly effective. It can mean that there’s low temperature water in a convective radiator panel which doesn’t provide sufficient output. Our customers with similar set ups are far happier to hit a set flow temp of 50/55 which ensures the panels convect warm air into the rooms.
You can experiment with using the weather compensation mode to see if it suits, but we would recommend just to keep the set flow temperature. Ultimately the thermostat will turn off once it’s hit the set temp so the heat pump will be operating for a shorter period of time at a slightly higher flow temperature and you’ll find little difference in the ultimate efficiency. You could try adjusting the set back temperature by a few degrees which would mean the temperature in the house is maintained.
Hope that makes sense and do come back to me if there are any further issues re. upstairs heating."
Posted by: @littlered@derek-m We are waiting to hear from the developer as we have been told not to touch any controls in the loft otherwise we jeopardise the warranty from Daikin. One neighbour has ignored this and has been changing settings, monitoring the system and feeding this back to the rest of us while we await the developers response. He has just told us he thinks that the back up system is coming on all the time which is costly, as it is set to come on at 0 and he has changed his to -5. We are not sure if this is the case with our system or not and he is going to monitor the change he has made to it over the next few days and feed back to us all so we can jointly pursue the developer to allow us to change our own systems or at least check them to see if they are working efficiently. We suspect not due to energy usage but no choice other than to wait while they respond.
Hi LittleRed,
Has anyone carried out the simple test that I suggested? Please ask your neighbour, who appears to be more proactive, to measure the ambient air temperature well away from his ASHP, and then to measure the air temperature at the rear of his ASHP.
If there is a difference in temperature then your heat pumps may be sitting in a 'cold well', in that they are pulling the cold air coming out of the front, back into the rear. This may be the cause of your backup heaters operating. What is your energy usage like on warmer days?
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
7 hours ago
-
Running my new Nibe ASHP efficiently
2 months ago
-
Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
7 months ago
-
Ecodan consuming 100kwh per day in new build!!!
8 months ago
-
Help with understanding my Mitsubishi Ecodan air source heat pump
11 months ago
Currently viewing this topic 2 guests.
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 300 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 2 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 3 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 5 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 6 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 7 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 7 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 8 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 9 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 11 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 11 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 13 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 14 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 14 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 15 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago