Ecodan Controller Placement?
Does the location of the controller affect the settings, i.e compensation curve?
Our controller is located with the tank in a 'boiler cupboard' which as expected stays reasonably warm. Whenever I check the app it claims the temperature in both zone 1 and 2 to be 22'c whilst at the same time the thermostats will be saying 16'c so I'm assuming it's getting the reading from the main controller and not the thermostats?
Any way around this or just switch to fixed flow setting?
Posted by: @walsham_mattDoes the location of the controller affect the settings, i.e compensation curve?
Our controller is located with the tank in a 'boiler cupboard' which as expected stays reasonably warm. Whenever I check the app it claims the temperature in both zone 1 and 2 to be 22'c whilst at the same time the thermostats will be saying 16'c so I'm assuming it's getting the reading from the main controller and not the thermostats?
Any way around this or just switch to fixed flow setting?
If your thermostats are of the on - off variety, they do not send a temperature measurement to the Ecodan controller.
The Ecodan controller does contain a thermistor for temperature measurement and display, but it is only used for heat pump control when operating in Auto Adaptation (AA) mode. If your system is operating in Weather Compensation (WC) mode, the controller adjusts the Leaving Water Temperature (LWT) based upon the outside air temperature measurement and the settings of the WC curve.
With your present setup, it would probably be best to operate in WC mode, and adjust the settings of the WC curve to match the characteristics of your home. If you have radiators then start with WC settings of 50C LWT at -5C outside air temperature and 25C LWT at 20C outside air temperature. If you only have UFH then try setting the cold end of the WC curve at 40C LWT at -5C outside air temperature.
Then set any thermostats to 2C above the desired indoor temperature, and fully open any TRV's located in the living area, but not the bedrooms.
If the indoor air temperature increases, then lower the WC setting at the cold end, obviously do the opposite if the indoor air temperature falls.
There's a setting in the menus somewhere to use remote thermistors, but I think it only works if they're either on a long wire from the controller, or are Mitsubishi remote units.
Third party thermostats just send on/off signals, as described.
I got my installer to relocate my controller and replace my 3rd party (on off) room stat with the wireless Mitsubishi which is now set up as the room temp stat. I now have modulating auto adaptive control and weathe compensation. From the convenience of either my kitchen or lounge.
my argument was the installation did not give me the full functionality of the system.
We have 2 thermostats (1 in the master bedroom - right next to the 'boiler cupboard' and 1 in the downstairs hallway - right next to the front door).
From memory they are Honeywell thermostats (I'll check when I get back) and were installed by Lovell's before we moved in. I'm able to set temperature and daily programs from them which the pump seems to respond to.
If it would help I'll ask Lovell's to provide a wireless Mitsubishi unit but only if I know it'll help.
Regarding the WC setting...we've been using the above suggested settings for the past 4/6 weeks and haven't noticed a great deal of difference. Particularly downstairs it seems to never reach the called for temp even when left for hours. This weekend for example we left the house at 3:30pm with the thermostat showing 16.5'c...before we left I turned it up to 18'c so that when we returned in 2/3 hours the house would be warm...but when we had got back the temp had dropped to 16'c. I know the DHW hadn't been on as that's on a timer.
I don't really want the temp at night above 16.5/17'c as A. it's too warm and B. too expensive but it takes what seems like a lifetime to then get back to a decent temp. The wife is getting pretty fed up with daily bills being well in excess of £10 a day whilst still being cold, so much so she's started to consider putting in a wood burner which defeats the purpose of an eco ASHP.
Posted by: @walsham_mattWe have 2 thermostats (1 in the master bedroom - right next to the 'boiler cupboard' and 1 in the downstairs hallway - right next to the front door).
From memory they are Honeywell thermostats (I'll check when I get back) and were installed by Lovell's before we moved in. I'm able to set temperature and daily programs from them which the pump seems to respond to.
If it would help I'll ask Lovell's to provide a wireless Mitsubishi unit but only if I know it'll help.
Regarding the WC setting...we've been using the above suggested settings for the past 4/6 weeks and haven't noticed a great deal of difference. Particularly downstairs it seems to never reach the called for temp even when left for hours. This weekend for example we left the house at 3:30pm with the thermostat showing 16.5'c...before we left I turned it up to 18'c so that when we returned in 2/3 hours the house would be warm...but when we had got back the temp had dropped to 16'c. I know the DHW hadn't been on as that's on a timer.
I don't really want the temp at night above 16.5/17'c as A. it's too warm and B. too expensive but it takes what seems like a lifetime to then get back to a decent temp. The wife is getting pretty fed up with daily bills being well in excess of £10 a day whilst still being cold, so much so she's started to consider putting in a wood burner which defeats the purpose of an eco ASHP.
Check and set the WC curve as shown in the video below. Try initial settings of 50C LWT at -5C outside air temperature and 25C LWT at 20C outside air temperature.
Once completed open fully any TRV's in the living areas, and set any thermostats to 1C above the desired temperature.
Leave the system running for a few hours then report back what has happened to the indoor temperatures.
My Ecodan controller is wall mounted beside the main box in the same (airing) cupboard as the DHW tank. However I am set up for WC and adjust room temp' via a Mitsubishi wireless remote in the hall. I would like to try Auto Adaptation to see if financial savings can be had. Does my set up as described preclude or allow auto adaptation?
One single remote thermostat, single zone all to radiators.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
Posted by: @morganMy Ecodan controller is wall mounted beside the main box in the same (airing) cupboard as the DHW tank. However I am set up for WC and adjust room temp' via a Mitsubishi wireless remote in the hall. I would like to try Auto Adaptation to see if financial savings can be had. Does my set up as described preclude or allow auto adaptation?
One single remote thermostat, single zone all to radiators.
Should be fine. You need to make sure that the Room Sensor setting is set to "Main RC". It's on the menu under Initial Settings (the little cog wheel). You also need to enable Auto Adaptation via a dip switch. SW5-2. The default is enabled (mine was enabled)
Have you tried just changing to Room Temp mode on the main controller in the airing cupboard? If the two above things are in place it should just work. You'll know because the first thing that will happen is your radiators will get much hotter for a couple of days.
Posted by: @morgan@kev-m Oh, dip switches! I don't have the confidence to take the front off that box.
Just try room temp mode without looking at the dip switches. If it's not set to auto adapt I think it'll just act like a dumb thermostat like it's doing now. If you want to know if it is on AA, turn up the temp a couple or three degrees and the radiators will get hotter. If it isn't, they won't.
Posted by: @kev-mPosted by: @morgan@kev-m Oh, dip switches! I don't have the confidence to take the front off that box.
Just try room temp mode without looking at the dip switches. If it's not set to auto adapt I think it'll just act like a dumb thermostat like it's doing now. If you want to know if it is on AA, turn up the temp a couple or three degrees and the radiators will get hotter. If it isn't, they won't.
In WC atm and if I turn the temp up on the thermostat (Mitsubishi wireless) the radiators get hotter.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
-
Installing your own ASHP - DIY
2 weeks ago
-
New Installation - Grant Aerona 3 + 210L Hot Water Cylinder
4 weeks ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 months ago
-
ASHP heating issues / error code - advice very much appreciated
2 months ago
-
Ecodan DHW Settings missing
2 months ago
- 25 Forums
- 1,438 Topics
- 30.1 K Posts
- 30 Online
- 1,223 Members
Join Us!
Latest Posts
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I find increasingly staggering that the MCS rules don't...
By JamesPa , 25 seconds ago
-
-
RE: Save the Energy Save the World using Daikin Altherma 3 operation mode and schedules settings.
Hello Mevl, I won't be able to answer all your question...
By HCas , 6 hours ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@ianmk13 It just depends on individual circumstances. I...
By bontwoody , 7 hours ago
-
RE: Spacing for roof fixing bolts ?
@heat-pump-newbie I don’t see why they shouldn’t show a...
By Mars , 19 hours ago
-
I have been watching, with interest, the rebuild and re...
By iantelescope , 19 hours ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@elton, @kenbone has a lot of Samsung ASHP experience a...
By Mars , 19 hours ago
-
RE: Making best use of Agile with a battery and ASHP
On the subject of automating battery charging schedules...
By jamesw , 20 hours ago
-
Safety update; RCBOs supplying inverters or storage batteries
BEAMA have issued a safety update (March 2024) regardin...
By Transparent , 1 day ago
-
RE: Incorrect Billing of Customers with a Smart Meter
Yes, that's the point I'm making in this topic. The B...
By Transparent , 1 day ago
-
RE: Home energy storage & battery register
Hanchu ESS - Home-ESS-LV9.4K (9.4kWh)
By IRMartini , 2 days ago
-
RE: Insulation of flow and return Heat Pump piping
@dr_dongle I saw a YouTube presentation from one of ins...
By Toodles , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@editor Oh Mars, just as I was becoming interested … To...
By Toodles , 2 days ago
-
Are You Getting the Most Out of Your Renewable Energy?
This article is aimed at you if you have recently taken...
By Majordennisbloodnok , 3 days ago
-
It is certainly possible, using a modbus connection. If...
By cathodeRay , 3 days ago
-
I did another reconnection/ reconfiguration session wit...
By Abernyte , 4 days ago
-
RE: Recommended ASHP installers in Hampshire
@benson After my initial enquiries with Octopus, we had...
By Toodles , 4 days ago
-
RE: Air source heat pump roll call
To help bolster the rather small number of NIBE owners ...
By Steve D , 4 days ago
-
RE: A beginner's journey into DIY home energy storage - no solar!
@editor All good here! I'm happy to say that the system...
By KoRWraith , 5 days ago
-
RE: Say hello and introduce yourself
@fse_bec welcome to the forums, and it’s very generous ...
By Mars , 5 days ago
Heat Pump Humour
Latest Topics
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 2 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 2 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 5 days ago
-
Home energy storage & battery register
By Mars 5 days ago
-
Meter Readings - What are theses meters telling me?
By Potatoman 6 days ago
-
Have Octopus Energy discovered a way to Narnia?
By Davesoa 6 days ago
-
Making best use of Agile with a battery and ASHP
By jamesw 1 week ago