Ecodan Controller Placement?
Does the location of the controller affect the settings, i.e compensation curve?
Our controller is located with the tank in a 'boiler cupboard' which as expected stays reasonably warm. Whenever I check the app it claims the temperature in both zone 1 and 2 to be 22'c whilst at the same time the thermostats will be saying 16'c so I'm assuming it's getting the reading from the main controller and not the thermostats?
Any way around this or just switch to fixed flow setting?
Posted by: @walsham_mattDoes the location of the controller affect the settings, i.e compensation curve?
Our controller is located with the tank in a 'boiler cupboard' which as expected stays reasonably warm. Whenever I check the app it claims the temperature in both zone 1 and 2 to be 22'c whilst at the same time the thermostats will be saying 16'c so I'm assuming it's getting the reading from the main controller and not the thermostats?
Any way around this or just switch to fixed flow setting?
If your thermostats are of the on - off variety, they do not send a temperature measurement to the Ecodan controller.
The Ecodan controller does contain a thermistor for temperature measurement and display, but it is only used for heat pump control when operating in Auto Adaptation (AA) mode. If your system is operating in Weather Compensation (WC) mode, the controller adjusts the Leaving Water Temperature (LWT) based upon the outside air temperature measurement and the settings of the WC curve.
With your present setup, it would probably be best to operate in WC mode, and adjust the settings of the WC curve to match the characteristics of your home. If you have radiators then start with WC settings of 50C LWT at -5C outside air temperature and 25C LWT at 20C outside air temperature. If you only have UFH then try setting the cold end of the WC curve at 40C LWT at -5C outside air temperature.
Then set any thermostats to 2C above the desired indoor temperature, and fully open any TRV's located in the living area, but not the bedrooms.
If the indoor air temperature increases, then lower the WC setting at the cold end, obviously do the opposite if the indoor air temperature falls.
There's a setting in the menus somewhere to use remote thermistors, but I think it only works if they're either on a long wire from the controller, or are Mitsubishi remote units.
Third party thermostats just send on/off signals, as described.
I got my installer to relocate my controller and replace my 3rd party (on off) room stat with the wireless Mitsubishi which is now set up as the room temp stat. I now have modulating auto adaptive control and weathe compensation. From the convenience of either my kitchen or lounge.
my argument was the installation did not give me the full functionality of the system.
We have 2 thermostats (1 in the master bedroom - right next to the 'boiler cupboard' and 1 in the downstairs hallway - right next to the front door).
From memory they are Honeywell thermostats (I'll check when I get back) and were installed by Lovell's before we moved in. I'm able to set temperature and daily programs from them which the pump seems to respond to.
If it would help I'll ask Lovell's to provide a wireless Mitsubishi unit but only if I know it'll help.
Regarding the WC setting...we've been using the above suggested settings for the past 4/6 weeks and haven't noticed a great deal of difference. Particularly downstairs it seems to never reach the called for temp even when left for hours. This weekend for example we left the house at 3:30pm with the thermostat showing 16.5'c...before we left I turned it up to 18'c so that when we returned in 2/3 hours the house would be warm...but when we had got back the temp had dropped to 16'c. I know the DHW hadn't been on as that's on a timer.
I don't really want the temp at night above 16.5/17'c as A. it's too warm and B. too expensive but it takes what seems like a lifetime to then get back to a decent temp. The wife is getting pretty fed up with daily bills being well in excess of £10 a day whilst still being cold, so much so she's started to consider putting in a wood burner which defeats the purpose of an eco ASHP.
Posted by: @walsham_mattWe have 2 thermostats (1 in the master bedroom - right next to the 'boiler cupboard' and 1 in the downstairs hallway - right next to the front door).
From memory they are Honeywell thermostats (I'll check when I get back) and were installed by Lovell's before we moved in. I'm able to set temperature and daily programs from them which the pump seems to respond to.
If it would help I'll ask Lovell's to provide a wireless Mitsubishi unit but only if I know it'll help.
Regarding the WC setting...we've been using the above suggested settings for the past 4/6 weeks and haven't noticed a great deal of difference. Particularly downstairs it seems to never reach the called for temp even when left for hours. This weekend for example we left the house at 3:30pm with the thermostat showing 16.5'c...before we left I turned it up to 18'c so that when we returned in 2/3 hours the house would be warm...but when we had got back the temp had dropped to 16'c. I know the DHW hadn't been on as that's on a timer.
I don't really want the temp at night above 16.5/17'c as A. it's too warm and B. too expensive but it takes what seems like a lifetime to then get back to a decent temp. The wife is getting pretty fed up with daily bills being well in excess of £10 a day whilst still being cold, so much so she's started to consider putting in a wood burner which defeats the purpose of an eco ASHP.
Check and set the WC curve as shown in the video below. Try initial settings of 50C LWT at -5C outside air temperature and 25C LWT at 20C outside air temperature.
Once completed open fully any TRV's in the living areas, and set any thermostats to 1C above the desired temperature.
Leave the system running for a few hours then report back what has happened to the indoor temperatures.
My Ecodan controller is wall mounted beside the main box in the same (airing) cupboard as the DHW tank. However I am set up for WC and adjust room temp' via a Mitsubishi wireless remote in the hall. I would like to try Auto Adaptation to see if financial savings can be had. Does my set up as described preclude or allow auto adaptation?
One single remote thermostat, single zone all to radiators.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @morganMy Ecodan controller is wall mounted beside the main box in the same (airing) cupboard as the DHW tank. However I am set up for WC and adjust room temp' via a Mitsubishi wireless remote in the hall. I would like to try Auto Adaptation to see if financial savings can be had. Does my set up as described preclude or allow auto adaptation?
One single remote thermostat, single zone all to radiators.
Should be fine. You need to make sure that the Room Sensor setting is set to "Main RC". It's on the menu under Initial Settings (the little cog wheel). You also need to enable Auto Adaptation via a dip switch. SW5-2. The default is enabled (mine was enabled)
Have you tried just changing to Room Temp mode on the main controller in the airing cupboard? If the two above things are in place it should just work. You'll know because the first thing that will happen is your radiators will get much hotter for a couple of days.
@kev-m Oh, dip switches! I don't have the confidence to take the front off that box.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @morgan@kev-m Oh, dip switches! I don't have the confidence to take the front off that box.
Just try room temp mode without looking at the dip switches. If it's not set to auto adapt I think it'll just act like a dumb thermostat like it's doing now. If you want to know if it is on AA, turn up the temp a couple or three degrees and the radiators will get hotter. If it isn't, they won't.
Posted by: @kev-mPosted by: @morgan@kev-m Oh, dip switches! I don't have the confidence to take the front off that box.
Just try room temp mode without looking at the dip switches. If it's not set to auto adapt I think it'll just act like a dumb thermostat like it's doing now. If you want to know if it is on AA, turn up the temp a couple or three degrees and the radiators will get hotter. If it isn't, they won't.
In WC atm and if I turn the temp up on the thermostat (Mitsubishi wireless) the radiators get hotter.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
They should only get as hot as the WC target if you're on WC. If you're in AA they will get a lot hotter than that.
-
ASHP install contract and BUS grant money
6 days ago
-
Oversized Ecodan
1 week ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 week ago
-
Ecodan consuming 100kwh per day in new build!!!
2 weeks ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 weeks ago
- 21 Forums
- 1,964 Topics
- 42.6 K Posts
- 41 Online
- 2,278 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Towel rails. An unexpected final hurdle
I had a similar issue but convinced the installer to le...
By Pie_Eater , 33 minutes ago
-
Cliff, welcome to the forum. You’re running into one ...
By Mars , 40 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
This whole discussion highlights just how much of a mes...
By Mars , 52 minutes ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
@cheshirejohn thanks for the update and for sharing. I’...
By Mars , 1 hour ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa @bontwoodyHeat loss calculations found and att...
By BAMi , 3 hours ago
-
RE: Setback savings - fact or fiction?
Here's the same plot, less the R squared values, done q...
By cathodeRay , 4 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 4 hours ago
-
@robs useful thread! Thanks for sharing - Octopus are c...
By big_si , 4 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 6 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 7 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 8 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 12 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 1 day ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 2 days ago
Latest Topics
-
By cliffhanger 53 minutes ago
-
Heat Pump Sizing & Installation Costs
By Mars 14 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 15 hours ago
-
SolarPV tables / online calculator
By MichelleC 22 hours ago