Three months and two deep freezes later and I'm pretty happy with how my Daikin heat pump is running.
It is now running on what Heat Geek's Adam Chapman calls 'Pure Weather Compensation' and Daikin call 'Leaving Water Temperature control' on a 'home made' design temperature of 38º @ -3º . Today it was -3 when I woke up and the house is a comfortable 22º. I'm fairly sure it will cope with 37º @ -3º if not 36º.
For those who didn't see my original post when choosing an installer it's here. I chose Octopus for cost and because as soon as I met the technical team (as opposed to the nice heat loss surveyor) I was very impressed with their keenness and understanding of heat pumps.
I argued unsuccessfully against the Octopus 50º design temperature and then lobbied hard for radiator upgrades that weren't originally specified. I learned as much as I could, mostly from the experts in this very forum, and in my head designed for a 40º flow temperature with my radiator lobbying.
Just to recap my home is a bungalow of about 89sqm built into a hill with a big cellar (partially) on the ground floor and a garage with a utility room/space inside (freezer, washing machine, tumble dryer etc.,) both of which were excluded from the measuring & heat loss. Loft insulation 300mm and very patchy/holey cavity insulation. The 28sqm living room is effectively on the 1st floor and pretty exposed. The 180litre tank is in the cellar back-to-back with the 6kw Daikin heat pump. The hall is a square room used for play and workouts in the centre of the house and I argued against the MCS guideline of 18º for 21º. I also had one bedroom designed for 21º as it is used for an office.
I started off using the Madoka as a room thermostat alongside weather compensation. I have no monitoring equipment except the Octopus app which tells me my electrical consumption and the flow temp/speed etc sensors on the MMI monitor. I found this combination of Madoka/WC erratic. My electricity use was, at times, up and down like a yo yo no matter how I tweaked the curve. What suited one OAT didn't suit another - the heat pump would switch on and off.
Finally, a month after owning the heat pump I switched to LWT control and ditched the Madoka - it just no longer controls the pump. Houston we had lift off! This method is genius and Daikin seem to have designed this very well. I'm impressed. No ups and downs in the Octopus electricity consumption just super smooth sub 200-300w lines most of the time. No cycling. The heat pump never turns off. The flow rate is usually very low at around 7-9 litres pm except when it does defrosts and it shoots up to 29 litres.
Recently I started experimenting with a small night time set back. If Daikin are very good at the tech, they are famously dire at writing manuals or offering access to information. There is nothing on how to programme a set-back on LWT control, zilch, nada, nix - bearing in mind room temperatures are not part of the equation.
Eventually I discovered that you can tweak the overshoot number +/- 1º or whatever. This also very usefully permits testing of the 'design temperature' without restarting the heat pump. If it runs well at the room temperature you prefer on the chosen minus (or +) degree number you can programme the left side of the curve accordingly. Easy peasy!
Oh, and even in the 'Big Freeze' it doesn't run the defrost very often and today I actually saw it (it's very quiet). 😁
Radiator design things to note:
I kept my trendy towel rail in the shower room and added my own designer radiator. It was really hard finding a small radiator with a high output for low temp. heating.
Solution: Nordic Omega Aluminium 790mm x 660mm - Italian made, kicks out the heat and it's a very stylish 'designer radiator' with vertical convection fins on both ends. Everyone both designer and techie has admired it including Octopus. Sadly, no VAT reclaim for a self-install which is crap.
When looking for radiators use an online calculator to convert from the standard 50º delta T - I converted to 20º delta T - which provides a rough capability estimate for a 40º flow temp according to HG. (It clearly works).
Big beastie K3s 'disappear' (to a degree) if you paint them exactly the same colour as the walls. I use Tikkurila Optiva 3 (super matt paint) on the walls tinted to my chosen colour and Tikkurila Helmi 10 on the radiator and woodwork. Tikkurila is a Finnish brand, not cheap but cheaper than Little Greene etc., and tint-able to any colour. The numbers are the sheen levels and it is super tough and water-based.
I knew my install team were good - the quality of workmanship is meticulous, they weren't threatened by female geekiness, they listened, they are heat pump evangelists, they worked hard and long hours but were easy going and great fun to have in the house for a week. Every single one of them has been promoted recently.
To sum up..... ditch those thermostats - you really don't need them except as fairy wheels in the beginning. Oh, and mercury rules OK! 🫢😁😂
Glad to hear it all went well; I wanted to use Octopus for all the reasons you have experienced, it was just that at the time of the survey, they had not progressed to the point where my installation would have been ‘within scope’ as they put it then. Very good chaps and I have always found their teams on the road and in the offices to be excellent. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@lucia And just to add, the Daikin ASHP is very good but it is a shame their manuals and their programmers are such cr@p. Ours is controlled by Homely now but the installers fitted the MMI and a stupidly dumb Neo thermostat initially! As soon as Homely came along for the Daikin EDLA08 with a secondary pump - with jumped for it! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@lucia Further, I would like to add that using WC on the Daikin is impressively good at maintaining a constant IAT - except at the extremes (particularly on the milder end) where I found manual tweaking was required sometimes. Mind you, we are super fussy in our requirement of 22.5 degrees C at all times and not deviating by more than 0.5 degrees! Very happy with the system - just the appalling energy prices tagged to the possible use of gas in generation plants! Kill the Spark Gap I say! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@lucia Thanks for the update post installation. Also, thanks for posting the link to the original thread. I must have missed that completely. Going through that thread in detail made me realise that the quote I have received from Aira may not that different from Octopus after all. If Octopus insist on 50 degrees flow temperature, then I think there shouldn't be more than two radiators changes in our case. I did play around with Heat Punk and heat loss of most of our rooms are well below the radiator outputs at 50 degrees flow temperature.
Aira is happy to offer two radiator changes as part of the original discounted quote, but their prices are still slightly higher. I was leaning towards Octopus as their online quite is for replacing as many radiators as needed for our home after the survey, but still much cheaper than Aira. And Aira confirmed that their quote includes 15 year warranty and I don't have to pay for annual servicing. The first figure Aira quoted for any radiator changes needed was almost double Octopus' quote. I couldn't justify that much of a price differential. But, if Octopus aren't going to change any radiators due to their design, then probably the quotes are kind of similar.
Or maybe, I should go with Octopus but just ask for more radiator changes so that I can tweak the flow temperature post installation like you did. Either way, thanks for the very useful update.
16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
@boycey The Homely price was £370 plus fitting but I can’t work that component out as it was contained within a day’s labour whilst other installation work was been carried out. As to how it works … Very Well!
OK, to be more helpful: The Homely controller interfaces with the heat pump’s control circuitry via Modbus. In the case of Daikin, there is a D.comm unit and the Homely talks to this and the control signals are sent to the heat pump using P1 and P2 connections. Homely constantly monitors many parameters and controls the flow temperature, monitors the OAT, the IAT, the delta T of the heat pump’s circuit. Homely also makes allowances for solar gain, uses TOU tariffs if required and proactively adjusts the heat pump having ‘learnt’ the system’s needs and your comfort requirements over a week or so. As Evergreen Energy explain it, it is like having an engineer micromanaging your heat pumps 24/7. My installation is in the airing cupboard, has 2 PSU’s on 13 amp plug bases that power the Homely unit itself and the other for the D.Comm unit. There is a ‘node’ (temperature and light sensor) that you place in your favoured room such as the sitting room and this communicates to the Homely controller via Zigby. The app is available for IOS and Android and allows for all the programming of schedules, temperatures, TOU tariffs and other preferencces too. See my review on RHH which I will post presently. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@boycey The Homely Review may be seen at:
https://renewableheatinghub.co.uk/homely-smart-controller
Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@boycey Sorry, but apart from my provider’s energy bills that are for all consumption, no. The Onecta app is next to useless and I do not have any meaningful long term energy use trends* as before I moved to Octopus, I was with a provider who could / would not read my meters or provide sensible billing details. From my own calculations, I am using less energy now on electricity only than when I was on gas as well and had a gas boiler for heating.
*I have made so many changes and improvements to our property over the last 3 or 4 years that I feel the situation has been a moving target. Please see:
for just some of the improvements.
My gut feeling is that as I have spent / invested £Many on Solar, Battery, ASHP, Insulation etc., I ‘must’ be paying less than I did for heating when on gas and even less now with Homely.😉 Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@lucia And even further… I have rarely been out in the garden at the right time to notice a defrost cycle but yesterday I just happened to pass the pump and noticed a very impressive plume of steam! I checked on the Homely dashboard today and noted that with the OAT hovering around zero degrees C for the whole 24 hours, the pump defrosted 10 times and takes approx. 8 minutes from start to finish. Once or twice over the last year or so, I have noticed a cold area at the base of the radiator panels for a few minutes then we are back in business. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles I've not been able to catch a defrost so recorded a time lapse video (view with link, file is mp4 about 44MB).
This was taken at 1 second intervals over about an hour from 8am to 9am. Running time is about 2.5 minutes. The outside air temperature was 2C.
A bit like watching paint dry but you can see several defrost cycles over the time period. It had already done a few before I set up the camera. Nothing to celebrate as each cycle represents use of a lot of electricity.
Mike
Grant Aerona HPID10 10kWh ASHP
-
Daikin Error Code 7H05
2 months ago
-
Are Octopuses Slowing Consumer Adoption of Heat Pumps?
4 months ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
4 months ago
-
Daikin COP / energy used measurement from MMI
10 months ago
-
Do I need a bigger volumizer: 8kW Daikin Altherma R32 LT split
11 months ago
- 21 Forums
- 1,875 Topics
- 40.9 K Posts
- 19 Online
- 2,196 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump? Or already have one but it’s not performing as it should? Rob is here to help!
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
Latest Posts
-
RE: Vaillant Arotherm ASHP gets noisier when it gets colder outside
I didn’t hear any problem with that noise it was less t...
By Judith , 6 hours ago
-
RE: New Project! ASHP, Solar PV + Battery, MVHR!
@editor yes please Mars, that would be fantastic.
By nickmorgan , 7 hours ago
-
Struggling to Find a Top Heat Pump Installer? We Can Connect You With the Best Installers in the UK
We know from homeowner’s posts and emails how stressful...
By Mars , 9 hours ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathoderay Our 01.00 to 06.00 electricity tariff is go...
By Cathyem1 , 9 hours ago
-
-
RE: Recommendation for Consultants in West Yorkshire for 1850's House Installation
Welcome to the forums. I’ll connect you some recommende...
By Mars , 9 hours ago
-
RE: Large ASHP recommendations for listed house
I’ll connect you via email (using the email address you...
By Mars , 9 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
An update - got through to a helpful Octopus employee, ...
By samiebon1 , 10 hours ago
-
There should be no significant change in the load on th...
By JohnR , 11 hours ago
-
RE: Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
@ajbevster If it's fully pushed in yes, better if it...
By JamesPa , 11 hours ago
-
RE: Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
@heatgeek Thank you, yes this is quite a meal and I'...
By Uk_pete_2000 , 12 hours ago
-
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Its the actual flow rate, after you have bypassed the b...
By JamesPa , 15 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
@lokisam Thank you for reply. I have posted here bef...
By Dwynwen , 18 hours ago
-
RE: Is My Midea Heat Pump Inherently Defective?
Absolutely, I am very aware of that! Moving to a fan co...
By cathodeRay , 19 hours ago
-
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@odynsfee Hi, I only just saw your post. Sorry to hear ...
By Lokisam , 1 day ago
-
RE: Best way to heat and store hot water with ASHP and Solar - am I being stupid?
@nickmorgan you’re absolutely spot on with your thinkin...
By Mars , 1 day ago
-
RE: Grant Aerona3 with Octopus Cosy tariff
Unless I completely misunderstood you (in which case ap...
By JamesPa , 1 day ago
Latest Topics
-
By bretix 14 hours ago
-
Large ASHP recommendations for listed house
By Greenlover75 16 hours ago
-
VisitaHeatPump Participants - Guidance Please
By Toodles 2 days ago
-
By KundK 2 days ago
-
Pipes and cables exposed on roof
By MichelleC 2 days ago
-
By Silverkop 3 days ago
-
Baxi Air Source Heat Pump tips and tricks please
By Cathyem1 3 days ago