buffer/volumizer cupboard space eater, do i need one?
if i have about 13 rads, long runs of 28mm into 22mm, min 15mm to rads 4 bed house with a heat loss of 5.58-6.8kw why do at least 2 of the companies ive had round want to put these in? after watching Heat Geek vids it seems better to run direct?
It rather suggests to me that any company that is wanting to install a buffer in that size of system is placing themselves on the rejected companies list! (Sticking to KISS is best!) Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @adamkif i have about 13 rads, long runs of 28mm into 22mm, min 15mm to rads 4 bed house with a heat loss of 5.58-6.8kw why do at least 2 of the companies ive had round want to put these in? after watching Heat Geek vids it seems better to run direct?
I agree with @toodles. By way of a direct answer to your question, so you have a good reason to reject them and look elsewhere.
I adopted the approach of telling prospective installers before they quoted that I wouldn't accept a buffer, llh or phe for system separation, although I was prepared to accept a 2 port volumiser.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I'll rock the boat as I've got a buffer tank as part of an installation of similar size to what is proposed and reckon that it's one factor in getting an average COP of well over 5 since October (Vaillant's numbers say a COP of 6 but I feel that's optimistic, perhaps due to accuracy of measurement). The buffer tank lets the heat pump do what it thinks is best while I can adjust the flow around the house to what seems to work most efficiently. The extra water capacity provided by the buffer also helps with defrosting and avoids short cycling.
@johnr what’s the size of the buffer tank? With a COP like that it’s likely very well balanced pre and post buffer.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editor@johnr what’s the size of the buffer tank? With a COP like that it’s likely very well balanced pre and post buffer.
50 litres https://www.telford-group.com/product/tempest-heat-pump-indirect-50l-buffer-copy
But a flow temperature of less than 35C must be a major contributor to the good COP.
Posted by: @johnrPosted by: @editor@johnr what’s the size of the buffer tank? With a COP like that it’s likely very well balanced pre and post buffer.
50 litres https://www.telford-group.com/product/tempest-heat-pump-indirect-50l-buffer-copy
But a flow temperature of less than 35C must be a major contributor to the good COP.
You are right, the very low flow temp is the major contributor to good COP. Also, at low flow temperatures, the potential penalty of a buffer is less.
There is nothing wrong in principle with buffers, but many, perhaps most, are it seems, badly installed/badly controlled. This being the case they are best avoided in almost all domestic situations.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
one installer said the extra tank was for the defrost cycles. could that be a volumizer then?
We have a 26L volumiser. I invited a potential installer to leave (to save his time!) if he was proposing a 4 port buffer. They came back (having talked to the boss) offering just a volumiser (aka. 2 port buffer). Our system works well! COP of ~6 in warm weather like now, ~3 in the cold snap.
Volumisers can be smaller than low loss headers (aka 4 port buffers often shortened to buffer), so take up less space with no apparent performance penalty.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @adamkone installer said the extra tank was for the defrost cycles. could that be a volumizer then?
Absolutely could be a volumiser and thats what I would recommend if the extra system volume is needed to meet the minimum requirement.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamkone installer said the extra tank was for the defrost cycles. could that be a volumizer then?
Absolutely could be a volumiser and thats what I would recommend if the extra system volume is needed to meet the minimum requirement.
Agreed, but I would say we need to do far more than just meet the minimum recommended requirement. We have a similarly sized system to @adamk (12 large radiators, 28mm primaries, 22mm CH pipework dropping to 15mm into the rads) and we also have a 50L volumiser installed. This gives us a total system volume of around 200L. The minimum recommended system volume for our ASHP is 50L (but that is a minimum recommended volume) so we would have been 3 times over this without the volumiser yet they still installed one. The extra volume certainly helps during defrost cycles if the heat pump takes heat from the system to defrost itself.
Take a look at this recent video:
So... where would you install the volimiser? See choices in the attached sketch. I think this will help to resolve some nagging inconsistencies in previous statements on various forums.
From my perspective I think there is only one correct answer with justifiable reasoning. However what do you think......?
@toodles @jamespa @judith @old_scientist @editor @adamk @johnr
@anyone
There are 7 options in the sketch labelled A to G. The layout has been elongated to give some space and is a simple heating and DHW system with 28mm primaries dropping to 22mm after the first tee.it is supposed to show a three port valve for the DHW. It shows only 6 radiators but could be 12 or 15 radiators. Assume existing volume to be 150 litres.
Would be interesting to see reasoning for your choice/choices.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 60 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 17 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 24 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 1 hour ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 2 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 3 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 14 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 17 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 19 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 21 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 22 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 23 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 3 hours ago
-
SolarPV tables / online calculator
By MichelleC 10 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 22 hours ago
-
By Toodles 2 days ago