Thanks for the pointers. 

Regarding the bypass valve, I assume winding it in will effectively shut it off for now would it?

The diverter valve is operating correctly now, the first installer got it wrong but was corrected soon after. 

The BUH has only operated once, in the cold snap at the end of November but that was when the thermostat kept interrupting the running of the pump so it wasn't operating effectively. It didn't operate for the whole of December according to the stats in the controller but I can isolate it via a FCU so I'll take that advice. 

COP for the last few days is 3.4 which I think is pretty reasonable but it has been very mild. 


   
ReplyQuote
(@saenergy)
Trusted Member Member
105 kWhs
Expert
Joined: 2 years ago
Posts: 15
 

@hydros it should do but it will depend on system hydraulic resistance.  Can’t hurt to try it  

id definitely be looking to alter the comp curve too.  Run it lower for longer will always be cheaper.  Mines targeting about 30 degrees at the moment running from 5:00 to 22:00.  I just watch my overall energy usage for feedback but will be changing to a lower output gen6 Samsung  when I get round to fitting it.  Then I’ll get some data out of it as the old gen3 does nothing. 

Internationally recognised award winning installer of heat pumps and stuff


   
HydroS and HydroS reacted
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13722 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4165
 

@editor 

Hi Mars,

Thank you for the kind wishes, and my wife and I would like to wish you, your wife and all the forum participants a happy and prosperous new year.

I would also like to thank you and your wife for setting up the forum, which I feel certain is proving very useful and helpful to many.


   
Mars and Mars reacted
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13722 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4165
 
Posted by: @jonathans

@derek-m

Thanks very much -- I think I understand this now, as well as the source of my confusion. My Vaillant 12kW operates only w/the Vaillant Sensocomfort controller, ie, it has no other independent thermostat. So if I grasp your explanation, this means that even under weather compensation, I would use that controller as usual. That is, I would set a set-back temperature and then any other higher-heat demand periods (this is what I mean by 'as usual' -- putting in exactly the desired temperature rather than something slightly higher), initiate the function that adjusts the flow temp based on the current room temp, and then just let the ASHP run itself & adjust flow temps as it sees fit.

Have I correctly grasped the difference between the ASHP controller and the thermostat in your explanation?

Hi Jonathans,

Because your system is using the Vaillant SensoComfort controller you don't have to be concerned about thermostats. If my understanding is correct, you set the desired room temperature on your controller and you can also program setback temperatures as required.


   
ReplyQuote
(@hydros)
Estimable Member Member
326 kWhs
Joined: 2 years ago
Posts: 59
Topic starter  

@saenergy 

I've altered the curve. Currently running at 28-29C today and the house is plenty warm enough. Would bigger radiators result in an improved COP? I'm guessing I could put more heat into the house at a lower running temperature. Very few of my radiators were changed during the retrofit, most were already K2, but upgrading a few to a bigger output is within my skill set.

I think I could get away with a smaller heat pump and improve efficiency but it'll be a few years before I can justify that, and I really need a good cold snap longer than a couple of days to prove it. 


   
ReplyQuote
(@saenergy)
Trusted Member Member
105 kWhs
Expert
Joined: 2 years ago
Posts: 15
 

@hydros general rule is the bigger the emitter the lower the temp can be.  Also, lowering the temp will allow you to run the unit longer which is generally very cheap to do.  There will be a point of diminishing returns though so a decent heat loss calc to allow sizing of rads at various temps would be useful.  

 

Internationally recognised award winning installer of heat pumps and stuff


   
HydroS and HydroS reacted
ReplyQuote



(@derek-m)
Illustrious Member Moderator
13722 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4165
 
Posted by: @hydros

@saenergy 

I've altered the curve. Currently running at 28-29C today and the house is plenty warm enough. Would bigger radiators result in an improved COP? I'm guessing I could put more heat into the house at a lower running temperature. Very few of my radiators were changed during the retrofit, most were already K2, but upgrading a few to a bigger output is within my skill set.

I think I could get away with a smaller heat pump and improve efficiency but it'll be a few years before I can justify that, and I really need a good cold snap longer than a couple of days to prove it. 

Hi Hydros,

You could use the modelling tool that I produced to see the effect of changing the size of heat emitters.


   
ReplyQuote
(@hydros)
Estimable Member Member
326 kWhs
Joined: 2 years ago
Posts: 59
Topic starter  

@derek-m 

Hi Derek

I would be good to try some different numbers in a modelling tool. Are you able to send me a copy please?

COP still hovering around the 3.4 mark which is nice and consistent, running with a leaving water temperature of 30C but still 6 cycles per hour. Would bigger radiators do anything about the cycling, or is that just a factor of the house not needing the heat and the pump not being able to modulate low enough?


   
ReplyQuote
(@saenergy)
Trusted Member Member
105 kWhs
Expert
Joined: 2 years ago
Posts: 15
 

@hydros yes, it’s because you aren’t losing enough heat from the water return.  You should be able to see the temps on the controller.   Most are set to run around a 5 degree differential.

if you can get flow and return temps as well as external air temp, you will be able to see what’s going on a bit better   

I set my heat pump up to have a minimum flow temp of 20 but a comp curve set to minimum 30.  I can play with the flow temp by +/-5 degrees to see what works best. 

are you finding the house is warm enough at that flow temp?

 

Internationally recognised award winning installer of heat pumps and stuff


   
Mars and Mars reacted
ReplyQuote
(@hydros)
Estimable Member Member
326 kWhs
Joined: 2 years ago
Posts: 59
Topic starter  

@saenergy 

My controller is set to a 7C differential but I'm definitely not seeing that differential at the lower leaving temperature, though the house is plenty warm enough, it's 21.5C in the living room.

Current view is leaving water (flow) 28.2C, inlet (return) temp 28.0C, external air temp 9.0C, flow rate 17.l/min, I've seen the difference up to 3C between flow and return but only when the pump is running at ~21l/min. 

image

When the outside temperature is cooler and the pump is running warmer the difference does sit around the 7C difference mark. When I recorded figures back before Christmas I got figures around 44C leaving and 37C on the return. Outside temp was about 2-3C if I remember correctly. 


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13722 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4165
 
Posted by: @hydros

@derek-m 

Hi Derek

I would be good to try some different numbers in a modelling tool. Are you able to send me a copy please?

COP still hovering around the 3.4 mark which is nice and consistent, running with a leaving water temperature of 30C but still 6 cycles per hour. Would bigger radiators do anything about the cycling, or is that just a factor of the house not needing the heat and the pump not being able to modulate low enough?

Hi Hydros,

I have attached a copy of the modelling tool. I would suggest that you read the notes on the first sheet which explain how to use the tool.

Installing larger heat emitters could allow you to operate your system at a lower water flow temperature, but I doubt it would have much effect on the cycling. In fact it could cause cycling to occur down to lower outside air temperatures.

A further possible problem of changing selected radiators would be to unbalance the overall system, which when re-balanced may not show much improvement in overall performance. When was your system last balanced?

 

 


   
ReplyQuote
(@hydros)
Estimable Member Member
326 kWhs
Joined: 2 years ago
Posts: 59
Topic starter  

Hi Derek

I balanced the system about a month ago but it's not been done by a professional. I've watched some YouTube videos and have a IR thermometer to measure the in/out temperatures on the radiators. It's not perfect.

image

The highlighted line is the furthest rad from the heat pump. Maybe I should spend some more time trying to improve the balancing?


   