Air Source Heat Pump - Side Alley Suitability
@jamespa I used an assumed indoor temperature of 18C. Is this what you mean by nominal heating temperature? If i reduce the indoor temperature to 15.5C for the calculation, then the estimated peak heat loss drops to 6.7kW
Posted by: @ad3628@jamespa I used an assumed indoor temperature of 18C. Is this what you mean by nominal heating temperature?
Thats probably fair enough. The degree-days calculation (on which quite a few heating formula are based) uses the formula
sum (max (Tbase-OAT ,0))
where Tbase is usually set at 15.5 (not sure why this figure is chosen). This basically ignores completely any time periods where the OAT is above Tbase. In the height of the season, when the OAT never rises above Tbase, thats the same as Tbase - average (OAT), so degree days (which are easily downloaded for a load of whether stations) can be used as a proxy for OAT - which is what I did in my graph.
Another way to look at is that your house benefits from waste heat from your electrical appliances. Given that the average house uses about 3.5MWh/year, and you can reasonably assume all of that ends up as heat, this is 3500kWh/365/24 = 400W. You can add 100W per person to that, so 600-800W in total which is not insignificant.
Personally I preferred simply to plot gas consumption vs average OAT (for the reason set out above you can alternatively use degree days instead of average OAT). This then automatically takes into account heat sources other than the heating system, and allows you directly to read off the figure at any desired design OAT. If your water is heated by gas this also includes your water heating, so no need to add that in (that's probably true in your calculation also).
In principle you need, in this calculation, to account for the efficiency of the gas boiler which could be as high as 110%* if its actually condensing, or perhaps as low as 75% if its very old. Very few boilers are set up to condense because installers set the flow temperature too high and we, stupidly, don't generally use weather compensation for boilers in the UK, so the return temperature is above the condense temperature. This means that even modern boilers are most likely operating at max 95% efficiency, so measured gas consumption, provided most of the house is warm most of the day and night, really could be considered an upper limit on your house heating demand.
from what you have said I think there is a fighting chance 8kW will suffice, particularly if you accept that a little supplemental heating may be needed if there is an extended very cold patch. Obviously its your call and also depends on whether you can persuade an installer to take any notice of measured consumption (some will, others wont)
Going back to the low loss header matter and noting that this fixed your neighbours system, please note that its actually the secondary pump that does the job, because it provides enough oomph to push the water through the narrow pipes. The LLH decouples this from the primary, isolating the installer from any potential warranty issues with the boiler. A better solution is simply to have a sufficiently powerful pump in the first place, but of course most boilers and many ashps come with a pump included (which is normally powerful enough). This is another matter for your designer to get right - I would be looking for a solution where there was a single pump of sufficient power not two pumps and an LLH, and if that means restricting your choice to an ASHP that does not have a bundled pump then so be it. Alternatively it may be that changing a few selected lengths of pipework will suffice, again this does depend on the layout and crucially on the actual demand, which is why, in your particular case, a methodical approach by a knowledgeable designer is required. If you can deduce the pipe layout and in particular when pipes change sizes it will likely help.
Hope that helps.
* of course boilers aren't really 110% efficient, that would be impossible. the declared calorific value of gas doesn't include the latent heat of condensation which is recovered in condensing boilers, so is less than the energy that theoretically can be extracted.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,300 Topics
- 51.6 K Posts
- 416 Online
- 5,965 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: 10kw heat pump run in 24*7 data?
Depends on the outside temp, i'd say in the coldest of ...
By jeegnesh , 2 minutes ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
It is an excellent discussion and I'm glad everyone foc...
By AndrewJ , 14 minutes ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@kevh TJ actually recommends the warm weather value sho...
By AndrewJ , 24 minutes ago
-
RE: DHW heat loss through pumps.
Hi @ngillam I don't have anything as sophisticated for ...
By Marzipan71 , 32 minutes ago
-
RE: Electricity price predictions
I am aware how the market operates on a high level. Giv...
By Batpred , 3 hours ago
-
Luckily, the DNO is the competent organisation and they...
By Batpred , 3 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Oh I know, am just raging, apologies. 2 years has worn...
By Crimson , 4 hours ago
-
Why Millions of UK Homes Struggle With Heat Pumps
For years, we’ve heard a consistent refrain from homeow...
By Mars , 4 hours ago
-
RE: Here is my heat pump installation with questionable COP in Italy
Hi, and welcome to the forum. I cant quite u...
By JamesPa , 6 hours ago
-
I signed up to Havenwise control on the day after the h...
By Sheriff Fatman , 16 hours ago
-
That's not always the case.Let's see what they say once...
By Transparent , 19 hours ago
-
Hello All Our solar system consisting of 2 x 6Kw inve...
By AlanB , 21 hours ago
-
RE: BUS grant voucher expires before install date
@bornagain That is what our installer is pr...
By Bash , 21 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
I'm not so sure. New gas boiler £10...
By Bash , 24 hours ago
-
RE: Renewables & Heat Pumps in the News
I thought an aircon doubling as a heat pump could do ou...
By Batpred , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
Just wanted to share some info for anyone facing challe...
By Batpred , 1 day ago
-
Daikin Altherma HT Temperature Sensor Question - Caution: Mentions AI...
Hi All - first post for a while, hope you are all well,...
By Marzipan71 , 1 day ago
-
RE: Do Heat Pumps need to start up at Full Power?
@steelbadger We have an LLH with secondary pump; the se...
By Toodles , 1 day ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa Yes, the OAT sensor is situated on the back pa...
By Toodles , 2 days ago