Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Adding underfloor heating
We currently have an ASHP installed, which was fitted with our existing radiators and one zone for both upstairs and downstairs. We are currently building a small extension (12 sq.m.), and we want to put underfloor heating in it. We also intend, at a later date, to replace the downstairs radiators with underfloor heating, possibly in the next 5 years.
My question is, how should the plumber add underfloor heating to the extension, given (a) the small area currently, and (b) the plan in the future to put UFH all through the downstairs? Is this something that any plumber can do, or do we need to go back to the original installers?
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
if your ashp has hydraulic schematics for these types of install (vaillant for example) then copy those exactly. Otherwise:
The plumber should use close coupled Ts on the return line to take a parallel circuit to the UFH mixer/pump station. They should use an Ivar unimix3 blending valve (unless your your rad sizing was done to a suitable ufh temperature such as 35 degrees) because these are suitable for blending down low flow temps.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @hughfif your ashp has hydraulic schematics for these types of install (vaillant for example) then copy those exactly. Otherwise:
The plumber should use close coupled Ts on the return line to take a parallel circuit to the UFH mixer/pump station. They should use an Ivar unimix3 blending valve (unless your your rad sizing was done to a suitable ufh temperature such as 35 degrees) because these are suitable for blending down low flow temps.
Thanks so much, that's really helpful!
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
@scrchngwsl I can't advise you on the technical aspects of it but can give you my opinion after carrying out similar works.
We were adding an extension and switching to a heat pump. We had specified ufh in the extension but mid works asked for a quote for the existing concrete floors to be removed, insulation and ufh to be retrofitted downstairs - approx 85sqm. The quote came back as €12k which was too much so just went for the kitchen and wetroom shower for €5k.
We are in about a year and recently switched electricity providers and went for a smart tariff with a cheap rate for 3 hours (2am - 5am). We now heat the ufh to 22 degrees overnight and those rooms don't need any more heat during the day.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 2,173 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 2 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 7 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 13 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 4 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 5 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago