11.2kW Mitsubishi Ecodan replacing LPG boiler
My setup is very similar to yours @Peterr although I am in a 1950s house with insulation added post construction and don't have any SPV. I'm running with a weather curve 24/7 and looking at the period 1-18/11/21 I used 271kWh on heating. average COP of around 4.
What system are you running now (curve or flow temp) and have you seen any drop in electricity usage?
Posted by: @peterrHi Derek,
It is the downstairs rooms that are sometimes a bit colder than desired. If we turn up the flow temperature to get the downstairs rooms right, then the upstairs becomes too warm.
As far as I can tell there must be some sort of control between the UFH and the FTC. The heat pump responds to demands for heat from the UFH pretty quickly. I think this is the control that goes in to IN1 on the FTC, although it's little tricky to trace because the wiring is a complete mess! I have been trying to get this information out of our installer for a while now, but they are not being very cooperative.
We don't have a buffer tank, the cylinder is a Telford Tempest.
There isn't a pump specifically for the radiator circuit. There is one pump that circulates the flow from the ASHP to either the DHW or the heating circuit, depending upon the setting of the 2x 2-port valves controlled by the FTC.
Hi Peter,
Just to clarify, how many water pumps are there external to the ASHP, one or two?
If my understanding of how your system is laid out is correct, then the easiest method, in the short term, to achieve the desired temperatures both upstairs and downstairs, would be to set the weather compensation curve slightly higher, and regulate the upstairs temperatures using the TRV's. Whilst not the optimum solution, it should give reasonably accurate control in quite an efficient manner.
A longer term solution would probably be to install a further 2-way valve, so that both zones can operate independently.
We are now running with weather compensation 24/7. Our installer originally left us running on fixed flow temp at 50C. I don't really have any figures to compare consumption from before the switch to after.
Just the one pump external to the ASHP (excluding the UFH pump).
Your longer term solution is certainly the one that I would prefer, but just need to work out who is going to do the work.
I am still trying to discuss the state of our system with our installer, although they are being very unresponsive. When we originally spoke to their "Renewables Consultant" we told him that we wanted to be able to control the UFH and rads separately and he assured us that we would be able to - it seems either he was lying, or the message didn't get back to the install team!
Had a local installer come out to look at our system yesterday (judging from the Google reviews they're pretty good). Overall he was not very complementary!
Main issue is that the current flow rate being achieved is around 20l/min, it should be a minimum of 28l/min for the ASHP that we have. He described the system as a bare, basic install that is inadequate for the size of unit and house. UFH has no way of creating a demand to the system. No strainer installed. External insulation not installed to any standard, and uses insulation intended for indoor use. No low-loss header. Confirmed my thoughts that there is no way of independently controlling the UFH and rads.
It is all fairly easily correctable - adding a low loss header and an extra pump should resolve the flow issue, and a little bit of re-plumbing and re-configuring should get us back to what we had with two independent heating zones. All I need to do now is work out how to get the original installer to pay for it. I do not want them doing the work, but unfortunately I have to give them the opportunity to correct their errors.
What really irritates me is that an installer can put in a system like this, and yet still claim that they are MCS certified. The guy who came yesterday was so apologetic when he was giving me the bad news, but he said that it was sadly all too common.
@peterr you should have an insurance agreement as part of the install to cover "workmanship" and "quality"
In addition to your legal obligation to give customers a free guarantee against manufacturing faults in goods supplied, you must guarantee the installation work for a minimum of two years
I think it's very often true to say that if you were to get 3 plumbers to design a plumbing system, you'd get 3 designs, all of which would be sub optimal according to the other 2 plumbers. Whilst all 3 designs would be functional.
Asking your installer to pay for changes suggested by a third party might be a stretch, but I guess it depends on whether they agree with the third party. I'd ask politely but wouldn't get upset if they declined.
Posted by: @markcI think it's very often true to say that if you were to get 3 plumbers to design a plumbing system, you'd get 3 designs, all of which would be sub optimal according to the other 2 plumbers. Whilst all 3 designs would be functional.
Asking your installer to pay for changes suggested by a third party might be a stretch, but I guess it depends on whether they agree with the third party. I'd ask politely but wouldn't get upset if they declined.
I understand what you're saying, but it's not just that the guy who came yesterday thinks it is sub-optimal, it is actually wrong. Continuing to run the ASHP with a lower flow rate than required has the potential to cause expensive faults in years to come.
I shall, of course, be polite in my comms with the original installer when pointing out the serious problems with the install, and remind them of their obligations to correct them under their own guarantee. I shall also give them a date by which they have to respond, otherwise I will deem them to have given permission for me to use a 3rd party to correct their problems with them paying the bill. I am fairly certain that they will continue to ignore me!
Ensure you have the various elements in writing, particularly the inspection you’ve just had, and present to the MCS, insurers or even if necessary the small claims court. Good luck.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 41 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil Fwiw I have the 7kW model with which I'm, ver...
By JamesPa , 32 minutes ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@grahamf you appear to value your recirculating loop de...
By Judith , 43 minutes ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 1 hour ago
-
RE: Midea ASHP – how to set weather compensation
@cathoderay OK let's wait and see, it sounds an interes...
By Tasos , 4 hours ago
-
RE: What is the Heat Geek Guarantee?
@judith, I’m with you on Heat Geek, but there really do...
By Mars , 5 hours ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 1 day ago
-
Inventor (Midea) Heat Pump short cycling advice
Hello, I have a Inventor (Midea) 8kW with a 800meters Φ...
By immunity , 1 day ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
I have signed up as well. @belsnugg could you outline ...
By JamesPa , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 1 day ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 2 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 2 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 2 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 2 days ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 3 days ago
-
@drei When I was in local government we were of cours...
By JamesPa , 3 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 3 days ago