Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Surge Protection Devices
@jancold and @ga3_usr - have checked the Lewden manufacturer's leaflet for their Anti-surge devices, and they do indeed state a 40A MCB in series 'for protection'
I have two observations:
1. What does Lewden think needs protecting?
If the SPD were to blow itself to pieces in a desperate attempt to absorb a massive surge-spike, would I consider that a waste of a good SPD?
Contrarywise, if checked my CU after a lightning strike, and found a nice intact SPD, but all the appliances on my other circuits damaged because the MCB contacts had opened, would I give a sigh of relief that at least I had an anti-surge device which could be moved into a new distribution board? I think not!
The whole point of an anti-surge device is that 'it goes down fighting'!
2: 30 years ago I supplied a pair of Phoenix Contact rapid anti-surge protection units and plug-in bases to a regional electricity board who had won the tender to install wiring in a new secondary school.
They were to be placed in the consumer unit supply to a computer-lab with 32 new PCs.
Halfway through the first term, the school received a lightning strike on the building which housed their local substation transformer.
As you'd expect, any trip which could do so immediately opened its contacts, plunging the entire school into blackout.
On resetting trips, everything powered up OK, except for the new computer suite.
Since the anti-surge devices were pluggable and cost nearly £200 each, the electricity board hadn't installed them inside the distribution board as instructed.
Instead they'd run a 5m long 2.5mm² cable to the adjacent store-room, and placed them high up in a steel box to prevent them being nicked.
That length of cable was carefully protected by a 20A MCB, as per the prevailing regulations.
Every PC in the suite had been 'fried' because the MCB contacts had opened at the first lightning strike.
Consequently the Surge Protectors hadn't been in circuit during the rest of the storm. 🤦
Moral of the story... use common sense when fitting SPDs.
Save energy... recycle electrons!
@transparent I did not understand why an MCB would be needed so I got down my BS 7671 2018 (now superseded) so With regard to Lewden I imagine the reason for a overcurrent protective device could be to comply with BS7671 534.4.6, for TN systems. It said this is needed in the event of a fault in the SPD
But as I say my copy has been superseded and that may be wrong. Also, If I remember correctly, departures from BS 7671 are allowed in certain circumstances
As you say if the MCB is activated you lose lightening protection and you may not be aware.
I would be most grateful if the latest Bs7671 (why are they so expensive!) could be checked and if I have got it wrong please delete this post I don't want to muddy the waters.
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
Like any electrical component, an SPD may fail. They're generally Metal Oxide Varisters (MOV), and over repeated high voltage spikes tend to slowly drift downwards in activation voltage - so that they will eventually pass current when they should not, heat up and fail short circuit. They need some sort of overcurrent protection:
This could be an MCB in series
It may be an internal one way thermal fuse
It may be an integral resettable MCB
I assume the suggestion is an MCB prior to an SPD, with all loads in parallel to this SPD. I expect it can be arranged that the SPD will fail short, within the rating of the upstream MCB. Then if there is a surge that tripped out the MCB, it would trip out the entire CU? It does sound sensible, why isn't this done - it must have been considered.
I'd agree that Lewden are attempting to comply with BS7671 534.4.6.
There's a discussion about this very point here on the IET's own Forum.
Although one respondent points out that the BS88 Service Fuse is also in line, he's forgotten (or possibly unaware) that lightning-induced surges are 'common mode'. They are being passed along the conductors equally by both Phase and Neutral. If the Service Fuse blows, then it only 'opens' the phase connection.
Yes, there's a level of risk associated with an SPD, in that it might itself exhibit a fault. But that's not going to be diminished by wiring it in series with an MCB which itself usually has a 6kA breakage capacity. In contrast, the majority of SPDs are designed to provide a short-circuit to earth of at least 20kA, and often 40kA.
Which device does the IET think will fail the worst?
Have they and the SPD manufacturers realised that an MCB is also single-pole?
If we're dealing with a lightning strike, then something is likely to get 'fried'.
The whole point is that it should be the SPD!
I buy and fit top-of-the-range Phoenix Contact anti-surge devices on both mains and my renewable generation incomers (solar and wind-turbine tower). I've supplied dozens of these to others. I've only ever known of one unit which blew sacrificially. It went open-circuit.
If anyone thinks their SPD might blow short-circuit, and that this will somehow not 'take out' the Service Fuse, then you're probably buying the wrong SPD.
It's an insurance device, and you should feel confident to trust it.
Save energy... recycle electrons!
Your argument makes absolute sense to me. As the latest edition of cu made SPDs mandatory for more sites, it is odd that it did not clarify the way SPD needs to be deployed 🤔
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
I know this is off topic but I did take the cover off my CU to look at the spd. BUT found the Electrician had not fitted a bi-directional RCBO to the inverter. I have asked for an explanation. note the surge MCB is off, I may have touched it off with the cover, It's on now.
!
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
Well spotted @jancold - It depends when that RCBO was installed of course.
The Amendment to the 18th Edition of the IET Wiring Regulations isn't retrospective, but I would hope that news spreads to other homeowners, allowing them to voluntarily get their RCBOs changed to bi-directional devices.
Save energy... recycle electrons!
Posted by: @transparentWell spotted @jancold - It depends when that RCBO was installed of course.
The Amendment to the 18th Edition of the IET Wiring Regulations isn't retrospective, but I would hope that news spreads to other homeowners, allowing them to voluntarily get their RCBOs changed to bi-directional devices.
From a compliance perspective, yes it would depend on the time amongst other things.
But if that circuit to the inverter needs to have differential protection, we know that it has been put at risk, @jancold so there is a potential shortcoming and safety issue.
RCBO are expected to be tested (monthly I believe) by pressing the test button.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
@transparent It was fitted just before Christmas 25! So not good.
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
O-oh!
Let's take this as an opportunity to 'pass the word' about bi-directional RCBOs onward to the professional electrician community!
Save energy... recycle electrons!
Posted by: @jamespaPosted by: @batpredAll this reminds me why electricians insist to look at a photo of the open CU, full-width.. There seems to be a lot in a Vaillant heatpump circuit. I am sure my sister's Panasonic AC unit runs on a normal socket circuit.
![]()
The version of the Vaillant installation manual I have says that a Type B RCD must be used 'if these are specified for the Installation Site'.
I have a Contactum CU. Would the below RCBO (description as per Contactum) be suitable for a 7kW Arotherm? I believe so, as it seems to be RCD Type B (and C Curve).
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,661 Topics
- 62.2 K Posts
- 602 Online
- 7,058 Members
Join Us!
Directory
Latest Posts
-
RE: Cooling with air to water heat pumps
Another detail, as I understand it, is that with the us...
By springswood , 1 hour ago
-
RE: GivEnergy inverter tripping due to over-voltage?
Many thanks for the helpful and educational inputs! I...
By Tim441 , 10 hours ago
-
RE: Failed Heat Pump Install: IWA Claim Rejected
Many of the estimates we received mention IWA and RECC....
By Batpred , 14 hours ago
-
RE: Rural burning – I've had enough
Same here in Finland. It's strictly forbidden ...
By upnorthandpersonal , 14 hours ago
-
RE: Renewables & Heat Pumps in the News
Something worth flagging... we've just published a news...
By Mars , 14 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
The Homeowners' Q&A podcast is back... I've changed...
By Mars , 15 hours ago
-
RE: Anyone concerned about GivEnergy?
I have already signed up with Axle so yes, that takes c...
By KevH , 16 hours ago
-
I think its quite likely a failure to think it through ...
By JamesPa , 21 hours ago
-
@batpred Would it pass the airbnb feedback test no. I...
By EtchedPixels , 1 day ago
-
A quick update... we've just launched the beta version ...
By Mars , 2 days ago
-
RE: Who Actually Owns a Heat Pump in Britain? We Asked. Here Is What We Found.
The age part doesn't surprise me - only 25% of UK home ...
By EtchedPixels , 2 days ago
-
RE: Home automation and the cloud; is there a better way?
Nothing you've said there, @etchedpixels, is something ...
By Majordennisbloodnok , 2 days ago
-
I've heard from others living in the vicinity of Derril...
By Transparent , 2 days ago
-
RE: Being screwed over by Volkswagen Audi Group
@morgan, much as I like the cars they produce, I can't ...
By Majordennisbloodnok , 2 days ago