@davidnolan22 That made me smile but yes just about, I think the smallest units can be from 4 or 5kW and modulate down to 35% so close to 1.8 or 2kW
You can also be a bit smart with the design and programme in rest periods, for example if it such a low KW loss its likely unless the house is tiny it will retain the heat longer than average so run to 22 Deg C and then have a dead band of maybe 3 Deg so cycle at 19 Deg giving you an av of 20.5. this would allow the system to run longer and less cycles. That said it slightly goes against the perfect setup but what can you do?
I suppose you could install a 5kW and create a 5kw loss by ventilating a bit more? this way the system would keep running but then that it literally wasting energy.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba Not a chance for a swap unfortunately, this is already a 5 years old system. On the bright side though this is in the middle of continental Europe so we can hit -15C on winter which makes system not ~4x oversized but "only" around ~2.5x. + solar gain is also higher on the summer but I don't know how that's calculated for cooling.
Posted by: @gergoh@jamespa
Your understanding is entirely correct. It is massively oversized. And the compressor can't seem to be able to modulate to under ~3kW or so, which means balancing demand is quite the challenge. This setup is what came with the property so now I'm trying to cook from what I have. 🙂 I guess I need a way to store heat? Either in the thermal mass of the home or in a tank?OR perhaps add another heat source for shoulder seasons?
I'm really sorry to hear that.
As others have said this is massively oversized. It is also massively overcomplicated. Taking the two together this is, I'm sorry to say, one of the most extreme examples of a poorly designed system reported on this forum.
Storing heat, other than in the concrete slab if there is one, or a swimming pool sized vesse, is not likely to be practical. If you do have a concrete slab in which the ufh is burried, then maybe, just maybe, you can find a batch heating schedule, perhaps using octopus cosy, that works and has tolerable temperature swings. If that's a remote possibility it might be worth giving it a go and I'm happy to make suggestions or better still you could try to find someone who already does that and therefore can advise from practical experience not just theory
Otherwise, unless you are prepared to accept massive inefficiency, I think you need to redesign from scratch, eliminating buffer tank and most of the controls and valves (including mixing valves) and buy a heat pump closer to the right size which is also capable of 'above dew point' cooling if that's what you want to do. Even in the high season the current system and way of operating it is going to struggle to deliver an efficient heating, in the shoulder season you have no chance.
I should clarify I am not a heating engineer, just a householder with a background in physics/engineering who has been studying this stuff for a couple of years.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks for telling the cold hard truth 🙂 Even though it sounds bad I'm pretty optimistic right now.
Replacing the heat pump with a smaller model doesn't make much sense for me financially speaking because running the current one inefficiently might be cheaper than the initial cost of a new one. But once the current compressor inevitably dies I will downsize.
Other than that all the rest what you've suggested sounds like easily solvable by just disabling "by software". I can keep all the valve actuators open to match the minimum load of the heat pump, essentially having something like a (semi) open-loop system. I can also override the mixing valve, essentially bypassing it entirely.
Even the dew point is a not a problem since I can change the setpoint via MQTT.
Then if all else fails in shoulder seasons I can always switch to using the AC.
It kind of sounds like to me that following your suggestions I can improve a lot by just having more intelligent control, even though it probably never will be "optimal" in it's current form.
Then when the time comes and the heat pump will be replaced I will let someone re-design the system (and I will have DATA to do so!) and get rid of the buffer tank too.
Does this sound like an OK plan?
> I should clarify I am not a heating engineer, just a householder with a background in physics/engineering
I get it. I'm an electrical engineer / SW developer but I also have to learn this stuff out of necessity. It's kind of fun, tho.
It sounds like you get it, maximise the load by opening everything up, cancel mixing by setting the mixer valve temp to max, and then batch heat your slab (assuming you have one). I don't know how much it might improve efficiency nor whether the temperature variations will be tolerable but its got to be worth a try. Maybe align heating periods to octopus cosy. For cooling keep the flow temp above the dew temp, check for condensation and adjust if necessary. Beware of the possibility of condensation in humid voids though. Others may want to comment further
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
In addition to the above you might want to balance out the buffer so it is acting as if not there. Adjust pump speeds for minimum difference in temp between the two flow ports (flow from hp and flow to emitters) and min difference in temp between the two return ports. You will need to turn up the flow temp to make this adjustment.
Quite a few things will be difficult until the next heating season.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @carpenterstation@ashp-bobba I am watching this post with interest… I too have Ecodan, DT of 2degrees, and lots of short cycling (especially now the weather is warmer).
I can’t seem to find a way to stop the ASHP heating cycle when the outside temp is above 18 degrees - which seems really daft? (Unless I go to the controller and manually switch off the heating! - can’t even do that from the MELCloud app!)
Mitsubishi have a setting called summer mode for this. It's in the service menu under Operational Settings. There are settings for switching summer mode on/off, ambient on/off temperatures and how often to check the OAT (judgement time).
Posted by: @carpenterstationUnless I go to the controller and manually switch off the heating! - can’t even do that from the MELCloud app!)
Does the big on/off button at the top left corner of the MelCloud front page not do that?
@jamespa Please correct me if I'm wrong here, but isn't the temperature difference between each pair of ports a function of the difference in flow rate on the two sides of the buffer?
For example:
- higher primary flow rate than secondary flow rate -> primary return is now a mixture of primary feed flow and secondary return flow -> increase in difference between primary and secondary return temps -> distortion
- higher secondary flow rate than primary flow rate -> secondary feed temp is now a mixture of secondary return flow and primary feed -> not much difference between primary and secondary return temps BUT primary feed temp is higher than secondary so the pump will have to work harder to be able to keep the same temp difference between ambient and UFH flow temp, so it's ineffective.
So what I'd think from this quick thought experiment:
- minimal temp difference between each pair of flows is exactly where flow rates are equal.
- it's better to be on the higher on the secondary side than the primary, than vice versa.
Since nothing restricts flow at the primary side and the flow rate is usually at maximum then (if I'm right above) an important goal would be to keep the sum of flow rates at open loops at all times as close to 27.7L/min as possible.
Posted by: @gergohPlease correct me if I'm wrong here, but isn't the temperature difference between each pair of ports a function of the difference in flow rate on the two sides of the buffer?
Yes
Posted by: @gergohSo what I'd think from this quick thought experiment:
- minimal temp difference between each pair of flows is exactly where flow rates are equal.
- it's better to be on the higher on the secondary side than the primary, than vice versa.
Yes to the first
No to the second (I think) as this results in cold return water being swept up into the flow, reducing the flow temp to emitters for any given flow temp from the HP. Thus the HP COP is lower (since the required flow temp to the emitters is determined by the output you need from them).
Given this is presumably out of warranty and if you fancy some DiY plumbing you might want to consider bypassing the buffer (turn it into a two port volumiser on either the flow or return) and secondary pumps altogether. With the right combination of shut off valves this can be done reversibly. Nice summer project!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,220 Topics
- 49.2 K Posts
- 187 Online
- 5,880 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Say hello and introduce yourself
We may not know the regulations which apply to installa...
By Transparent , 5 minutes ago
-
This is my current set-up, with some experimental thing...
By DREI , 22 minutes ago
-
RE: Isolating the system for a planned power cut
@transparent Just wanted to share this link that Sol...
By Batpred , 1 hour ago
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
Buffer tanks can best be thought of as part of a 'produ...
By JamesPa , 1 hour ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
This is often a problem when units are installed under ...
By dgclimatecontrol , 2 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@jamespa This is a 4 port buffer tank.
By ChandyKris , 2 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas Thank you. Much appreciated. So, once connected t...
By plasfron , 2 hours ago
-
Very Much Awake – Renewing the Heating Industry One Step at a Time
Like any industry that touches so many lives, and is so...
By Aadil Qureshi , 3 hours ago
-
Ah.... I'd like to make a couple of observations: &nb...
By Transparent , 3 hours ago
-
RE: Battery storage to run Heat Pump.
Hats off to the ones that persist, @Transparent ! ...
By Batpred , 3 hours ago
-
RE: What is the Heat Geek Guarantee?
@colinc, that’s a very fair and well-balanced comment, ...
By Mars , 15 hours ago
-
@toodles Thanks. I will assume they have made som...
By Papahuhu , 16 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That sounds suspiciously like an argument by an install...
By JamesPa , 16 hours ago
-
RE: PV Panels on roof in Conservation Area
@colinc Do your own due diligence re reviews etc but...
By Morgan , 17 hours ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
So true, possibly with the exception of people you woul...
By JamesPa , 18 hours ago
-
RE: Midea ASHP – how to set weather compensation
Some things worth mentioning: (1) the Headroom Heat P...
By cathodeRay , 19 hours ago
-
RE: Heating Turned Off but Radiators Still Warm
@9jwr9 I didn't get an answer at the time and there has...
By Pipcart , 19 hours ago
-
RE: Renewables & Heat Pumps in the News
You've completely missed the point. Old, unpatched so...
By Majordennisbloodnok , 20 hours ago
-
RE: Ecodan Energy Monitoring Pack
@batpred that’s an idea yes. Will look into it
By Carpenterstation , 20 hours ago