@davidnolan22 That made me smile but yes just about, I think the smallest units can be from 4 or 5kW and modulate down to 35% so close to 1.8 or 2kW
You can also be a bit smart with the design and programme in rest periods, for example if it such a low KW loss its likely unless the house is tiny it will retain the heat longer than average so run to 22 Deg C and then have a dead band of maybe 3 Deg so cycle at 19 Deg giving you an av of 20.5. this would allow the system to run longer and less cycles. That said it slightly goes against the perfect setup but what can you do?
I suppose you could install a 5kW and create a 5kw loss by ventilating a bit more? this way the system would keep running but then that it literally wasting energy.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba Not a chance for a swap unfortunately, this is already a 5 years old system. On the bright side though this is in the middle of continental Europe so we can hit -15C on winter which makes system not ~4x oversized but "only" around ~2.5x. + solar gain is also higher on the summer but I don't know how that's calculated for cooling.
Posted by: @gergoh@jamespa
Your understanding is entirely correct. It is massively oversized. And the compressor can't seem to be able to modulate to under ~3kW or so, which means balancing demand is quite the challenge. This setup is what came with the property so now I'm trying to cook from what I have. 🙂 I guess I need a way to store heat? Either in the thermal mass of the home or in a tank?OR perhaps add another heat source for shoulder seasons?
I'm really sorry to hear that.
As others have said this is massively oversized. It is also massively overcomplicated. Taking the two together this is, I'm sorry to say, one of the most extreme examples of a poorly designed system reported on this forum.
Storing heat, other than in the concrete slab if there is one, or a swimming pool sized vesse, is not likely to be practical. If you do have a concrete slab in which the ufh is burried, then maybe, just maybe, you can find a batch heating schedule, perhaps using octopus cosy, that works and has tolerable temperature swings. If that's a remote possibility it might be worth giving it a go and I'm happy to make suggestions or better still you could try to find someone who already does that and therefore can advise from practical experience not just theory
Otherwise, unless you are prepared to accept massive inefficiency, I think you need to redesign from scratch, eliminating buffer tank and most of the controls and valves (including mixing valves) and buy a heat pump closer to the right size which is also capable of 'above dew point' cooling if that's what you want to do. Even in the high season the current system and way of operating it is going to struggle to deliver an efficient heating, in the shoulder season you have no chance.
I should clarify I am not a heating engineer, just a householder with a background in physics/engineering who has been studying this stuff for a couple of years.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks for telling the cold hard truth 🙂 Even though it sounds bad I'm pretty optimistic right now.
Replacing the heat pump with a smaller model doesn't make much sense for me financially speaking because running the current one inefficiently might be cheaper than the initial cost of a new one. But once the current compressor inevitably dies I will downsize.
Other than that all the rest what you've suggested sounds like easily solvable by just disabling "by software". I can keep all the valve actuators open to match the minimum load of the heat pump, essentially having something like a (semi) open-loop system. I can also override the mixing valve, essentially bypassing it entirely.
Even the dew point is a not a problem since I can change the setpoint via MQTT.
Then if all else fails in shoulder seasons I can always switch to using the AC.
It kind of sounds like to me that following your suggestions I can improve a lot by just having more intelligent control, even though it probably never will be "optimal" in it's current form.
Then when the time comes and the heat pump will be replaced I will let someone re-design the system (and I will have DATA to do so!) and get rid of the buffer tank too.
Does this sound like an OK plan?
> I should clarify I am not a heating engineer, just a householder with a background in physics/engineering
I get it. I'm an electrical engineer / SW developer but I also have to learn this stuff out of necessity. It's kind of fun, tho.
It sounds like you get it, maximise the load by opening everything up, cancel mixing by setting the mixer valve temp to max, and then batch heat your slab (assuming you have one). I don't know how much it might improve efficiency nor whether the temperature variations will be tolerable but its got to be worth a try. Maybe align heating periods to octopus cosy. For cooling keep the flow temp above the dew temp, check for condensation and adjust if necessary. Beware of the possibility of condensation in humid voids though. Others may want to comment further
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
In addition to the above you might want to balance out the buffer so it is acting as if not there. Adjust pump speeds for minimum difference in temp between the two flow ports (flow from hp and flow to emitters) and min difference in temp between the two return ports. You will need to turn up the flow temp to make this adjustment.
Quite a few things will be difficult until the next heating season.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @carpenterstation@ashp-bobba I am watching this post with interest… I too have Ecodan, DT of 2degrees, and lots of short cycling (especially now the weather is warmer).
I can’t seem to find a way to stop the ASHP heating cycle when the outside temp is above 18 degrees - which seems really daft? (Unless I go to the controller and manually switch off the heating! - can’t even do that from the MELCloud app!)
Mitsubishi have a setting called summer mode for this. It's in the service menu under Operational Settings. There are settings for switching summer mode on/off, ambient on/off temperatures and how often to check the OAT (judgement time).
Posted by: @carpenterstationUnless I go to the controller and manually switch off the heating! - can’t even do that from the MELCloud app!)
Does the big on/off button at the top left corner of the MelCloud front page not do that?
@jamespa Please correct me if I'm wrong here, but isn't the temperature difference between each pair of ports a function of the difference in flow rate on the two sides of the buffer?
For example:
- higher primary flow rate than secondary flow rate -> primary return is now a mixture of primary feed flow and secondary return flow -> increase in difference between primary and secondary return temps -> distortion
- higher secondary flow rate than primary flow rate -> secondary feed temp is now a mixture of secondary return flow and primary feed -> not much difference between primary and secondary return temps BUT primary feed temp is higher than secondary so the pump will have to work harder to be able to keep the same temp difference between ambient and UFH flow temp, so it's ineffective.
So what I'd think from this quick thought experiment:
- minimal temp difference between each pair of flows is exactly where flow rates are equal.
- it's better to be on the higher on the secondary side than the primary, than vice versa.
Since nothing restricts flow at the primary side and the flow rate is usually at maximum then (if I'm right above) an important goal would be to keep the sum of flow rates at open loops at all times as close to 27.7L/min as possible.
Posted by: @gergohPlease correct me if I'm wrong here, but isn't the temperature difference between each pair of ports a function of the difference in flow rate on the two sides of the buffer?
Yes
Posted by: @gergohSo what I'd think from this quick thought experiment:
- minimal temp difference between each pair of flows is exactly where flow rates are equal.
- it's better to be on the higher on the secondary side than the primary, than vice versa.
Yes to the first
No to the second (I think) as this results in cold return water being swept up into the flow, reducing the flow temp to emitters for any given flow temp from the HP. Thus the HP COP is lower (since the required flow temp to the emitters is determined by the output you need from them).
Given this is presumably out of warranty and if you fancy some DiY plumbing you might want to consider bypassing the buffer (turn it into a two port volumiser on either the flow or return) and secondary pumps altogether. With the right combination of shut off valves this can be done reversibly. Nice summer project!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,306 Topics
- 51.7 K Posts
- 212 Online
- 5,970 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
If you saw it with your own eyes I wouldn't attempt to ...
By AndrewJ , 7 hours ago
-
Our 7kW Vaillant is wall mounted, no problem neat insta...
By Judith , 7 hours ago
-
RE: Replacing my 18 month old ASHP
@trebor12345 @jamespa If it helps any this documents...
By RobS , 8 hours ago
-
RE: Cashback Incentives That Reward Shorter Ideal Heat Pump Warranties
Comment to bring this topic back into the spotlight for...
By Mars , 9 hours ago
-
RE: Maintaining temperature on windy day
I used to, but now I am retired. Mostly I miss doing th...
By cathodeRay , 9 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Quick update, Solis AI looks like work in progress. Had...
By Batpred , 10 hours ago
-
@davidalgarve that sounds like the recommended method, ...
By F1p , 12 hours ago
-
RE: Extend the colder range of the weather compensation curve?
Daikin has a slope WDC which changes per degree of temp...
By RadWhisperer , 14 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
The idea (and at least one similar product) has been ar...
By JamesPa , 15 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
In a nutshell, yes- set weather compensation curve and ...
By benson , 19 hours ago
-
RE: Commencing on an ASHP Installation Process
@sheriff-fatman looks very nice. And good shout check...
By benson , 19 hours ago
-
RE: ECO4, ECO3, ECO2, ECO1, HUS, BUS, GBIS Dedicated Support and Advice
@toodles very happy too (I have no vested interest othe...
By Bart , 19 hours ago
-
-
RE: Boxt Heat Pump Installation Experience
By Andrew J H , 1 day ago
-
RE: Don’t Install a Heat Pump Until You Read This
I feel for you. I have never done a major 'build' per...
By JamesPa , 1 day ago
-
Threeway Diverter Valve question
I am looking at a few upgrades/fixes to my Grant Aerona...
By Grantmethestrength , 2 days ago
-
Thank you! I use plotly in python, with the data comi...
By cathodeRay , 2 days ago
-
RE: 10kw heat pump run in 24*7 data?
Vaillant are pretty good maintaining their ...
By JamesPa , 2 days ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
So this morning marked 24 hours up for installer. Rooms...
By Crimson , 2 days ago