Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
And we are now back down to 7.2lpm but heating is still going
If removing that strainer made a difference, then it's possible that something has become dislodged within the pipework.
We can't tell if that 'something' was an object within the body of the strainer,
or possibly elsewhere, and that the sudden loss of flow has moved it.
Equally, you will definitely have introduced fresh air by opening the strainer,
and that will require purging from the various release-valves over an hour or two.
Save energy... recycle electrons!
So, looks like it might be an incorrect sizing of primary pump. The installer (who was the subcontractor to who I used) came out and advise he was never given the heating design by the company who contracted him despite asking multiple times. When installing he pointed out that there was no primary pump ordered so the main contractor went and purchased one (the Evosta 3 60/130). What the installer and I think has happened is the main contractor has seen the price difference between the 60/130 and the 80/130 and went for the cheaper 60/130 (without actually understanding what those values mean).
I am in the process of requesting the full heating design (they did come out and survey everything) which brought them to the conclusion of not needing any new radiators and an 8kW system. Will let you all know how I get on.
P.S We also notice that even when the heating wasnt on, the secondary Grundfos pump was still running which seems to make the radiators cool down super quick if it's still pumping the water around and the ASHP isnt heating it. When we set DHW to on, the secondary pump goes off. Is this normal or has some mis-wiring occured?
Thanks
@netdonkey The primary pump should stop after a while when there is no DHW or Heating demand, it may have an overrun to dissipate the small amount of heat left over but I am sure this is only for 30s on some systems. This pump should also be wired through the ASHP control and not on an independent supply with a switch on the wall.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
To add, the primary pump also can run for a while before the system fires up to confirm flow.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Posted by: @ashp-bobba@netdonkey The primary pump should stop after a while when there is no DHW or Heating demand, it may have an overrun to dissipate the small amount of heat left over but I am sure this is only for 30s on some systems. This pump should also be wired through the ASHP control and not on an independent supply with a switch on the wall.
So the primary pump ( EVOSTA 3) does this, only comes on when required. The secondary pump which is at the bottom right of my setup picture which is attached the the flow towards the radiators is on all the time.
Going to trace where it goes on the MIM
@netdonkey OK, so this Grundfoss pump should only turn on an off when required in heating mode as your system runs through a buffer, there will be some form of stat that controls this, its should ideally through the ASHP controls if you are using their smart controls linked to a main stat, or through the ASHP control when engaging heating mode which can also be via a 3rd party stat or controls. So it depends how they have set up your system.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Save energy... recycle electrons!
@netdonkey Primary pump should run as follows:
Heating demand on
DHW demand on
Defrost demand on
Secondary pump should run as follows:
Heating demand on
Defrost demand on (only of the volume of the buffer is not enough for the min volume for the ASHP to defrost)
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Do all ASHPs have that Primary Pump inside the building?
Or is it sometimes within the external heat-pump / heat-exchanger unit itself?
Save energy... recycle electrons!
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
-
Issue with Samsung Cascade System
3 months ago
-
First time wall mounting an ASHP
12 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
12 months ago
-
Samsung problems
1 year ago
-
Sudden drop in COP
1 year ago
Currently viewing this topic 10 guests.
- 27 Forums
- 2,799 Topics
- 66.2 K Posts
- 4,814 Online
- 7,206 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
@editor Hi, To resolve this, please tap on the A...
By Indevolt Tech , 2 hours ago
-
RE: How will removing the standing charge on gas bills benefit heat pumps?
@toodles GIGO always stands! My Cosy 6, as you can...
By Watcher , 10 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
Interestingly we had an internet outage about a month a...
By Rob of York , 17 hours ago
-
RE: Double or Triple Glazed Windows?
Posted by: @singlespeed With 9 years repairing windo...
By Rob of York , 17 hours ago
-
@transparent we’re still running a secure version of PH...
By Mars , 21 hours ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
Much longer than that here. The heating isn't even on. ...
By bobflux , 2 days ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Obviously the weather is changeable but there's a defin...
By Singlespeed , 2 days ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@rob-of-york I must admit that when we had a Daikin hea...
By Toodles , 2 days ago
-
RE: Forum updates, announcements & issues
Get the Renewable Heating Hub heads-up on WhatsApp. I...
By Mars , 2 days ago
-
RE: Safety study for plug in batteries out to tender - looks like Q3 2027 at best before legal
@editor I pointed out to the one of the Fuse execs that...
By dansus , 2 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews As well as loft insulation, there are othe...
By Rob of York , 2 days ago
-
RE: BT cuts you off, Plusnet blames Openreach... welcome to “seamless” broadband switching
Both of which (in most cases) use Openreach for the las...
By JamesPa , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Yes, this is a swiss and german standard I believe, Vai...
By Batpred , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@editor FWIW my problem was resolved, eventually, after...
By BigFish , 3 days ago
Members Online
No online members at the moment