Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
@editor Thanks Mars, interesting as most ASHP manufacturers a while back were stating or suggesting the reason for a hydraulic break was to ensure minimum standards of flow, therefore less cycling and therefore more efficient, as each manufacturer cannot ensure what you bolt their systems to and the fact that they know most installers will not upgrade the existing pipework within a home as its to expensive and disruptive, adding a buffer for them is a save all. Their equipment heats the hydraulic break store and engineer can do what they want feeding the rest of the system with that stored heat.
I wonder if all the manufacturers will start to drop the use of them from their literature.
Professional installer.
@ashp-bobba I think we’ll see a different approach to buffers in the years ahead. Volumisers are a different story.
Neil, from Grant UK, stated quite categorically in our latest video that Grant don’t mandate buffers:
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor I am aware, open loop, less pumps, slow and steady heat generation has proven more efficient, the clever engineering in ASHP is the inverter tech and compensation partnership, anything that restricts this take away some of that.
Professional installer.
@editor I think these podcasts are great. I did watch this one yesterday I think. Lets see if the MI drop buffers in their schematics as options in the future. Yes volumiser will be needed for defrost on low volume systems. Perhaps they will drop the rule with split / duel zones on buildings over 150m2. All manufacturers also still allow for duel zones in their controls at the moment. Not open loop if you shut a zone down.
Professional installer.
@editor Can you do a podcast on standards of training, whats available, how engineers get trained, where they come from, what level they get trained to, how engineers will get trained in the future, when to use and not to use some components and so on. That would be very interesting to see what the specialist say.
Professional installer.
@ashp-bobba we actually touched on that in yesterday’s recording that will go live on New Year’s Eve. Spoiler alert: there are very few options out there to train low temperature heating installers, but work is going on behind the scenes to improve standards.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor I will keep an eye out for that podcast, thank you.
Just a side note relevant to buffers, rails separators and volumisers. I may not be correct about all of them but I seem to remember that most ASHP manufacturers can provide full solutions so the ASHP and a pre-plumbed cylinder, if I remember correctly most pre-plumb cylinders come with 3 pumps, primary for the ASHP through a 3 port then connected to a rail / low loss header or the plate exchanger for DHW, heating pump on the other side of the header and a hot water pump from a plate. This in effect means most pre-plumbs come set up in one form or another as a low loss header / rail separator and a plate heat exchanger.
Not all are the same but many are. Perhaps these will not be popular in the future.
Professional installer.
My system has one of the Telford Tempest cylinders with a 50 litre buffer tank in the bottom. It seems to work very efficiently (claimed COP of about 6 when 6C outside but a 28C heating flow temperature must be a key factor) and enables my 7kW Arotherm+ heat pump to run intermittently when it's warmer than about 7C outside and the house needs some heat but not a lot. I haven't seen any info about what's inside the buffer tank but suspect that there may some form of baffle between the heat pump circuit (pipe connections on left side) and the radiator circuit (pipe connections on right side). It's the same water in both circuits and both run as similar temperatures but the tank enables each circuit to run at its own flow rate as well as increasing the overall flow volume. The top title implies that having a buffer tank may be adversely affecting the efficiency of my system but I struggle to see how and why.
Posted by: @johnrThe top title implies that having a buffer tank may be adversely affecting the efficiency of my system but I struggle to see how and why.
A properly installed buffer tank system can be efficient, but the challenge lies in the skills and knowledge of the installer. In the UK, many installers struggle to correctly balance flow rates before and after the buffer, leading to energy losses and reduced efficiency.
This is why many of the country’s top installers (that deliver highly-efficient systems) are moving towards open-loop, buffer-less systems. These systems deliver significantly higher efficiency, provide more uniform heat distribution, and eliminate the need for circulation pumps. Circulation pumps not only increase running costs but are also not accounted for in COP/SCOP calculations, further skewing perceived efficiency. Our buffered system has four circulation pumps because it's been so appallingly designed and fitted.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Why, oh why, are these system NOT Mathematically designed? In Electrical engineering many circuits are designed using P-SPICE Software. In electrical/Electronic engineering SPICE software calculates the behaviour and performance of an Electrical/Electronic circuit using precise mathematical models. Why are heat pumps NOT properly, mathematically designed?
These disputes about Buffer tanks, volumisers could be settled in the flash of a PC! Does anyone know of an affordable Mathematical design software?
Posted by: @iantelescopeThese disputes about Buffer tanks, volumisers could be settled in the flash of a PC! Does anyone know of an affordable Mathematical design software?
PSPICE I think, it seems highly likely that a heat pump system, including the house, can be described in electronic terms. Cant see the average plumber doing this though. Its more a 'suck it and see' trade.
In all seriousness I think its becoming increasingly clear that in the vast majority of domestic situations its actually fairly easy with the exception of the first bit - determining the loss. However once you have done that,
- Put in a heat pump of adequate size, a diverter valve and if you must a new DHW tank.
- Roughly estimate system volume and if there is doubt put in a volumiser.
- Dont put in a buffer, LLH, heat exchanger of any type.
- Use pipe sizes according to heat geek cheat sheet or similar unless its a mansion or a silly route. Prefer swept bends over elbows. If any existing pipes are undersized assess risk and (probably) suck it and see unless its an obvious fail
- Set up WC and radiator balance as best you can and give homeowner some simple instructions how and when to tweak.
- If homeowner doesn't want to tweak then set up WC as best you can, erring on the high side, and layer the system thermostat, not a third party one, on top to give fine control.
Obviously the above (and the associated works) has to be done properly, but I don't think it merits much simulation in the vast majority of cases.
How many plumbers actually calculate the index circuit when replacing a boiler? Boiler manufacturers know this which is why they supply boilers with circulation pumps adequate for the majority of realistic situations.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@iantelescope They say its as a result of the combi birth and delta T changing from 11 to 20! as tech got better it required less flow so all of the existing pipework in building was instantly over sized, oversized pipework is completely fine for systems, also over sized rads (with new TRV tech at the time no longer mattered as TRV's would stop the oversized boiler from overheating the oversized rad in the room) and so on, the combi sizing chart also helped, hello Sir would you like 6lts, 7lts 11lts or even 13lts of 55 deg hot water flow? This means you will get a 20kW, 24kW, 32kW or a 36kW boiler respectively. So now you have a heating boiler oversized by 8 times the requirement just to do the hot water. From that date all new engineers generally got told the water is what matters heating will always be fine.
Now hydraulics matter, friction matters, emitters matter, pressure matters and effectively the whole design matters more than ever. I think they need to make a rule if you cannot design it or get it designed then you should not install it.
Does make you wonder if there is a whole gap in the market for ASHP designers, nice little business running around designing systems correctly.
I wonder if the big 6 (meaning power companies) design accurately and can still offer the av install £2000 less than your av smaller companies and supervise all of the sub-contractors they use to install to design when they don't have enough engineers of their own. Just a thought.
Professional installer.
-
Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
3 months ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
4 months ago
-
6 Red Flags to Avoid When Considering a Heat Pump Installation
4 months ago
-
L9 error with Mitsubishi ecodan heat pump
5 months ago
-
Ecodan DHW Settings missing
1 year ago
- 22 Forums
- 2,069 Topics
- 45.3 K Posts
- 56 Online
- 3,343 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
The point about needing a legionella cycle at all and h...
By bontwoody , 9 minutes ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnnyb I was on Smart, mostly because I was on Agile ...
By Arundalep , 43 minutes ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 6 hours ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@johnmo You are correct, standard Ethylene glycol used ...
By Brendon Uys , 7 hours ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 12 hours ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 12 hours ago
-
RE: Kensa GSHP finally installed - now to start the optimisation process
Just had a quick scan of the manual and should be weath...
By Johnmo , 1 day ago
-
RE: Potentially more choice including air to air heat pump grants
Hi all, I agree, the consultation documents are alway...
By madbilly , 1 day ago
-
RE: Commencing on an ASHP Installation Process
I think those are pretty much the standard figures that...
By JamesPa , 1 day ago
-
RE: Load Compensation and Weather Compensation
I think that maybe what the adia thermal system does, b...
By JamesPa , 1 day ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
@old_scientist @profzarkov thanks to you both for the v...
By Grahamh-uk , 1 day ago
-
RE: Nibe F2040 periodic warm water increase fails
@tribol here's an official reply from NIBE on your case...
By Mars , 1 day ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
@ecodan-efficiency On the other hand, the fact that the...
By Richard24738 , 3 days ago
-
RE: How accurate was your heat loss survey?
@scalextrix for our house 1950s detached the air leakag...
By Judith , 3 days ago
-
-
RE: Air Changes per Hour - ACH and the MCS requirement
@matwin If you plan to commission one it might b...
By JamesPa , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
In a similar vein, this recent spell of sustained good ...
By Majordennisbloodnok , 3 days ago
-
RE: Home energy storage & battery register
By the end of next month... 8 kW PV + Tesla Powerwall...
By Algienon , 3 days ago
-
RE: Various different approaches to battery storage.
I thought I'd share my story/journey and experiences he...
By Old_Scientist , 3 days ago