Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@transparent I am happy to pass the skillset(s) but assume it will be useful for others to see what it takes. I wish it was a trainset that just takes a bit of space, this will form part of the fabric of the house! 🤨
Fogstar responds quickly, but it is a very long email thread.. The balancing was just one of the surprises that was not in the youtube video. 😉
Just today Fogstar suggested me to upgrade the firmware of the Seplos BMS they shipped! And the Seplos apps require passwords that nobody seems to know, I already had to ask for that again..
The power bench delivered 5A to start with and is the brand they recommended..
I understand your questions about the BMS balancing capabilities, same occurred to me in the last couple of calls with them..
But Fogstar are not yet at optimisation stage supporting my adventure, it is more about getting the basics done.
When they recommended this BMS firmware upgrade, it was to solve an warning where the name of the battery is not recognised by the Solis, which would potentially also unlock some ability to set it to charge at the optimum voltage..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Ah... now I can see a photo,
and that changes the advice I've previously given here.
Firstly you've connected that Power Supply Unit at the near-end of the entire set of 16 cells.
In my earlier photo I had a 12A PSU connected in the centre of the row.
The cell at the far end of your set is receiving electricity which has been passed through 16 preceding connectors,each of which adds resistance.
Secondly, your PSU is connected using crocodile clips.
Those add a considerable resistance.
Fortuitously I've previously done that experiment, and took a photo as evidence:
My 12A supply is recording just 0.42A
This is the major reason why you'll be waiting until 2026 for your cells to charge up 😳
Thirdly, only now do know that you've bought a Seplos enclosure from Fogstar.
I had (incorrectly) assumed that you'd got one of Fogstar's own designs with the Pace BMS.
Posted by: @batpredWhen they recommended this BMS firmware upgrade, it was to solve an warning where the name of the battery is not recognised by the Solis, which would potentially also unlock some ability to set it to charge at the optimum voltage..
Ah... perhaps so.
But I have no hands-on experience of the Seplos BMS design.
Frankly it won't matter much whether the Solis inverter 'recognises' the BMS or not.
It's not going to act in any Smart manner by implementing that connection!
Chinese designers are very much 'into compatibility' as a sales feature.
But they make that claim when all that's happening is the Inverter App telling you the state of charge of the battery.
If the BMS attempts to report a fault-code, or anything that's "useful", there's no guarantee that the inverter will know what to do about it.
It may not even bother to tell you via a message on the App.
I've been running four batteries with three inverters for most of this year (2025).
At no time did any of the inverters change their operation as a result of faults/alerts!
Save energy... recycle electrons!
@batpred Can we please have an update regarding your cell top-balancing operation?
Have you now got rid of those croc-clips?
With what effect?
Thanks
Save energy... recycle electrons!
Posted by: @transparent@batpred Can we please have an update regarding your cell top-balancing operation?
Have you now got rid of those croc-clips?
With what effect?Thanks
I had some very pleasant moments packing the cells into the box. They are apparently only 45% charged, and not their only job is to allow Solis to have a look at the inverter settings. When I get my UPS I will hardly remember how it started!
Getting back to the BMS upgrade topic, the firmware update that is supposed to remove some potential wrinkles is in need of some guidance from Fogstar. I chased it but could only speak to the PACE specialist, the only one that knows enough about Seplos must be asleep at the moment!
I think the pleasure of eventually getting it to work automatically will not be easily decoupled from all the weeks leading up to it.
Still, I am not saying never again, as tempting to think I learnt enough and the next battery DIY assembly would be quick..😉
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
That's good news for the moment anyway.
Can we try to keep your Storage Battery saga all on one topic as things progress from here?
You mentioned putting cells into the box yesterday on the topic Battery Storage to run a Heat Pump where we were discussing battery chemistry
and the questions on wiring in your Solis inverter are on the topic Isolating the System for a Planned Power Cut.
Others will arrive here in months to come and not understand how they seem to missing bits of your story.
When I write a response to something, I tend to check my text against the Topic Title before pressing the Send button.
That gives me a moment to either add links to relevant discussions elsewhere,
... or to split what I've written across several Topics, according to the subject matter.
With hindsight we should probably have recommended a completely new topic for your installation...
into which I could then have added the cross-topic links for others to follow at a later date.
I now have multiple tabs open just to keep on track with what you and I have discussed!
aagh!
Save energy... recycle electrons!
So following on the AC connections of the inverter ( on the topic Isolating the System for a Planned Power Cut.). Repeating my last post on it below.
Posted by: @batpredJust wanted to share this link that Solis posted on the sensitivity of the RCDs. To be honest, I will not be looking into it in much detail as just focus on my specific case is hard enough!
But you may have a lot more to say and perhaps influence the powers. A bit more focus from them to advise each market (or perhaps Europe as a whole) may help reduce safety issues.. Or even ideally they will defend the safer standards should be used everywhere..
When I spoke to a Solis engineer, I got the sense the reason for the RCD 100ma recommendation is, as we thought, unrelated to their inverters. Some experience of 30ma RCDs triggering easily when PV installed on metal sheeting roofs is supplying the inverter was hinted at. It seems working on industrial sites with PV on metal roofs needs extra care and electrical insulation.
But back to point, 30ma RCBO arrived and will have to be swapped at my "site" before the inverter can be commissioned.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Oh, and still no answer on how to upgrade the SEPLOS BMS firmware...
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Have you tried going to Fogstar's website and looking for downloads?
It took me about 10secs to find the instructions there! 🤔
Save energy... recycle electrons!
Posted by: @transparentHave you tried going to Fogstar's website and looking for downloads?
It took me about 10secs to find the instructions there! 🤔
I downloaded the firmware without a problem. The issue is the software does not upload it.
I then quickly scanned the web for seplos apps to do it, but they need passwords etc - fair 3nough. Then Fogstar surprised me as they could not recognise them straight away... 😂
The seplos bms is not easily accessible from the outside so not a big issue that the passwords are posted everywhere.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
What do you mean by "the software"?
Are you referring to a piece of code which runs on a PC and just does upgrades (via a serial port perhaps)?
Or is the upgrade system a feature of the Seplos mobile-phone App?
I would be surprised if the issue hasn't been covered by the Off-Grid Garage YouTube channel.
He's an Australian guy who isn't afraid to post passwords and 'inside knowledge'.
Save energy... recycle electrons!
It could be an app working via Bluetooth or windows software connecting to the typical port for these devices, using serial protocol.
As I hope this firmware update will not need to be done again, it is just something that Fogstar should advise on how to get through to the end. Hopefully after this update the inverter team will stop raising concerns about the battery not being supported!
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Some light at the end of the tunnel. Fogstar had some issue with their ticket management system, so it must have been quiet for the 3rd level engineering folks for a few days. 😊
The system now pushed the batched ticket updates..
And so happy to report the problem with the firmware update (windows software) is now accepted Seplos will get a call when they reopen! I do not have any illusion of a software development team behind it, a quick turnaround would be a welcome surprise.
Solis is still bouncing tickets back unanswered quicker than they get them.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 136 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 7 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 7 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 7 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 8 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 9 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 10 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 12 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 12 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 14 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 17 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 20 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago