@transparent We do not connect thermal stoor DHW units to the central heating. If you want a heat pump to work efficiently in heating mode, DO NOT connect it to a multi fuel heating and DHW thermal stoor. Heating is Heating, DHW is DWH, nether the twain shall meet, where heat pumps are concerned.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Well that's pretty clear @heacol ... except that I do not understand why this should be so. 🤔
What is different in a heat pump such that it lacks efficiency if it receives return water from one 'cylinder' which is being heated towards 50C, but is better able to handle two such bodies of water?
If I were to remove the heat input from my existing gas boiler to my thermal store, and replace it with a GSHP, where does energy then get wasted?
Would your answer be different if the same thermal store also received heat input from a solar-thermal array, thus making it 'multi fuel'? What feature of the thermostatic control would the GSHP find difficult to handle?
To avoid blind alleys in the maths, let me point out that my UFH takes water from the thermal store at 46C. If the temperature of the thermal store is higher than that, then the return water from the UFH manifolds is passed via a mixer-valve. That maintains the 46C maximum feed to the UFH.
Nothing in this suggests to me that switching to a GSHP would be inefficient.
I certainly wouldn't want to feed the UFH directly from the output of the HP because it could be above 46C when entering the manifolds. That, in turn, could over-heat the oak boards on the suspended floor zones, resulting in warping.
Save energy... recycle electrons!
Well my understanding of the issue is that the water in the store is hotter than it needs to be for the UFH. Since the COP of the Heat pump decreases as the temperature increases then its inefficient to heat the water to a higher temperature than needed. However since you also have a heat source other than a heat pump I think that muddies the water a bit, but since most of your heating requirement will be in the winter when the solar input is low, it would still seem that the inefficiency would apply
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Rereading your post, I think you are suggesting that the heat pump only supplies water at one temperature? Mine has a DHW and an UFH temperature which switches when the demand area is changed.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I've just swapped a Thermal Store for a UVC as part of a new ASHP installation (my TS is for sale if anyone wants it - 277 Gledhill Solar RE).
I initially wanted to keep the TS - I liked the relative simplicity and ease of servicing etc....and given it was already in place it seemed daft not to use it.
I did a lot of research into the pros and cons of keeping it, searching forums, speaking to installers and even contacting John Cantor - the man who wrote the book on heat pumps:
Everyone, but everyone said forget it and I'd be better off with a UVC. The final decider was discovering the RHI scheme wouldn't accept Thermal Stores on their paperwork. It meant I wouldn't have got RHI for water heating and would have lost out on around £2k....so on top of everything else it didn't make financial sense. (I actually ended up £1,000 better off having a new UVC).
Here are some of the reasons I was told about why an ASHP and TS won't work efficiently together:
* TS not as well insulated as a UVC so loses heat quicker
* You need to heat a TS to a higher temperature than a UVC because of losses in transfer
* Increased cost of heating a larger volume of water in a TS compared with UVC
* Hot water from a TS depletes quicker than a UVC (difference between direct and indirect hot water)
One installer, who has contributed to this site, had actually fitted a TS to his ASHP...I emailed him for his thoughts and this is what he had to say:
"It could be difficult using a thermal store. This is because it will have been designed to store water at a fairly high temperature. The energy-efficiency of a heat pump will drop at high temperatures. My initial feeling is that it won't be efficient or cheap to run.
Ideally you would operate it as it is and monitor the flow and return temperatures to the store.
WRT heating. It seems likely that the radiators should go direct from heat pump to the radiators.
"I would normally not expect a thermal store designed for a boiler to work with a heat pump. This is because it has a fairly small coil in it and the water flowing through the coil (see page 77) needs to heat up instantly, and to be able to get say 50° at the tap, the store water needs to be well over 60°. A specially designed heat pump cylinder has a big coil as I was showing in the book. You are probably best off with a cylinder designed to go with the heat pump"
I'm no expert and only passing this on in case you can make use of it. Everyone's installation is different so it may work for you....but be aware you may end up running the ASHP hotter than you have to - so costing you more.
BTW I've learned a lot from reading @heacol previous posts and glad to see him back on the forum. He seems to know more than most about how heat pumps work.
Andy
Posted by: @bontwoodyRereading your post, I think you are suggesting that the heat pump only supplies water at one temperature? Mine has a DHW and an UFH temperature which switches when the demand area is changed.
That's useful to know. In my case I'd be expecting take output from a HP at a maximum 50C for both DHW or UFH use. The ability of a HP to offer two different heating rates hasn't seemed necessary to evaluate.
Posted by: @andygo - quoting from John CantorI would normally not expect a thermal store designed for a boiler to work with a heat pump. This is because it has a fairly small coil in it
Ah... this possibly explains why our views differ.
My present Thermal-store doesn't have a coil to transfer heat from the existing gas boiler. The water circulating to/fro the boiler is exactly the same as that filling the main body of the TS. So there is no heat transfer loss to be taken into account. In effect my 'coil' is infinitely large!
I too am grateful to read @heacol's comments. It's discussions like this which help shape the decision-making process.
Even if I do opt to install a separate DHW cylinder, I would want to check what I'm buying much more closely than I did when acquiring the TS.
When it arrived here, the build-quality was poor.
- the ports entering/leaving the tank hadn't been assembled with a jig. Consequently they weren't aligned to the radius, but stuck out at odd angles!
- two valves and two thermostats were pre-wired to an electrical box. This had 7 loose connections, including the neutral-in. The wires used were standard PVC rather than high-temp (105C). Four of the earth wires in the connection box had been made using red wire 😡
- the suppliers (who also designed the product) explained that they never see the TS before it gets shipped because they come direct from a 3rd-party manufacturer. As such they offered no redress, claiming that 'it isn't our fault'!
Caveat emptor!
No wonder this country manufactures so little these days.
Save energy... recycle electrons!
Posted by: @transparentPosted by: @bontwoodyRereading your post, I think you are suggesting that the heat pump only supplies water at one temperature? Mine has a DHW and an UFH temperature which switches when the demand area is changed.
That's useful to know. In my case I'd be expecting take output from a HP at a maximum 50C for both DHW or UFH use. The ability of a HP to offer two different heating rates hasn't seemed necessary to evaluate.
Posted by: @andygo - quoting from John CantorI would normally not expect a thermal store designed for a boiler to work with a heat pump. This is because it has a fairly small coil in it
Ah... this possibly explains why our views differ.
My present Thermal-store doesn't have a coil to transfer heat from the existing gas boiler. The water circulating to/fro the boiler is exactly the same as that filling the main body of the TS. So there is no heat transfer loss to be taken into account. In effect my 'coil' is infinitely large!
I too am grateful to read @heacol's comments. It's discussions like this which help shape the decision-making process.
Even if I do opt to install a separate DHW cylinder, I would want to check what I'm buying much more closely than I did when acquiring the TS.
When it arrived here, the build-quality was poor.
- the ports entering/leaving the tank hadn't been assembled with a jig. Consequently they weren't aligned to the radius, but stuck out at odd angles!
- two valves and two thermostats were pre-wired to an electrical box. This had 7 loose connections, including the neutral-in. The wires used were standard PVC rather than high-temp (105C). Four of the earth wires in the connection box had been made using red wire 😡
- the suppliers (who also designed the product) explained that they never see the TS before it gets shipped because they come direct from a 3rd-party manufacturer. As such they offered no redress, claiming that 'it isn't our fault'!
Caveat emptor!
No wonder this country manufactures so little these days.
Was it manufactured in China by any chance? 😌
Interesting suggestion @derek-m
But no. It was manufactured in Telford. And it won't take you too long to work out the highly-reputable British manufacturer who decided to cut corners once they realised that the product designers had put no QA checks in place.
Save energy... recycle electrons!
Posted by: @transparentInteresting suggestion @derek-m
But no. It was manufactured in Telford. And it won't take you too long to work out the highly-reputable British manufacturer who decided to cut corners once they realised that the product designers had put no QA checks in place.
I'm afraid it is one further example of the world in which we now live. 'Never mind the quality, feel the width', or in this case increase the profit.
Hi Andy
Thanks for this, all sensible stuff. I think there are a couple of caveats though.
* TS not as well insulated as a UVC so loses heat quicker
My thermal store was custom built by Newark and has 125mm of foam insulation
* You need to heat a TS to a higher temperature than a UVC because of losses in transfer
Absolutely true if you dont count legionella purges. How often are you intending to do these with your new UVC?
* Increased cost of heating a larger volume of water in a TS compared with UVC
Again true, but I heat my store to 51C and never to 60C for the purge using an inefficient imersion element, so bigger volume of water but lower temperature and a more efficient heating system, so it depends on how often the legionella purge is done
* Hot water from a TS depletes quicker than a UVC (difference between direct and indirect hot water)
True, but you have a larger reservoir of heat to deplete.
Also with a custom thermal store you can specify any length of heating coil you want to match a heat pump.
I think i am coming down on the side of an UVC but the cost differences dont seem that big, particularly if the purge is done daily and you factor in annual services. One big adavantage of the UVC that we havent mentuioned yet is smaller size and weight 🙂
Mark
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Ive just found some temperature data for my thermal store for the past year.
Its average minimum daily temperature was 43.4C, so plugging this figure into my spreadsheet and altering the efficient down from 325% to 300% to mirror the efficiency of the Cylinder 2 figure and changing my size to 400 litres from 450 litres as I was mistaken about its capacity, gives the following:
|
Cylinder 1 (HP) |
Cylinder 2 (HP) |
Cylinder 3 (Imm) |
Totals |
Heat Store |
Vol of water (lt) |
170 |
170 |
170 |
|
400 |
Start Temp © |
35 |
42 |
53 |
|
43.4 |
End Temp © |
42 |
53 |
60 |
|
51 |
kJ needed |
4998 |
7854 |
4998 |
|
12768 |
Theorectical kWh needed |
1.39 |
2.18 |
1.39 |
|
3.55 |
Unit Elec Cost |
£0.30 |
£0.30 |
£0.30 |
|
£0.30 |
Eff of heater |
375.00% |
300.00% |
100.00% |
|
300.00% |
Actual kWh needed |
0.37 |
0.73 |
1.39 |
|
1.18 |
|
|
|
|
|
|
Cost of heating |
£0.11 |
£0.22 |
£0.42 |
|
£0.35 |
|
|
|
|
|
|
Spec Heat Cap water (J/kg) |
4200 |
4200 |
4200 |
|
4200 |
|
|
|
|
|
|
Weekly Cost (1 purge p/w) |
£1.55 |
£0.22 |
£0.42 |
£2.19 |
£2.48 |
Weekly Cost (1 purge p/d) |
£1.55 |
£1.53 |
£2.92 |
£6.00 |
|
This shows that my store costs about half as much to heat as the cylinder if a daily legionella purge is specified and is a bit more expensive (£2.19 v £2.48) if a weekly purge is used. I am of course assuming that my store and the cylinder produce the same amount of useable hot water.
To be clear Im not a die hard Thermal Store advocate, but given these figures the choice doesnt look as clear cut as some might suggest. Im more than happy for anyone to pick holes in my analysis as I would like a definitive answer too.
Ive attached a plan of my store below
Mark
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody I'm not even going to pretend I know what I'm talking about, but everything I've read suggests a weekly not daily legionella purge. Also seen lots of chat about them not really being needed in sealed systems or only needing heating to 50c. Lots of opinions on the internet....some might even be correct.
At the end of the day it's up to you to use what you think is best for you.
Posted by: @bontwoody
One big adavantage of the UVC that we havent mentuioned yet is smaller size and weight 🙂
I'd actually disagree with this - the 200l uvc isn't much smaller than the 277l TS it replaced - and there's other gubbins which comes with it. We've now got three expansion vessels, an exchange unit and a buffer tank crammed into the room where the store used to sit....
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 90 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 2 hours ago
-
RE: Cleaning up after gas meter removed
i had the gas pipe terminated out side the house in the...
By AgentGeorge , 3 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@toodles I have noticed that on some.days it takes a wh...
By ChandyKris , 12 hours ago
-
-
RE: Fan running in hot weather ...why?
I wonder if it has some kind of pressure transducer to ...
By ASHP-BOBBA , 16 hours ago
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 22 hours ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 24 hours ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@editor If it is of any interest, we had the BUS grant,...
By Toodles , 2 days ago
-
Sorry to hear that @bruce. Sadly I’ve heard from multip...
By Mars , 2 days ago
-
RE: Crystal Ball Time: Communal or even Area Energy Storage?
I am invested in a couple of listed energy storage fund...
By Old_Scientist , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
That would be my biggest commitment -time to gain great...
By SUNandAIR , 3 days ago
-
RE: Who has a V2G EV installation
As has been discussed on other threads, trying to justi...
By Majordennisbloodnok , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks @mikeh. Then I will also go back to non smart ta...
By ChandyKris , 4 days ago
-
RE: Location of hot water isolation valve on cylinder
@transparent Thank you so much and very helpful. Earlie...
By rossowheels , 5 days ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 6 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 6 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 7 days ago