I'll leave it tonight and post the graph tomorrow to see it anything starts to make sense !
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody "but after a minute the 3 way valved closed."
I might be wrong but could it be a 3 port, 2 way valve with mid-position?
Operation by the following voltages
My question would be is it a new valve or the original, has it been plumbed correctly, has the wiring to it been disconnected and reconnected correctly?
Was the new tank fully recommissioned and signed off accordingly as per Mixenergy installation manual? It kind of sounds like to me it hasn't been😗 Is that a fair assessment?
@iaack Hi, thanks for the input.
So the situation is that I had a direct mixergy cylinder fitted 3 years ago but plumbed my heat pump ready so that I could add the Mixergy heat exchanger at a later date. The original cylinder failed and the replacement I was sent is an indirect cylinder.
Getting the plate heat exchanger isnt really financially viable at the moment so I thought I would try partially heating it from the coil.
The plumber who installed the new cylinder wasnt very confident with the wiring around my PV diverter so I said I would commision it as he was nice enough to plumb the coil into my system for me.
I dont think I have a mid port valve (I hope!) as I made that mistake in my last house and knew the issue Picture of my valve is below.
This mornings DHW run shows the same pattern. The flow rate is shown in red.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I may have found the problem. There is a valve on the return side to stop the water when it was originally plumbed in with nowhere to connect to. It was closed! I've opened it and will try again tonight 😁
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Fingers crossed @bontwoody
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist Well it does seem pretty evident that it wouldnt work with it closed 🙂 but its odd OEM was showing flow, so lets see!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@old_scientist Yip Yip! it worked.
So the DT was small, probably because the stratification pump is off and the coil isnt big, but it got to a 40% charge on its own before it was stopped and the immersion kicked in. COP was pretty dire though averaging about 1.4. Ill try it in eco mode now which should be slower and give the water more time to conduct the heat away.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodySo the DT was small, probably because the stratification pump is off and the coil isnt big, but it got to a 40% charge on its own before it was stopped and the immersion kicked in. COP was pretty dire though averaging about 1.4. Ill try it in eco mode now which should be slower and give the water more time to conduct the heat away.
If you can turn on the destrat pump COP should improve because the water in contact with the coil will be colder. You will also heat more of the tank likely to a higher temp.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa absolutely. But I think I might have to get the Mixergy Control unit to achieve that. Ill keep my eyes open on ebay. In the mean time I will also drop the desired tank temperature and maybe heat in short batches with a longish gap.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody so pleased it's finally working.
Posted by: @bontwoody@old_scientist Well it does seem pretty evident that it wouldnt work with it closed 🙂 but its odd OEM was showing flow, so lets see!
Yes, this is what threw me when I read your post yesterday - how were you recording flow for 1min with a closed valve, and if there were no flow, why did the controller not immediately raise an E911 error code. Anyway, kinda irrelevant now it's working.
I hope you are able to improve the COP a little. I use Quiet Mode to limit the output when heating my DHW, which hopefully makes it a little more efficient (lower and slower). My LWT normally sits around 8C above the DHW tank temp during the DHW heating cycle. Without Quiet mode enabled, it's a little higher.
Don't forget to turn Quiet Mode OFF when going back to space heating as it does strange things in space heating, as noted by Glyn Hudson here
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist yes. No E911 error. Very odd. Thanks for the link, very interesting.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
So this was last nights DHW run using economic mode.
Im a bit unsure as to what the actual COP was as it states 3.00 for the whole window, but the instanteous values are much lower. Either way its better than last night.
Ive knocked the target temperature back 5C and scheduled two 30 minute runs with a break for tonight. 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
-
Mixergy HP Cylinder and Solar Diverter
2 years ago
Currently viewing this topic 3 guests.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 682 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
That’s my pleasure, @andrewj. The only challenge now is...
By Majordennisbloodnok , 55 minutes ago
-
RE: Electricity price predictions
@toodles @skd Then there is not going to be much from t...
By ChandyKris , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
@batpred I reckon Andy might know a thing or 2 about...
By Bash , 2 hours ago
-
RE: What determines the SOC of a battery?
@batpred Ironically you didn't have anything good to...
By Bash , 3 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here’s a current graph showing a bit more info. The set...
By benson , 3 hours ago
-
RE: Setback savings - fact or fiction?
True there is a variation but importantly it's understa...
By RobS , 3 hours ago
-
Below is a better quality image. Does that contain all ...
By trebor12345 , 4 hours ago
-
Sorry to bounce your thread. To put to bed some concern...
By L8Again , 4 hours ago
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 4 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 8 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 11 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 12 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 1 day ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 2 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 2 days ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago