Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heat pumps and OPEN VENTED DHW tanks?
I am struggling to find an installer, or manufacturer, who can fit me an ASHP in conjunction with a vented DHW tank. Out here in the wilds of Shropshire, 1000 ft up, the water pressure (or even availability) of mains water is iffy so there are two large cold water tanks in the loft. This also avoids the need for pressure relief to the outside world, in the event the immersion heater decides to boil the tank. Am I chasing unicorn poo, or do such systems exist (even on the Welsh marches)?
I guess I need an MCS installer to avoid planning issues, though I may have those anyway since I have a 20 YO A2A aircon system, and I believe I am only allowed one HP under permitted developments? I do have 10 years of energy consumption data from my oil burner (10 kwhr per day per degree day of heating needs) so maybe I can duck the heat loss calculations?
Absolutely nothing at all to stop any ashp being used with a vented tank except that I'm not sure anyone advertises a vented tank with a large enough coil. Most tank manufacturers will do specials or you can use a plate heat exchanger instead of a coil (arguably better anyway), or just plumb an 'unvented' tank with a vent (although this is unnecessarily expensive). Really this shouldn't be an issue for any half competent plumber.
Doubtless some will give a spiel about legionella, you should run a legionella cycle in accordance with recommendations (although others may argue that this is unnecessary).
Sadly you are getting the usual nonsense of installers who can't think outside their very small box and insist on using the ashp manufacturers pre plumbed cylinder so that they can put complete rookies on the job whilst still charging a premium.
Permitted development applies only to one heat pump so you will need express consent if you already have one. Once you have express consent MCS isn't necessary unless you want the grant. Sadly (and disgracefully imho) MCS is necessary for installation under pd.
You probably can't duck the loss calcs because emitters need to be sized but it might be possible to persuade an installer to use your actual consumption for the system sizing. Most will probably refuse however because as a customer you can't be trusted and likely over-size as a result.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Gledhill do a range of OV HP tanks .. eg Gledhill SL Plus HP 300HP3SQM EE Open Vented - PLUHP300OV, though these are not, of course, part of any manufacturer's standard kit. Sounds like I figured right - I need planning approval for the second HP. Might be easier just to upgrade the existing one and go A2A for the whole bungalow. I used to despise hot air heating, back when it was gas furnaces, but since I want aircon anyway ..
The fact BUS doesn't apply to A2A is another stupid government decision. Much of the continent (well, Scandinavia) runs on A2A as far as I know, thus avoiding a whole ton of freezup issues.
Legionella and even DHW in total are not really a consideration.. I have enough PV and battery to just run an immersion heater on cheap (thanks Octopus) overnight electrons, and leave the heatpump to do the space heating.
As you say though, finding a flexible installer, out here in the wild especially, is a challenge .. much easier to shift BUS-funded boxes en mass. Even Octopus (as Which recommended) won't play with me, whether because they just don't have anyone out here, or whether because of non standard needs, is hard to tell. Maybe they just don't like anyone who has actually done some research. 🙂
Posted by: @dave1234As you say though, finding a flexible installer, out here in the wild especially, is a challenge .. much easier to shift BUS-funded boxes en mass. Even Octopus (as Which recommended) won't play with me, whether because they just don't have anyone out here, or whether because of non standard needs, is hard to tell. Maybe they just don't like anyone who has actually done some research. 🙂
Not sure you are any worse off than those like me who live close to London when it comes to flexible installers. Many including me report similar problems.
Octopus seem to have a fairly good reputation for being tolerably flexible but will only engage if your house fits their current target market.
Few installers, in my experience, like people who have done any research, oresumably because it makes it more difficultf for them to spout bs to get the sale they want. Those that do like such people deserve our custom.
Unfortunately the bus and pd rules, both of which require mcs, have created an industry which some argue is not healthy.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
you can use any manufacturers ashp unvented cylinder as an open vented cylinder have done it numerous times as the water flow rate and pressure is quite bad here in the Sw London area! All that the installer needs to do is not use the expansion vessel and combination valve . Cap the prv and plumb it like an open vented cylinder. It’s surprising how many installers don’t know thisPosted by: @dave1234I am struggling to find an installer, or manufacturer, who can fit me an ASHP in conjunction with a vented DHW tank. Out here in the wilds of Shropshire, 1000 ft up, the water pressure (or even availability) of mains water is iffy so there are two large cold water tanks in the loft. This also avoids the need for pressure relief to the outside world, in the event the immersion heater decides to boil the tank. Am I chasing unicorn poo, or do such systems exist (even on the Welsh marches)?
I guess I need an MCS installer to avoid planning issues, though I may have those anyway since I have a 20 YO A2A aircon system, and I believe I am only allowed one HP under permitted developments? I do have 10 years of energy consumption data from my oil burner (10 kwhr per day per degree day of heating needs) so maybe I can duck the heat loss calculations?
- 27 Forums
- 2,787 Topics
- 65.8 K Posts
- 855 Online
- 7,192 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Home energy storage & battery register
A useful register should record model, usable kWh, inve...
By EnergyStorageTech , 3 hours ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
I assume the 2.5 - 3kW required to heat the hot water c...
By Paul1098 , 6 hours ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
@trebor12345 I have been meaning to get home assista...
By Batpred , 7 hours ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent I was replying about the accuracy of "AI" ...
By EtchedPixels , 9 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
SunSynk hybrid inverters also have the capability to as...
By Transparent , 10 hours ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
If you've got a sash window or a door you can remove th...
By EtchedPixels , 11 hours ago
-
RE: Heat Geek Zero Disrupt: Are We Sleepwalking Into Another Race to the Bottom?
Roughly how most air/air is done except that step 3 doe...
By EtchedPixels , 12 hours ago
-
RE: Nook batteries from Octopus
@batpred If your energy use is low enough that just get...
By EtchedPixels , 12 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
I suspect 4 yrs ago, their approach had not got to this...
By Batpred , 12 hours ago
-
RE: battery storage without solar
Also don't forget that in you may not be able to use th...
By JamesPa , 22 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
One practical safeguard is to separate the calibration ...
By EnergyStorageTech , 23 hours ago
-
RE: tepeo ZEB UK Support & Info Thread
There is at least one large scale system in this catego...
By Toodles , 1 day ago
-
RE: Getting closer to a finished Haier system
Apart from sealing the external Primary Pro joints and ...
By Singlespeed , 2 days ago
-
RE: Air-to-Air Heat Pumps & Air Conditioning: UK Heating and Cooling Q&A
Our latest Homeowners’ Q&A episode has just dropped...
By Mars , 3 days ago
-
RE: Vaillant ecoTEC Plus with sensoCOMFORT and weather compensation
Yes, its described in the sensocomfort manual. Its als...
By JamesPa , 3 days ago
Members Online
No online members at the moment