RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW

@CBrenewable @ashp-bobba seems to be on the case so I will step out for now to avoid possible confusion, name check me if you want me to step back i...

4 months ago
Reply
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's

yes thanks! Im not sure I can really comment further as your key concern (unless I misunderstand you) seems to be the thermal offs which appear to b...

4 months ago
Reply
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW

I cant immediately see anything wrong but I also cant follow the pipework. As you say this is a poor time to test/set things up, but I would still ...

4 months ago
Reply
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW

Great. If you could post a picture of the area around the cylinder it would confirm that there is nothing untoward here.

4 months ago
Reply
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's

Can you explain what you mean by 'off' please? If they are off how is that affecting the heat pump/circuits. If you are getting a SCOP of 3.5 what ...

4 months ago
Reply
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW

@cbrenewable Hopefully the diagram shows one of the valves in the wrong place, otherwise there is a valve in the wrong place. Any idea why two pumps...

4 months ago
Reply
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's

@trebor12345 Hi. What is it you are still trying to solve/understand. I will see if I can help. Definitely that is a 4 port buffer.

4 months ago
Reply
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW

@CBrenewable A COP of 2.4 is definitely low and you are right to be concerned. You should be seeing 4 or better at present. Can you tell us s...

4 months ago
Reply
RE: help sizing rads based on room by room heat loss

The output of a rad is proportional to DT to the power 1.3, where DT is the average temperature difference between rad and room. At a flow temperatu...

4 months ago
Reply
RE: Ecodan - is there actually such a thing as a 'minimum' flow temp to avoid cycling, and why if so?