Hello all, first post here and a question
Doing a full retrofit on new house. Getting ASHP installed later this year but in the meantime preparing wood burning stove.
What are your experiences or opinions about benefit of direct air input for the stove? Was thinking to install air input from subfloor void near external vent.
House will be well insulated but far from air-tight. But considering direct air to avoid cold air being drawn into heat-pump warmed house when stove is on.
Worth it?
Thanks all!
T
@sune is ideal to answer this, but I think he's on vacation at the moment.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Hi Topher,
Thanks for the tag Mars. I am.indeed on hols in Denmark, home of the wood stove perhaps!
A direct air supply is a good idea for reducing draughts, but you have to be aware of a few things. Resistance in the duct is one, how it terminates is another, and making sure the fabric of the house is protected if you get downdraught- as the duct will then get hot.
I made a direct air guide - I can get it emailed to you if you like. I'm Sune@firepower.co.uk
The other consideration is that when you open the stove door to refuel then the duct doesn't supply that air. That air has to come from the room, and is a LOT higher flow rate than is just needed to.keep the stove burning (ie 25lt/s+). You may have enough air leaking in to supply that, you may need a direct vent to the room (nor so great for air tightness), or I came up with Airsmart which automatically opens a sealed vent to the outside whenever the stove door opens.
Hetas have a helpful assessment procedure to work this out (TN0020), which is basically shutting all doors and windows, turning on all extractors, and then testing a warm stove and chimney with the door open for smoke leakage with a smoke pellet. You could initially try yourself. If it smokes into the room a bit then open a window - does that improve things? You probably need a vent or Airsmart if so. Bear in mind that if you try to test when it's hot weather then your chimney draw will be poor, ie wait till its cold weather.
Good luck with it!
Sune
Planning your dream house? Book a simple one-to-one consultation to get you on a good path - here.
Posted by: @suneI am indeed on hols in Denmark,
I love the new fully Viking look... best personal avatar on the site.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @topherHello all, first post here and a question
Doing a full retrofit on new house. Getting ASHP installed later this year but in the meantime preparing wood burning stove.
What are your experiences or opinions about benefit of direct air input for the stove? Was thinking to install air input from subfloor void near external vent.
House will be well insulated but far from air-tight. But considering direct air to avoid cold air being drawn into heat-pump warmed house when stove is on.
Worth it?
Thanks all!
T
This depends on the size of your wood burner and size/type of house. If your house is a tad leaky, stoves labelled 5kw and below don't need direct air to satisfy HETAS regs.
5kw is a bit of a moveable feast I've seen whoppas sold with that label and smaller ones.
I have a heat pump & 5 Kw wood burner with no problems (except it can get a bit hot because I have a bunch of old oak to finish up) no cold air gets drawn in at all.
- 26 Forums
- 2,367 Topics
- 53.7 K Posts
- 333 Online
- 6,042 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
@drei The second PW2 was installed by the same company ...
By Toodles , 4 minutes ago
-
RE: New Fogstar 15.5kWh upright solution
They all use a standard or derivative communication and...
By swwils , 6 minutes ago
-
RE: Help needed with Grant Aerona 3 issues
The black cylinder in the second photo looks like an ll...
By JamesPa , 12 minutes ago
-
RE: How long will your energy contract last?
My INTELLI-FIX-12M-25-08-29 has less than 12 months to ...
By Batpred , 20 minutes ago
-
Wow, it looks like I missed out in the fun here.. Whe...
By Batpred , 24 minutes ago
-
RE: GivEnergy 2025 forthcoming batteries and inverters
Then, perhaps @toodles , you should've made a submissio...
By Transparent , 34 minutes ago
-
RE: Changing from 4-port buffer to volumizer
Here are my comments, others may have something to add ...
By JamesPa , 44 minutes ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I am wondering if anyone with an EV could find the 7p/k...
By Batpred , 46 minutes ago
-
Possibly, but it would also reduce DeltaT across the em...
By JamesPa , 53 minutes ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Solis are working to resolve some comms design issues b...
By Batpred , 60 minutes ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@cathoderay It was reminiscent of the BBC Open Universi...
By Toodles , 1 hour ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
TC Thermostatic Radiator Valve TRV Plastic Decorators S...
By Toodles , 24 hours ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
UPDATE: Thanks everyone who commened with suggestions h...
By 9jwr9 , 1 day ago
-
-
@morgan They are unsupervised these days, can’t get the...
By Toodles , 3 days ago
-
RE: Setback savings - fact or fiction?
Exactly. We only need to compare conditions, to decide ...
By cathodeRay , 4 days ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Welcome @mickamills We too have an oversized 12kW Sa...
By Old_Scientist , 5 days ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
@caron I can confirm that the power usage of the PW3 is...
By Old_Scientist , 5 days ago
-
RE: Speedcomfort radiator fans
Thats true, but having tried (and succeeded) in constru...
By JamesPa , 5 days ago