(@heatgeek)
Reputable Member Member
Joined: 5 months ago
Posts: 116
 

@johnmo  Agreed on size of buffer tank. They also say that the flow of secondary pump must be higher than primary, therefore they are proposing a kind of thermal store which, intuitively, would need to have some volume. Most manufacturers propose small 4 port buffers or LLHs in their system diagrams. This is the first I have seen specifically mandating a 2 port buffer. There could be some mileage in this in some circumstances. There could be some dilution of output flow temperature theoretically but buffer size (stratification) and minimising reverse bypass flow will mitigate this.

This post was modified 18 hours ago by Heatgeek

Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.


   
ReplyQuote
(@johnmo)
Noble Member Member
Joined: 2 years ago
Posts: 482
 

Posted by: @heatgeek

2 port buffer

2 port buffers by design work very differently from a 3 or 4 port. Heat pump is controlled to only work when the buffer asks for heat, not the house. The heat pumps job therefore becomes keeping the buffer satisfied.

So if you have a house call for heat, it draws energy from the buffer. As the buffer temperature falls, the ASHP is asked to start. If the heating system demand matches ASHP output, the buffer is bypassed either fully or partially, if there is a mismatch in flow/energy the excess flow/energy travels through the buffer. When buffer is hot enough heat pump is cycled off.

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
(@heatgeek)
Reputable Member Member
Joined: 5 months ago
Posts: 116
 

@johnmo  Agree entirely.

Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.


   
ReplyQuote



(@johnmo)
Noble Member Member
Joined: 2 years ago
Posts: 482
 

The other thing I forget to mention, just design out the buffer, save on the cost of a 200L+ buffer, which isn't cheap, plus the additional pump, various isolation valves etc, soon adds up. It's alright the manufacturer adding these lines of text, but the end user picks up the bill. Could quite easily add another £1k to the install bill, so even after the grant the end user just has to pay another £1k, for what? More cupboard space lost.

Just had a look - A Viessmann 6kW heat pump has a retail price of £11k, although Viessmann direct will sell you one for £6k and you still a cylinder, so that takes you to £7800 (retail £14k). So all of the grant has gone already, if installer sells to you for suggested retail price you already have a £7k bill, without install and heating system mods.

Just cannot see the justification in cost even at the reduced price. Swapping out my £1300 heat pump would not save me much, no matter how much better CoP I got.

Think the manufacturer have lost the plot on pricing, or the consumer and tax payer is being taken for a ride, take your choice. Poor consumer who doesn't know or have options, they just have to get a new mortgage. Or it's as some of the press say heat pumps - a rich persons game

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
👍
1
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2424
 

Posted by: @johnmo

Posted by: @heatgeek

They state that a buffer tank can "significantly" improve the operation of their heat pump.

Yes it would prolong run times as they say to use a minimum of 200L.  Great if you have space, but then you have lots of radiators so should have lots of water capacity anyway. They also say if running on radiators only.

... but a volumiser would prolong run times by the same amount without any of the downside risk in performance, difficulties with fault diagnosis and extra cost.

I'm still failing to understand why we are even considering buffers unless the use case is somehow exceptional.  Unless there is a concrete reason for system separation which cannot be designed out, why not (as @johnmo advocates), KISS?

Perhaps someone can give me a concrete reason.  It seems installers who use them cant, or at least won't come on here to defend their position.  For the avoidance of doubt my comment applies to domestic installations in 'normal sized' houses, not mansions or commercial neither of which I have thought much about.

This post was modified 15 hours ago by JamesPa
This post was modified 14 hours ago 3 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@damon)
Eminent Member Member
Joined: 1 year ago
Posts: 11
 

@heatgeek Nibe also promote the two pipe buffer, I use this set up when cascading.

 

you would want flow rates matching best you could though. Although secondary side would probably be pressure dependant pump tbe primary would be fixed speed as it slowed on the secondary it would allow flow through the buffer. The only issue with these diagrams is they don’t take into account any separation on the pumps as they are connected via the flow. I always upsize from the tee, and take into the buffer and too the secondary pump with increased pipe size. 

Professional heat pump installer


   
👍
1
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2424
 

@damon thank you for posting.

Would you care to tell us in what circumstances you fit a buffer tank, why, and how you set it up to avoid a cop penalty due to system distortion/blending of flow with return? 

So far professional installers who fit buffer tanks have been reluctant to explain their position on this forum, whereas those who don't have been happy to explain quite clearly why not (in a domestic situation other than a mansion).

This is a genuine question, it would be really interesting to know.

Also:

Posted by: @damon

you would want flow rates matching best you could though. 

How do you do this with heat pumps that modulate their water pump according to energy demand (eg Samsung, Daikin I believe), or don't you fit such heat pumps?

This post was modified 5 hours ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Page 3 / 3



Share:

Join Us!

Trusted Installers

Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.

✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available

👉 Find your installer now!

Latest Posts

Members Online

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security