Buzzing noise from UFH manifold
Our heat pump was installed in November 21 and was connected to our existing UFH system. All has been working well, but in the last week or two I’ve noticed a loud buzzing noise coming from the UFH manifold when the kitchen is calling for heat.
it’s a strange noise, it reminds me of an old dot matrix printer printing. I’ve uploaded a clip so you can hear what I mean:
https://youtube.com/shorts/F5N6KFYcJw8?feature=share
does anyone have any ideas what is causing the noise, and what I should do to stop it? As far as I can tell, the heating is still working as normal
i’ve discovered that turning the flow rate valve on the kitchen supply does temporarily stop the noise, but when I put it back to the original position the noise starts again after a short while.
Wow! ASHPs need to deliver more flow than conventional fired boiler heating systems, as they operate a much lower delta T supply and return temperature. For many retrofits, including wet rad and UFH, that usually means the existing piping system ends up with higher velocities than before. Velocities above certain speeds will start to generate audible noise. It's not normally practical to increase the piping sizes for retrofits, so you may have to adjust some flow rates to stop noisy valves and pipework where the flow is higher.
That makes sense, but I don't see why it would only start making a noise now - 14 months after installing the system. Up until now it's been running fine without any noise. I was wondering whether it could be the sound of air in the system, or something like that? Maybe that is a non-issue for these systems? We have no radiators, UFH throughout.
Maybe a bit of wear and tear? Bleed the system of air, it's not something you want in the system. I have one TRV that quietly 'sings' when it modulates down, and it's in our bedroom!!
Posted by: @novemberromeoThat makes sense, but I don't see why it would only start making a noise now - 14 months after installing the system. Up until now it's been running fine without any noise. I was wondering whether it could be the sound of air in the system, or something like that? Maybe that is a non-issue for these systems? We have no radiators, UFH throughout.
You have partially answer the question yourself, in that it has been working fine for 14 months without making any noise, so I don't think that the actual pipework may be at fault.
Is the noise coming from the flow regulation valve or the valve associated with the solenoid valve?
I am not that familiar with UFH systems, but it sounds like it could be some debris inside the valve or some part of the valve internals is working loose.
Is it still under warranty?
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 93 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: No-code, plug-and-play monitoring for your heat pump
By Grantmethestrength , 12 hours ago
-
@eliuccio good to hear you’re happy with the install. A...
By Mars , 21 hours ago
-
RE: Is this just haze or something more?
I am not a scientist nor a meteorologist and I know the...
By Toodles , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
It will improve performance, but by how much depends on...
By Brendon Uys , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 2 days ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 3 days ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 3 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 3 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 3 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 3 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 4 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 5 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 5 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 1 week ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 1 week ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 1 week ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 1 week ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago