Posted by: @gshpwoes@kev-m the v hot water isnt all the time - was just when we had the cold snap - the hot water out the tap was really hot, despite the fact the rads were barely warm. but sometimes its not hot enough... ug. we do have a an immersion that was on the first week we moved in, and our bills were astronomical(even back with low kwh prices!) so i know it is definitely not on now as we switched it off. House is approx 300m2, so it is large, but i know people with much larger houses using a lot less kwh than us...
I would look for a 3-way diverter valve or two 2-way valves that divert the warm water from the heat pump to the central heating or DHW cylinder. It is possible one of the valve/s is sticking intermittently.
Please provide some photo's of your system.
Posted by: @gshpwoes@hughf we are purely electric no gas. our kwh per year was approx 20,000kwh but last year was just over 16,00kwh...
if we assume 18000kWh, that’s a 3kW immersion heater, on for 24hrs a day, for 250 days…. Are you sure you aren’t running on the backup heater in the buffer tank?
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
thank you for all your replies and sorry im so clueless - im embarrassed i know so little after so much time!
@gshpwoes, there is absolutely nothing to be embarrassed about. These systems should just work, and for the geeks these systems allow us to geek out further, but it’s frustrating when they’re inherently broken. If you continue to struggle and would like a pro like @heacol to come out and investigate, I can connect you.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @gshpwoes@derek-m what photos would be helpful - i can take them tomorrow.
Wide view of the different parts of the system, then close-ups of individual items of equipment, along with screen displays from your controller showing anything of importance.
Basically the more information the better.
Locate your diverter valves or valves and see if you can check operation by initiating DHW heating then back to central heating. Check the temperature of the pipework around the valves and buffer tank or low loss header.
6kW immersion in the bottom of the hot water tank won’t be helping things….
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Why are you running your rads at 46 degrees in this weather? That seems excessive.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 30 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Nice one @toodles... always appreciate your enthusiasm ...
By Mars , 1 hour ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 6 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@patrickvito We have had car dealers re-powder coat the...
By ASHP-BOBBA , 6 hours ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 7 hours ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 7 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 7 hours ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 10 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 12 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 13 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 14 hours ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 1 day ago
-
@drei When I was in local government we were of cours...
By JamesPa , 1 day ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 2 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 2 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 2 days ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 2 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago