Simulation of ASHP with Gas boiler as part of decision process
Hello, new to the forum, thanks for having me.
I would like to transition to an ASHP, but it seems to be fraught with complications, so my brain tells me to experiment before making a decision; get more real data.
My approach is then, to simulate an ASHP with my current gas system boiler over the coming heating season. My question to the forum is if anyone did this before and any tips or tricks to make it as accurate as possible?
My approach so far;
1.Got a FOC heat loss survey.
2. Set my system boiler flow temperature to 50degC and reduced it's power output from 18kW to 8kW in line with total heat loss estimate @ -3C.
3. Downstairs TRVs all set to maximum (6). Upstairs set to 3 on a scale of 6, except bathroom set to max (6).
4. Home most days, set system to heat 6AM - 11PM, main thermostat target 23C (yes that's how the Mrs must have it!). Hot water 5AM - 6AM daily - will manually run weekly legionella heat to 60C on a Sunday.
Anything else I can do?
Known possible issues for accuracy of experiment:
Boiler modulation down to 5kW only - likely to cause cycling
Kitchen has new hydronic baseboard heater, heating system not balanced yet
Unsure about physical location of a future ASHP and pipe runs, how impacting might that be.
No weather compensation.
Thanks!
I did pretty much the same. The overall conclusion for me is that low and slow makes for a more comfortable living environment and it confirmed that my loss calculations based on actual consumption give a figure which keeps me warm.
Because my boiler isn't weather compensated I had to manually adjust the ft during the season which means that the trvs were still kicking in, but I don't think that materially affected the experiment.
Cycling is inevitable if your boiler can't modulate down to match your house demand.
In summary I felt it was a useful experiment that will remain in place until I can get an ashp because it results in a greater level of comfort.
I can't really offer any tips beyond what you have done, like me the missing feature is weather compensation but my feeling is that this will further improve comfort.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the reply, we tried this last year and we couldn't keep the living room to the tropical temperature required, which actually led me to investigate more and found some missing insulation, so whatever happens it's helped us.
Posted by: @scalextrix@jamespa thanks for the reply, we tried this last year and we couldn't keep the living room to the tropical temperature required, which actually led me to investigate more and found some missing insulation, so whatever happens it's helped us.
Better insulation is best but of course bigger radiators may also be necessary to get tropical room temperature with low flow temperature. That's part of the design process (t's not much use having an ashp that can kick out 12kW if your rads can only do 8kW at your chosen flow temp). In a living room consider fancoils, large output, small footprint, can also be used for mild cooling. Costly for anything well styled (they appear to be most common in Italy, so quite a few are) and of course there is a background hum from the fan, but a useful addition to the low temperature heating retrofit toolbox
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
We tried the retrofit fans that stick with magnets to the rads a few years ago just for fun. While they were silent before putting on the rad, once they were in place the radiator made an irritating buzz/rattle that wasn't acceptable for a living room. Other people may have different experiences.
We have 2 rads in there, one is a type 22 and can be made a bit wider, the other is a type 21, while it can't be any bigger, we can upgrade to a type 22. I'm hoping with the improved insulation that should be enough to get what we need.
Posted by: @scalextrixWe have 2 rads in there, one is a type 22 and can be made a bit wider, the other is a type 21, while it can't be any bigger, we can upgrade to a type 22.
I have a small old leaky listed building with limited wall space. As a very general rule of thumb, if you have correctly sized radiators for a fossil fuel system running at high flow temps, then for an ASHP system running at the upper end of acceptable flow temps, then you will need new rads that have twice the effective area of the fossil fuel rads. This is quite a big jump, something not always appreciated in the early planning stages. Doubling the area of the rad is one option, but so too are different form factors. I ended up with all K3 rads bar two, and some of the K3s needed to be quite a bit larger than the K2s they replaced. Instead of rads that were relatively discrete, I now have rads that no doubt an estate agent would describe as 'a feature'...
1330: Edited to change 'twice the output of the fossil fuel rads' to 'twice the effective area of the fossil fuel rads' as in my experience this is an area in which it is easy to get very confused very quickly... The key point to understand is that the heat transfer to the room depends on the 'delta t' (temperature difference) between the mean radiator temp and the room temp. Halve the mean rad temp, and keep everything else constant, then the heat transfer will be give or take half what it was at the higher temp. To compensate (get the same amount of heat transferred), you have to double the effective size (area) of the radiator.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayI ended up with all K3 rads bar two, and some of the K3s needed to be quite a bit larger than the K2s they replaced. Instead of rads that were relatively discrete, I now have rads that no doubt an estate agent would describe as 'a feature'...
This is an area where the industry tendency to oversize can cause a real problem. I decided to start rad upgrades in advance so far for half of the house only) and based the sizing initially on the MCS assumptions. This gave me one K3 in the master bedroom which my wife hates. Subsequently I have concluded that the MCS assumptions lead to an over estimate of the loss and, had I known this earlier, I could have got away with a much more acceptable K2.
Sizing doesn't just affect the odu, it affects the whole system, so it's important imho to get it as accurate as possible if wrong sizing is likely to drive difficult to reconcile design decisions
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@cathoderay 🤩 Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @jamespaSizing doesn't just affect the odu, it affects the whole system, so it's important imho to get it as accurate as possible if wrong sizing is likely to drive difficult to reconcile design decisions
I strongly endorse this. Some of the quotes I had from various goons claiming to be heating engineers had hopelessly out of whack rad specs. For radiator sizing, the steps are:
1. Accurate heat loss calcs for each room
2. Select a radiator that will (a) fit in the available space (a sina qua non) and (b) has the right heat output at AHSP flow temps for that room
Follow that procedure, and you won't go far wrong.
Midea 14kW (for now...) ASHP heating both building and DHW
I took this ‘simulation approach’ last year. Based on my own heat loss calculations (including a very wet finger in the air for air change), I suspect that I will need to change many of the radiators. One of my concerns (largely due to it being big concern of my wife) is that the 10mm radiator pipe work downstairs comes out of the wall so the pitch of the valve connections and their distance from the wall are fixed. Replacement radiators will likely need a couple of additional pipe fittings at each end - not an aesthetic solution and additional resistance to the flow.
Posted by: @ianmk1310mm radiator pipe work
10mm pipe is ok for about 1kW at dT5. So really depends how the system is laid out and how you transition to 10mm and the other piping sizes. Lots of consideration other than just replacing pipe tails
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
1 day ago
-
Rodents! A word of warning for heat pump owners
3 weeks ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
1 month ago
-
Running my new Nibe ASHP efficiently
1 month ago
-
Weather compensation- why you should use it
1 month ago
Currently viewing this topic 1 guest.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 343 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: What determines the SOC of a battery?
@batpred I didn't write the Seplos BMS software, I a...
By Bash , 12 minutes ago
-
RE: Electricity price predictions
Sorry to derail this thread ‘slightly?’ but back to the...
By Toodles , 22 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
Without knowing it, @andrewj, you've laid down the gaun...
By Majordennisbloodnok , 41 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos and @cathoderay thanks. I have some history grap...
By benson , 45 minutes ago
-
I am having my existing heat pump changed to a Vaillant...
By trebor12345 , 1 hour ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 2 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 4 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 4 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 10 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 20 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 22 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago