Hello, new to the forum, thanks for having me.

I would like to transition to an ASHP, but it seems to be fraught with complications, so my brain tells me to experiment before making a decision; get more real data.

 

My approach is then, to simulate an ASHP with my current gas system boiler over the coming heating season.  My question to the forum is if anyone did this before and any tips or tricks to make it as accurate as possible?

 

My approach so far;

 

1.Got a FOC heat loss survey.

2. Set my system boiler flow temperature to 50degC and reduced it's power output from 18kW to 8kW in line with total heat loss estimate @ -3C.

3. Downstairs TRVs all set to maximum (6). Upstairs set to 3 on a scale of 6, except bathroom set to max (6).

4. Home most days, set system to heat 6AM - 11PM, main thermostat target 23C (yes that's how the Mrs must have it!). Hot water 5AM - 6AM daily - will manually run weekly legionella heat to 60C on a Sunday.

Anything else I can do?

Known possible issues for accuracy of experiment:

Boiler modulation down to 5kW only - likely to cause cycling

Kitchen has new hydronic baseboard heater, heating system not balanced yet

Unsure about physical location of a future ASHP and pipe runs, how impacting might that be.

No weather compensation.

 

Thanks!

This topic was modified 4 months ago by Scalextrix

   
👍
2
Quote
(@jamespa)
Famed Member Moderator
8782 kWhs
Joined: 2 years ago
Posts: 1560
 

I did pretty much the same.  The overall conclusion for me is that low and slow makes for a more comfortable living environment and it confirmed that my loss calculations based on actual consumption give a figure which keeps me warm. 

Because my boiler isn't weather compensated I had to manually adjust the ft during the season which means that the trvs were still kicking in, but I don't think that materially affected the experiment.

Cycling is inevitable if your boiler can't modulate down to match your house demand.

In summary I felt it was a useful experiment that will remain in place until I can get an ashp because it results in a greater level of comfort.

I can't really offer any tips beyond what you have done, like me the missing feature is weather compensation but my feeling is that this will further improve comfort.


   
🤩
1
ReplyQuote
(@scalextrix)
Eminent Member Member
93 kWhs
Joined: 4 months ago
Posts: 12
Topic starter  

@jamespa thanks for the reply, we tried this last year and we couldn't keep the living room to the tropical temperature required, which actually led me to investigate more and found some missing insulation, so whatever happens it's helped us.


   
ReplyQuote



(@jamespa)
Famed Member Moderator
8782 kWhs
Joined: 2 years ago
Posts: 1560
 

Posted by: @scalextrix

@jamespa thanks for the reply, we tried this last year and we couldn't keep the living room to the tropical temperature required, which actually led me to investigate more and found some missing insulation, so whatever happens it's helped us.

Better insulation is best but of course bigger radiators may also be necessary to get tropical room temperature with low flow temperature.  That's part of the design process (t's not much use having an ashp that can kick out 12kW if your rads can only do 8kW at your chosen flow temp).  In a living room consider fancoils, large output, small footprint, can also be used for mild cooling.  Costly for anything well styled (they appear to be most common in Italy, so quite a few are) and of course there is a background hum from the fan, but a useful addition to the low temperature heating retrofit toolbox 

 

This post was modified 4 months ago 2 times by JamesPa

   
ReplyQuote
(@scalextrix)
Eminent Member Member
93 kWhs
Joined: 4 months ago
Posts: 12
Topic starter  

We tried the retrofit fans that stick with magnets to the rads a few years ago just for fun.  While they were silent before putting on the rad, once they were in place the radiator made an irritating buzz/rattle that wasn't acceptable for a living room.  Other people may have different experiences.

We have 2 rads in there, one is a type 22 and can be made a bit wider, the other is a type 21, while it can't be any bigger, we can upgrade to a type 22.  I'm hoping with the improved insulation that should be enough to get what we need.


   
ReplyQuote
(@johnmo)
Prominent Member Member
2299 kWhs
Joined: 2 years ago
Posts: 422
 

Posted by: @scalextrix

type 22.

Can you upgrade to to type 33?

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
8976 kWhs
Joined: 3 years ago
Posts: 1805
 

Posted by: @scalextrix

We have 2 rads in there, one is a type 22 and can be made a bit wider, the other is a type 21, while it can't be any bigger, we can upgrade to a type 22. 

I have a small old leaky listed building with limited wall space. As a very general rule of thumb, if you have correctly sized radiators for a fossil fuel system running at high flow temps, then for an ASHP system running at the upper end of acceptable flow temps, then you will need new rads that have twice the effective area of the fossil fuel rads. This is quite a big jump, something not always appreciated in the early planning stages. Doubling the area of the rad is one option, but so too are different form factors. I ended up with all K3 rads bar two, and some of the K3s needed to be quite a bit larger than the K2s they replaced. Instead of rads that were relatively discrete, I now have rads that no doubt an estate agent would describe as 'a feature'...

1330: Edited to change 'twice the output of the fossil fuel rads' to 'twice the effective area of the fossil fuel rads' as in my experience this is an area in which it is easy to get very confused very quickly... The key point to understand is that the heat transfer to the room depends on the 'delta t' (temperature difference) between the mean radiator temp and the room temp. Halve the mean rad temp, and keep everything else constant, then the heat transfer will be give or take half what it was at the higher temp. To compensate (get the same amount of heat transferred), you have to double the effective size (area) of the radiator.        

This post was modified 4 months ago by cathodeRay

Midea 14kW (for now...) ASHP heating both building and DHW


   
👍
1
ReplyQuote
(@jamespa)
Famed Member Moderator
8782 kWhs
Joined: 2 years ago
Posts: 1560
 

Posted by: @cathoderay

I ended up with all K3 rads bar two, and some of the K3s needed to be quite a bit larger than the K2s they replaced. Instead of rads that were relatively discrete, I now have rads that no doubt an estate agent would describe as 'a feature'...    

This is an area where the industry tendency to oversize can cause a real problem.  I decided to start rad upgrades in advance  so far for half of the house only) and based the sizing initially on the MCS assumptions.  This gave me one K3 in the master bedroom which my wife hates.  Subsequently I have concluded that the MCS assumptions lead to an over estimate of the loss and, had I known this earlier, I could have got away with a much more acceptable K2. 

Sizing doesn't just affect the odu, it affects the whole system, so it's important imho to get it as accurate as possible if wrong sizing is likely to drive difficult to reconcile design decisions 


   
ReplyQuote
Toodles
(@toodles)
Famed Member Contributor
10208 kWhs
Veteran
Joined: 2 years ago
Posts: 1661
 

@cathoderay 🤩 Toodles

Toodles, he heats his home with cold draughts and cooks his food with magnets.


   
ReplyQuote



cathodeRay
(@cathoderay)
Famed Member Moderator
8976 kWhs
Joined: 3 years ago
Posts: 1805
 

Posted by: @jamespa

Sizing doesn't just affect the odu, it affects the whole system, so it's important imho to get it as accurate as possible if wrong sizing is likely to drive difficult to reconcile design decisions 

I strongly endorse this. Some of the quotes I had from various goons claiming to be heating engineers had hopelessly out of whack rad specs. For radiator sizing, the steps are:

1. Accurate heat loss calcs for each room

2. Select a radiator that will (a) fit in the available space (a sina qua non) and (b) has the right heat output at AHSP flow temps for that room

Follow that procedure, and you won't go far wrong.

Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@ianmk13)
Reputable Member Member
2727 kWhs
Joined: 2 years ago
Posts: 164
 

I took this ‘simulation approach’ last year.  Based on my own heat loss calculations (including a very wet finger in the air for air change), I suspect that I will need to change many of the radiators. One of my concerns (largely due to it being big concern of my wife) is that the 10mm radiator pipe work downstairs comes out of the wall so the pitch of the valve connections and their distance from the wall are fixed. Replacement radiators will likely need a couple of additional pipe fittings at each end - not an aesthetic solution and additional resistance to the flow. 


   
ReplyQuote
(@johnmo)
Prominent Member Member
2299 kWhs
Joined: 2 years ago
Posts: 422
 

Posted by: @ianmk13

10mm radiator pipe work

10mm pipe is ok for about 1kW at dT5. So really depends how the system is laid out and how you transition to 10mm and the other piping sizes. Lots of consideration other than just replacing pipe tails

 

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   