Simulation of ASHP with Gas boiler as part of decision process
Hello, new to the forum, thanks for having me.
I would like to transition to an ASHP, but it seems to be fraught with complications, so my brain tells me to experiment before making a decision; get more real data.
My approach is then, to simulate an ASHP with my current gas system boiler over the coming heating season. My question to the forum is if anyone did this before and any tips or tricks to make it as accurate as possible?
My approach so far;
1.Got a FOC heat loss survey.
2. Set my system boiler flow temperature to 50degC and reduced it's power output from 18kW to 8kW in line with total heat loss estimate @ -3C.
3. Downstairs TRVs all set to maximum (6). Upstairs set to 3 on a scale of 6, except bathroom set to max (6).
4. Home most days, set system to heat 6AM - 11PM, main thermostat target 23C (yes that's how the Mrs must have it!). Hot water 5AM - 6AM daily - will manually run weekly legionella heat to 60C on a Sunday.
Anything else I can do?
Known possible issues for accuracy of experiment:
Boiler modulation down to 5kW only - likely to cause cycling
Kitchen has new hydronic baseboard heater, heating system not balanced yet
Unsure about physical location of a future ASHP and pipe runs, how impacting might that be.
No weather compensation.
Thanks!
I did pretty much the same. The overall conclusion for me is that low and slow makes for a more comfortable living environment and it confirmed that my loss calculations based on actual consumption give a figure which keeps me warm.
Because my boiler isn't weather compensated I had to manually adjust the ft during the season which means that the trvs were still kicking in, but I don't think that materially affected the experiment.
Cycling is inevitable if your boiler can't modulate down to match your house demand.
In summary I felt it was a useful experiment that will remain in place until I can get an ashp because it results in a greater level of comfort.
I can't really offer any tips beyond what you have done, like me the missing feature is weather compensation but my feeling is that this will further improve comfort.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the reply, we tried this last year and we couldn't keep the living room to the tropical temperature required, which actually led me to investigate more and found some missing insulation, so whatever happens it's helped us.
Posted by: @scalextrix@jamespa thanks for the reply, we tried this last year and we couldn't keep the living room to the tropical temperature required, which actually led me to investigate more and found some missing insulation, so whatever happens it's helped us.
Better insulation is best but of course bigger radiators may also be necessary to get tropical room temperature with low flow temperature. That's part of the design process (t's not much use having an ashp that can kick out 12kW if your rads can only do 8kW at your chosen flow temp). In a living room consider fancoils, large output, small footprint, can also be used for mild cooling. Costly for anything well styled (they appear to be most common in Italy, so quite a few are) and of course there is a background hum from the fan, but a useful addition to the low temperature heating retrofit toolbox
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
We tried the retrofit fans that stick with magnets to the rads a few years ago just for fun. While they were silent before putting on the rad, once they were in place the radiator made an irritating buzz/rattle that wasn't acceptable for a living room. Other people may have different experiences.
We have 2 rads in there, one is a type 22 and can be made a bit wider, the other is a type 21, while it can't be any bigger, we can upgrade to a type 22. I'm hoping with the improved insulation that should be enough to get what we need.
Posted by: @scalextrixWe have 2 rads in there, one is a type 22 and can be made a bit wider, the other is a type 21, while it can't be any bigger, we can upgrade to a type 22.
I have a small old leaky listed building with limited wall space. As a very general rule of thumb, if you have correctly sized radiators for a fossil fuel system running at high flow temps, then for an ASHP system running at the upper end of acceptable flow temps, then you will need new rads that have twice the effective area of the fossil fuel rads. This is quite a big jump, something not always appreciated in the early planning stages. Doubling the area of the rad is one option, but so too are different form factors. I ended up with all K3 rads bar two, and some of the K3s needed to be quite a bit larger than the K2s they replaced. Instead of rads that were relatively discrete, I now have rads that no doubt an estate agent would describe as 'a feature'...
1330: Edited to change 'twice the output of the fossil fuel rads' to 'twice the effective area of the fossil fuel rads' as in my experience this is an area in which it is easy to get very confused very quickly... The key point to understand is that the heat transfer to the room depends on the 'delta t' (temperature difference) between the mean radiator temp and the room temp. Halve the mean rad temp, and keep everything else constant, then the heat transfer will be give or take half what it was at the higher temp. To compensate (get the same amount of heat transferred), you have to double the effective size (area) of the radiator.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayI ended up with all K3 rads bar two, and some of the K3s needed to be quite a bit larger than the K2s they replaced. Instead of rads that were relatively discrete, I now have rads that no doubt an estate agent would describe as 'a feature'...
This is an area where the industry tendency to oversize can cause a real problem. I decided to start rad upgrades in advance so far for half of the house only) and based the sizing initially on the MCS assumptions. This gave me one K3 in the master bedroom which my wife hates. Subsequently I have concluded that the MCS assumptions lead to an over estimate of the loss and, had I known this earlier, I could have got away with a much more acceptable K2.
Sizing doesn't just affect the odu, it affects the whole system, so it's important imho to get it as accurate as possible if wrong sizing is likely to drive difficult to reconcile design decisions
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@cathoderay 🤩 Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @jamespaSizing doesn't just affect the odu, it affects the whole system, so it's important imho to get it as accurate as possible if wrong sizing is likely to drive difficult to reconcile design decisions
I strongly endorse this. Some of the quotes I had from various goons claiming to be heating engineers had hopelessly out of whack rad specs. For radiator sizing, the steps are:
1. Accurate heat loss calcs for each room
2. Select a radiator that will (a) fit in the available space (a sina qua non) and (b) has the right heat output at AHSP flow temps for that room
Follow that procedure, and you won't go far wrong.
Midea 14kW (for now...) ASHP heating both building and DHW
I took this ‘simulation approach’ last year. Based on my own heat loss calculations (including a very wet finger in the air for air change), I suspect that I will need to change many of the radiators. One of my concerns (largely due to it being big concern of my wife) is that the 10mm radiator pipe work downstairs comes out of the wall so the pitch of the valve connections and their distance from the wall are fixed. Replacement radiators will likely need a couple of additional pipe fittings at each end - not an aesthetic solution and additional resistance to the flow.
Posted by: @ianmk1310mm radiator pipe work
10mm pipe is ok for about 1kW at dT5. So really depends how the system is laid out and how you transition to 10mm and the other piping sizes. Lots of consideration other than just replacing pipe tails
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
-
ASHP install contract and BUS grant money
6 days ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 week ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 weeks ago
-
Heat Pump starting current
1 month ago
-
Running my new Nibe ASHP efficiently
1 month ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 53 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 1 hour ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 2 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 2 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 3 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 3 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 3 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 5 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 7 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 9 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 21 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 24 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 9 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 10 hours ago
-
SolarPV tables / online calculator
By MichelleC 17 hours ago
-
By Toodles 2 days ago